Generator for Pumping Station

07/08/2013 5:26 AM

Hi

We are constructing a temporary pumping station for sewage and the load requirements are as below

Pumps 2 duty, 1 standby, capacity 375 kW, 415V, operated through soft starter.

Other loads - 25 kW.

kindly help me in finding a suitably sized generator to run this station round the clock and please note that no pumps will start at the same time. ie the worst case scenario will be other loads +1 pump running and the second pump starting.

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: Generator for pumping station

07/08/2013 6:21 AM
Register to Reply
6
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Generator for pumping station

07/08/2013 6:51 AM

For soft starting, one rule of thumb is the sum of all running loads plus 2.5 x the load to be started. In your case, 400 + 2.5 x 375 = 1337.5; i.e. 1350 or 1400 kW.

I would verify this with the prospective genset supplier; their particulars may vary somewhat.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 6)
Member

Join Date: Jul 2013
Posts: 8
#3
In reply to #2

Re: Generator for pumping station

07/08/2013 7:48 AM

Thanks, Tornado and nobodysomebody 47

Register to Reply
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#4

Re: Generator for Pumping Station

07/09/2013 3:34 AM

One further point - when talking to the generator supplier remember to give them your local elevation and climate conditions as this will affect the performance of the generator and will likely reduce the peak output so youmay need a gen with a larger than apparently needed output

__________________
Free advice guaranteed or your money back
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jul 2013
Posts: 2
#5

Re: Generator for Pumping Station

07/09/2013 6:48 AM

Sounds like a commercial venture, I would suggest a Cummins Genset, ya I work for Cummins, but it is a good product. I do not represent Cummins, but I am suggesting you take a look at the HC Range of gensets, they run on just about any fuel you can come up with.

https://www.cumminsgeneratortechnologies.com/en/products/stamford/hc/

For further contact information go to this place:

https://www.cumminsgeneratortechnologies.com/en/contactus/

Hope this is helpful....

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Generator for Pumping Station

07/09/2013 1:18 PM

Dear Mr. rajnathr,

You have NOT mentioned, the Type of Motor used, and it has a ROLE in the magnitude of STARTING CURRENT, for the Motor. I am sure you will be using Slip-Ring Motor for the capacity of 375 KW.

Normally the Bigger size Motor is started first and then smaller Motor or other loads put on. Since only one Pump starting with other load of 25 KW, (45 Amps.) and for 375 KW, the Current will be 680 Amps., and the Power Factor is considered as 0.8.

TOTAL LOAD will be 725 Amps, But the STARTING CURRENT LOAD is applicable for 375 KW, (Obviously the 375 KW Motor Type, should be SLIP-RING type) and you should USE/SELECT "AUTO SLIP RESISTOR" Type STARTER, only to limit the starting Current with in 2.4 Times the FULL LOAD CURRENT and then only Starting Current will be contained to 2.4 Times the Full Load current, that is 1632 amps.

When one pump running and other load is 25 KW, the current will be 725 Amps, under this condition, when you start the second pump, the Momentary Load will be 725 + 1632 = 2357 Amps.

1200 KW DG set i.e. 1500 KVA Set will be SUFFICIENT, if the Motor is Slip-Ring Type.

If is Star-Delta Motor is used, the DG Set should be of 1500 KW or 2000 KVA., which will be MORE COSTLY

DHAYANANDHAN.S

Register to Reply
Anonymous Poster #1
#7
In reply to #6

Re: Generator for Pumping Station

07/09/2013 4:18 PM

Try reading the question.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #7

Re: Generator for Pumping Station

07/10/2013 4:34 AM

Dear friend,

Pl. enlighten your thinking and what you want to convey by saying "Try reading the question." remains silent.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dhayanandhan (2); nobodysomebody47 (1); rajnathr (1); RobertMc (1); simonsd (1); Tornado (1)