Motor Protection Settings:- Thermal Time Constants in REM 615

08/02/2013 12:49 AM

I am working out motor protection settings for 700kW motor, relay is ABB make REM 615, in thermal overload protection we have to set three different time constants viz. Time constant start, Time constant normal and Time constant stop. I need guidelines on how to set them.

In motor manufacturer datasheet cetain time constants are given which are as:

Thermal copper time constant - 9 min

Thermal time constant (long term)- 25 min

Thermal time constant for cooling down (standstill)- 175 min.

Kindly help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Moto protection settings:- Thermal time constants in REM 615

08/02/2013 1:11 AM

Basically, the first three you gave match in respective order the second three.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#2
In reply to #1

Re: Moto protection settings:- Thermal time constants in REM 615

08/02/2013 2:04 AM

but setting the Thermal time constant start= 9min (540 s) will result in tripping since the starting current = 6 x In and starting time is 31 Sec, according to trip curve given in technical reference manual of REM 615

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Moto protection settings:- Thermal time constants in REM 615

08/02/2013 3:16 AM

How did the phone call to the motor manufacturer go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Motor Protection Settings:- Thermal Time Constants in REM 615

08/03/2013 1:35 AM

Try the above settings.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Motor Protection Settings:- Thermal Time Constants in REM 615

08/05/2013 4:52 AM

In my opinion 9 min it is rotor locked [short-circuit]thermal constant, 25 min it is for overload estimation temperature and 175 it is for cooling -in standstill position-if two or more startings are involved.

If motor parts are heating the temperature rise is : DT=Tconductor-Tambiant=Tinf*(1-exp(-t/Tk).

For instance, if stall time[from the motor catalogue] is t=10sec and maximum DT=130-40 [for class F insulation and 40 dgr.C ambient] then Tinf1=90/(1-exp(-10/60/9))=4905 dgr.C[if the motor will stay in locked rotor position infinite time!]Then for 5 sec start time DT=4905*(1-exp(-5/60/9))=45.2 dgr.C.

If we want to know what could be the temperature when the motor is stopped and not energized after t3 sec. DT=Tload*(exp(-t3/Tk3) If Tload=Trated=90 and t3=1 min then DT=90*exp(-10/175)=85.

In usually load condition[rated]Tinf2 has to be 90[130-40] then for an overload of x% Tinf2x%=Tinf2*(1+x%/100)^2 and DTx%= Tinf2x%*(1-exp(t2/Tk2)). For instance x%=30,t2=1 min.

DT30%=90+90*(1.3)^2*1-exp(-1/25))=96 dgr.C

See also:

https://www.selinc.com/WorkArea/DownloadAsset.aspx?id=3690

__________________
Julius
Register to Reply