Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/15/2013 12:34 PM

Hi Users

Just wondering what should be the main considerations when using an existing feeder (fused switch) as an emergency incoming supply (from a generator) on an existing distribution board, providing the following assumptions are made:

- the existing 200A fused switch and cabling to it is adequately sized

- the load to be supported doesn't exceed the fused switch size

- we can accept a short outage between loss of mains and availability of emergency supply

- we will have an interlock arrangement preventing mains and generator supply for simultaneously supplying the distribution board

- a phase rotation instrument will be installed to ensure correct phase orientation

Any help would be greatly appreciated so that I ensure the designers are kept on their toes!

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Using existing outgoing feeder as an incomer (415v Distribution Board)

08/15/2013 1:10 PM

Yes it can be done.However the Generator rated current to be less than 200 A( fuse switch rating)

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/15/2013 2:38 PM

Are you worried about code requirements and insurance coverage in the event that the building burns down?

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/15/2013 8:03 PM

quote ramvinod "Yes it can be done. However the Generator rated current to be less than 200 A( fuse switch rating)"

Why would you need that requirement. The 200 amp fuse would limit the load on the generator. Suppose you have a large motor that requires175 amps FLA. The starting amps may be 3 times the FLA and the generator might not be able to supply the LRA. Do you have a reason for the limitation?

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4
In reply to #3

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/15/2013 11:48 PM

It is only precautionary advice to restrict the load to 200 A.There is no other reason.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#5

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/16/2013 12:02 AM

The following should also be provided a) Earth fault protection for the D.G source. b) The changeover arrangement shall be of four pole type. c) overload protection for the D.G to be provided.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/16/2013 3:11 AM

d) in order to protect the cable, the 200A fused switch is presently at the wrong end of it. Presumably this will be corrected during the re-routing exercise?

As in all things, local electricity regulations apply. In the UK, consult British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#7

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/18/2013 7:19 AM

...if this is a USA installation, it may qualify under the tap rule, NEC 240.21

__________________
BSEE but always learning
Reply
Participant

Join Date: Aug 2013
Posts: 1
#8
In reply to #7

Re: Using Existing Outgoing Feeder as an Incomer (415v Distribution Board)

08/18/2013 8:25 AM

It's for a UK installation....thanks