Anonymous Poster #1

Earth Fault in VVVF Drives

07/09/2013 1:14 AM

VVVF drives are used for hydraulics pumps and its circulation motors. But after some duration of operation drive is tripping on earth fault. we checked throughly for any problem in motors and cables, but both things found normal. After resetting fault operation found normal. This porblem is repetative and comes once/twice a week. What we have to do? Drive to motor cable length is approx 125 Mtr and output choke is not introduced in the drive.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Earth fault in VVVF Drives

07/09/2013 2:27 AM

For that long of a run, it seems that line output reactors should be present. How that might affect the fault indications, I'm not sure.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Earth Fault in VVVF Drives

07/09/2013 3:37 PM

Talk to the drive manufacturer or look in the drive manual or application notes, the lack of a choke may be your problem.

__________________
jack of all trades
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Earth Fault in VVVF Drives

07/09/2013 4:08 PM

Agreed. Capacitive coupling on the output conductors is the usual suspect. A reactor at the very least is indicated, a Sine Filter is a better idea, this may be an indicator of other problems as yet unseen, such as voltage spikes at the motor insulation that are going to lead to motor winding failure in relatively short order.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Commentator

Join Date: Mar 2011
Location: off the beaten track, not quite whoop whoop nor humptydoo
Posts: 57
#4

Re: Earth Fault in VVVF Drives

07/09/2013 10:11 PM

Just checking... is the drive tripping on an earth fault, or do you have ELCB that is tripping? Are you using generator or mains supply?

__________________
Everything works out in the end, just not neccessarily how you want
Reply
Anonymous Poster #1
#6
In reply to #4

Re: Earth Fault in VVVF Drives

07/10/2013 7:21 AM

No ELCB is installed. ABB make ACS-550 Drive is used for this application.

Main grid supply is used for the same. There is no generator power back up for the same.

Reply
Active Contributor
Canada - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Sep 2008
Location: Nova Scotia, Canada "Canada's Ocean Playground"
Posts: 20
#5

Re: Earth Fault in VVVF Drives

07/09/2013 11:10 PM

Just checking to see what type of drive you have as well are you using O-Flex or similar cable? I ran into similar problems caused by harmonics in a machine that had standard wiring used. The harmonics would build up enough to trip the drive on "Buss Over Voltage" as well as when running at over speed (90 Hz) the drive would have so much harmonic current "Current Overload".

Hope this helps...

__________________
TheCanadianBear
Reply
Anonymous Poster #1
#7
In reply to #5

Re: Earth Fault in VVVF Drives

07/10/2013 7:25 AM

Drive is of ABB make ACS-550 model. Cable is general pupose stranded cable.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Chook (1); jack of all trades (1); JRaef (1); TheCanadianBear (1); Tornado (1)