Dear Honorable Members:
A plant has faced a serious
problem (i.e. damaging of the Inverter) which I am sharing with all of you with
a hope that someone will help in tracing the root cause.
The VFD drive(
Vacon type NXP 1900-6) of 1.8MWatt. which needs 690Volts,and is being supplied
by 11,000 / 720V transformer and this transformer is only dedicated for this
drive which is for one Extruder motor. The VFD got damaged and as per Plant
version the motor (1.8 Mw) is in healthy condition. The plant has its own
generation ( 11,000/ 0.4 Kv) through gas generators
Last thirty
alarms recorded before VFD was damaged
are as follows
17 times
alarm number is 66. That is about main contactor.
12 times
alarm number is 63, that is about emergency stop.
1 time
alarm number is 29, that is about thermistor
On checking the
Inverter, four resistors of the rectifier are showing open circuit, as per
supplier they are concealed resistor with fuse inside, so fuse or resistor is
burnt; it is not clear.
As the machine
supplier can check on line the data, he might has seen overvoltage alarm on
line that is why he thinks there were spikes of high voltage from Transformer
which resulted in this damage.
The Plant
maintenance Department wants to know whether the cause of the damage was due to
spikes of high voltage generated from the transformer or some other relevant
cause
Good Answers: