Busbar Insulation Inside Medium Voltage VFD Converter Panel

06/01/2013 9:37 AM

Is it standard to have non insulated Busbars inside a 3.3KV Variable Speed Drive Convertor Panel, installed inside a substation, eventhough the panel door is interlocked i.e. when opened it trips the VFD and de-energize the converter panel?

Any Comment and or link to standard/code is appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Busbar Insulation inside Medium Voltage VFD Converter Panel

06/01/2013 1:02 PM

You should state your location. Codes or standards from elsewhere may not apply.

I would guess that uninsulated bus bars are acceptable with the described arrangements. Even if the bus bars were insulated, various connections would probably still remain exposed. If so, insulated bus bars could give a false sense of security.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Busbar Insulation inside Medium Voltage VFD Converter Panel

06/01/2013 1:32 PM

Yes.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Busbar Insulation Inside Medium Voltage VFD Converter Panel

06/03/2013 10:04 AM

The only value in using bus insulation inside of any MV equipment is in when physical clearances between live parts is restricted beyond what is necessary. There is ZERO personnel protection value to insulating the bus, because on MV equipment one should NEVER be working on it live unless extreme precautions and personal protective equipment is used. insulating the bus changes nothing in that regard.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#4

Re: Busbar Insulation Inside Medium Voltage VFD Converter Panel

06/05/2013 10:23 AM

At this voltage, busbar insulation is NOT for people's protection . This is why there must be anyway other devices as interlocks to prevent access to live parts.

If there is some insulation, it is to ensure proper insulation, and decrease overall size of the equipment . Personnally, I prefer non insulated bars, as sleeving can gather dust, age, in other words change of dielectric properties. And at this rather low voltage, thermal considerations are probably more impacting the overall dimensions than insulating distances.

Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments