Hello, Yesterday our electrical contractor doing performance test for the water pump with 75kW electric motor supplied by Portable generator. At first the Power Meter Reading show negative kW, power factor is leading and not balanced and it turns out that the wiring is wrong. After check and rewiring we run the pump again, now all the power factor is lagging but the values is very low 0.5. I check with 3 phase multimeter, the reading between kW and kVAR is reversed with Power Meter reading. Me and contractor have debate about this matter, they dont trust our multimeter but our bargaining position is better because the contractor can not provide the 3 phase multimeter for their own. I attach picture for the phasor reading in Power Meter, is it normal for 0.8pf motor to have these value? Is it possible that portable generator Power Factor affecting the motor power factor because portable generator nameplates shows Power factor is 0.8.