Transient Voltage Suppressor for 480VAC

07/06/2013 1:12 PM

Hello Everyone,

I am looking for something to protect voltage spikes for our drives on the elevators we have here. The main feeder is 480VAC and is wired directly to our OTIS frequency drives, we have too many of them getting fried every time there is a voltage spike, they cost $9,000 each!

Is there a way to protect them, thank you in advance for all your helpful input. I hope you are all well.

-Rob.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Transient Voltage Suppressor for 480VAC

07/06/2013 2:11 PM

there's always something you can do but I have to wonder about your power provider, why is your power so dirty to begin with??

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#2
In reply to #1

Re: Transient Voltage Suppressor for 480VAC

07/06/2013 4:58 PM

Hi Fredski, You are 100% right, I have installed a smart meter on our main 12.8kv feeder, if it drops below 6 percent I plan to claim back, however being on a small island with Mickey Mouse services there isn't much I can do about the spikes. Any suggestions?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Transient Voltage Suppressor for 480VAC

07/06/2013 8:08 PM

I would talk to GE(linked) about this problem and set up a strategy for protection and improvement to power supply quality....sounds like you need a harmonically compensated line reactor and perhaps some additional peripheral components....

http://www.geindustrial.com/solutions/engineers/docs/FETP-100.pdf

http://www.geindustrial.com/catalog/buylog/20_BL.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#11
In reply to #3

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 9:55 AM

Thanks Solar Eagle, this looks like the right thing, I will call them on Monday.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Transient Voltage Suppressor for 480VAC

07/06/2013 10:21 PM

If you make alteration without consultation with the elevator manufacturer and without performing a risk assessment you leave yourself wide open to charges of malpractice in the event of an accident.

Have you spoken to OTIS? What has been their advice?

It is NOT you're problem!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#12
In reply to #4

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 9:57 AM

Hi TonyS, they claim anything to do with the feed is my issue.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #12

Re: Transient Voltage Suppressor for 480VAC

07/08/2013 8:49 AM

Well, Otis must have seen the problem elsewhere. Milk their experience. Call again, and dig deeper. A lot deeper.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Transient Voltage Suppressor for 480VAC

07/06/2013 10:56 PM

Tony S is correct,no modifications to any of the electrical circuitry should be done without approval of OTIS.

With that in mind, here is a link to surge suppressors:

http://www.zerosurge.com/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#13
In reply to #5

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 9:59 AM

Thanks HiTekRedNek

Register to Reply
Participant

Join Date: Jun 2013
Location: LAGOS (NIGERIA)
Posts: 4
#6

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 12:27 AM

Are you sure that the Installation conditions for the OTIS frequency drives are satisfied? Is your site properly grounded/earthed and protecteted against such negative developments? Is there any installed reactor(s) between your drives and the powerline? Compare the input parameters settings of your frequency drives with the power available. Does the earth continuity conductor terminate on each of the drives? I recommend phoenix contact to you for guaranteed protection.

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#18
In reply to #6

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 10:07 AM

Thanks.

Register to Reply
Power-User

Join Date: Apr 2010
Location: Dominican Republic
Posts: 189
Good Answers: 6
#7

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 7:13 AM

I live in the Dominican Republic, also an island and not too far from you. We are also subject to bad power and it´s a gold mine for me and my Dranetz EP1 power monitor.

I agree with the rest about proceeding with caution and talking to OTIS however just to give you some new input I was working with the US Consul 15 years ago on power problems and after a lot of studies we discovered that a good old SOLA ferroresonant CVS voltage regulator pretty well cleaned up every anomoly from voltage regulation to spikes and distortion so they bought 3 giant ones and put them on each of the 3 phases feeding the entire building and since then no further problems have been reported. Thats 15 years of clean power after installing these units.

The only problem is they are a bit inefficient creating heat and very heavy so in this country, where power is expensive, this can be an issue.

How much power are you drawing? For the CVS to work you must cover the peak inrush current or they will not regulate so place some recording clamp meters like FLUKE sells on the input lines and observe them for a day or 2.

Best Regards

John

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#14
In reply to #7

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 10:01 AM

Thanks for your input John, much appreciated!

Register to Reply Off Topic (Score 4)
5
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#8

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 8:20 AM

I see the suggestion you may need a "harmonically compensated line reactor", etc., but I'd like to make one simple point. A transient voltage protector, or TVS can do the job.

TVS components may not be directly rated for 480vac, but they work perfectly well in series. You can build a simple or a complex power-line-spike protector circuit for as high a voltage as you'd like simply by finding parts (capacitors) with the right voltage rating, or by placing parts (TVS, inductors, etc) in series. For example, you can get a 30KPA360A, which is a 30kW (1ms) TVS device that stands off 360 volts and begins breaking down at 400V (5mA) and can clamp 55A while rising only to 650V (that's 35kW peak).

(High-voltage spike appearing on the power line turn into current spikes when you control their voltage by clamping them.)

OK, yes, 400V isn't a high enough standoff voltage for 480vac (745V peak, including a 10% margin), you'd most likely want at least 750V standoff capability. 30KPA280CA parts are 280-volt bi-directional TVS stocked at Digi-Key (the C means bi-dir, and the A means 5% tolerance). Three of those in series would work fine with 480vac. They'll have a holdoff rating of 840V peak, and will clamp modest spikes to under 1kV. They can clamp massive 65A spikes to 1.4kV, a level your electronics should be able to handle (if not, you can make a two-stage filter).

Actually, I can't believe there aren't already commercial protection-box products out there performing this task.

__________________
Thanks, Win
Register to Reply Good Answer (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9
In reply to #8

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 8:52 AM

I liked your answer, good info I was thinking after consulting with Otis he should be installing a line filter in front of his main feed as well on each individual load, I know that's a bit of overkill but just losing one drive is killing his budget. his problem is quite manageable with the right set up.personally I'd suggest he not build his own but go with filters that have been designed and thoroughly factory tested prior to being added to his site. you get a GA from me

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#16
In reply to #9

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 10:05 AM

Try 11 drives lol!!!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #16

Re: Transient Voltage Suppressor for 480VAC

07/08/2013 8:51 AM

So what?

<...lol...> Lots of love?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
United States - Member - Western Wisconsin

Join Date: Mar 2007
Location: Wisconsin USA
Posts: 305
Good Answers: 25
#26
In reply to #16

Re: Transient Voltage Suppressor for 480VAC

07/11/2013 5:22 PM

You've already lost 11 drives ?

__________________
Troy
Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#15
In reply to #8

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 10:04 AM

Thanks Winfield, I need an off the shelf solution though backed by a warranty though. Your input is appreciated!

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 9:07 AM

FWIW:

Compare the features if the devices at the link I provided to TVS type suppressors.Do not "Roll your own" in this situation.

TVS devices are "one Shot" devices, and sometimes give no indication when they have failed.A catastrophic failure, of course, will be very evident, but otherwise, the failure can be invisible.There are methods of detecting the failure, but still,you will have to replace the TVS after one shot.That makes you vulnerable to multiple rapid spikes.

The link provided,however, is a more advanced system.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#17
In reply to #10

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 10:06 AM

I will consult GE and see what they suggest. Thanks again!

Register to Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#19
In reply to #17

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 1:39 PM

Since the VFDs are fried (and no warranty), have you done an autopsy on them to see what has smoked? These will have built in MOV/TVS's, and these dump the energy to ground. So verify that you have a low impedance ground that can take large surge currents. That said, without having a oscilloscope capture of the surges, so you can see the duration, you don't know if you are just exceeding the joule rating of the VFD built in MOV/TVS surge protectors.

So you need to determine what the surge looks like in your power system. And this is needed for any solution. A line reactor is really a low pass filter, if the problem is long duration voltage surge, it will not fix your problem.

The built in surge suppressor of commercial equipment are really for lightning, and inductive energy suppression.

I will iterate, you must know what your power system is doing. If the surge is caused by a short circuit, that is cleared when a circuit breaker opens, the voltage regulator will overshoot, and this duration is a function of it's correct or incorrect tuning. Since you are on a island power system, you don't have the "infinite" system that the main land has to absorb regulator over/under shoot issues.

__________________
ignator -
Register to Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#24
In reply to #19

Re: Transient Voltage Suppressor for 480VAC

07/08/2013 1:41 PM

I read this, and I did not make it clear that the regulator is the power system, not the VFD that's being damaged.

__________________
ignator -
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#20

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 1:51 PM

A well designed surge suppressor system will have 3 mode suppression,(and in some cases 4 modes.)

Phase to phase

Phase to neutral

Phase to ground

Neutral to ground

Consider this and inquire before purchasing a system.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#21

Re: Transient Voltage Suppressor for 480VAC

07/07/2013 2:13 PM

Here is a link to a technical paper on this problem:

http://zerosurge.com/attachments/Equip_Prot_article_02c.pdf

Good luck.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#25
In reply to #21

Re: Transient Voltage Suppressor for 480VAC

07/08/2013 2:31 PM

Thanks HiTekRedNeck,

I will reach out to these guys to see what they can offer for the drives I have. Much appreciated!!!

-Rob.

Register to Reply
Participant

Join Date: Nov 2013
Posts: 1
#27

Re: Transient Voltage Suppressor for 480VAC

11/26/2013 12:50 AM

Hi Robotech,

I'm wondering if the I/O boards are also getting fried when you have a voltage spike. We have an OTIS elevator that the I/O board had to be replaced and the solid state starter had to be replaced due to shortages in the SCR (semi conductive rectifier). I'm just trying to understand if the trouble with our elevator is related to the power outages we experienced in our area or not. What on the frequency drives is going out in your situation.

Thanks,

Murph

Register to Reply Off Topic (Score 5)
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: