3 Phase 4 Wires System Can Apply 3 Poles CB?

07/29/2013 9:21 PM

3phase4wires system can apply 3 poles CB?

My customer told me it will have 4 wires(LV source) supply to me, however the CB in the drawing is 3 poles and the load is not motor.

Please help, I'm getting confuse now.

Thank alots.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 3phase4wires system can apply 3 poles CB?

07/29/2013 9:32 PM

You're not the only one.

Can you send copies of the schematics, plans, specifications, and purchase order to us for review? Oh, and specs for the CB's?

What color are the wires?

What gauge are the wires?

What polarity are the poles?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 3 Phase 4 Wires System Can Apply 3 Poles CB?

07/29/2013 11:27 PM

Yes, but there are cases in which a 3P+N CB is needed.

It might help more to say what the load is, rather than what it is not.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#3

Re: 3 Phase 4 Wires System Can Apply 3 Poles CB?

07/30/2013 2:47 AM

If you are not having secondary backup power (DG supply), then you can provide three pole breaker without switched neutral instead of 4 pole switched neutral breaker. The idea is to avoid providing multiple neutral earthing points.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4

Re: 3 Phase 4 Wires System Can Apply 3 Poles CB?

07/30/2013 12:21 PM

I would expect the norm to switch the "hot" three wires and not the neutral. If the contactor failed to engage the neutral, unpleasant things could happen when the load was unbalanced. As every one else said, special cases do occur.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5

Re: 3 Phase 4 Wires System Can Apply 3 Poles CB?

07/30/2013 4:28 PM

We may be getting too complex here assuming a neutral wire. Customer's can relay information in strange ways. Your customer, if like half of mine, may not be very well versed in industrial electricity and may be counting the ground as a "wire" not realizing he is setting off alarm bells because we are assuming that is a neutral conductor. So maybe you are getting three phases and a ground conductor (earth) - quite a normal situation. Check with your customer and verify what the fourth wire is.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#6

Re: 3 Phase 4 Wires System Can Apply 3 Poles CB?

08/02/2013 5:31 AM

Basically, for LV side, there is always come with 3Phase 4 wire where the 4th wire is a neutral. There are other method that we used for these situation. First you can use 4 pole MCCB which mean 3 phase + Neutral or you can used a 3 Phase MCCB with a neutral link at the side of the MCCB.

The neutral wire will be connected to the neutral link. But make sure that this is not for generator power system. For normal load it is o.k.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

lyn (1); NotUrOrdinaryJoe (1); Pattabhiraman (1); Phys (1); Simon Wan (1); Tornado (1)

Previous in Forum: CT Design   Next in Forum: Detroit S60 Engine with Kohler System Controller 550

Advertisement