Thermometer Mandatory or Not?

07/09/2013 4:54 AM

Is thermometer required for

250 kVA ONAN Type ( Oil cooled ) 11000V/433V, delta/star grounded aluminum wound transformer ?

and whats the maximum temperature limit at 70-80% load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Thermometer mandatory or not?

07/09/2013 6:07 AM

What does the specification say?

What does the transformer manufacturer say, given the ambient temperature (which isn't stated in the original post)? How did the phone call go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Thermometer Mandatory or Not?

07/09/2013 8:19 AM

Thermometer or over temperature trip? I wouldn't say mandatory, but I would say advisable.

As PWS has said, speak to the transformer manufacturer.

I've fitted quite a number of distribution transformers, some had O/T trips, and some didn't. It depended on what was specified for the location.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Thermometer Mandatory or Not?

07/09/2013 4:47 PM

A thermometer would be good for reading the oil temperature.

An over-temp trip would be good for saving the transformer.

But, see #1 and #2 above, They're the experts. I'm just a troll.

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#4
In reply to #3

Re: Thermometer Mandatory or Not?

07/10/2013 10:53 AM

On such a small unit, many times they do not have a thermometer (AL) or trip (ALR). Since it is oil filled it is most likely a 55/65 (degree Celsius rise over ambient)Ambient is normally 30/40 Cesius, so you are looking at a maximum of 105 Celcius. Alarm is frequently set at 105 with a trip at 120 Celcuis. Note that this is average top oil temperature and the hot spot is even higher. The nameplate should give the temperature rating. If it doesn't have a device, just use a point and shoot IR probe, they can be purchased for less than $20 and are fast and just as good as a gauge. The temperature can seem really hot and can cause a burn on touch. If you can hold your hand on the unit indefinitely at the area of the top of the oil on the tank which is well below the top of the transformer you do not have a problem.