Why Is Delta-Wye Transformer Used In Distribution Transformer
08/15/2013 11:39 AM
Hi guys.
would like to know why does most distribution transformer uses delta-wye connection. What are the reasons behind it.. and why are most instrument transformers wye-wye connected?
Please advise !
Thanks !
__________________
There is no limit towards how much one can learn.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/16/2013 4:59 AM
Dear Mr. RAMConsult,
During our college study days, my Professors have taught that STAR- CONNECTION - because of 120 Degree, Phase Angle the 3rd Harmonics are totally nullified. But your point is Delta connection nullifies 3rd Harmonics. Pl. clarify.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/16/2013 12:14 PM
Mr. Dhayanadhan:
In a delta the third harmonic currents circulate
within the delta and turn into heat thereby increasing the loading on
the cooling system.
Wye connections are different because of the neutral point
(grounded/ungrounded), where it appears (Primary/Secondary), and whether
the source is grounded or not, making a total of sixteen different
scenarios (which I will not bore you with, for more info see the
Westinghouse T&D Handbook).
To simplify(?), for certain wye-wye grounding configurations, the
third harmonic current has no choice but to pass through the
transformer, appearing in the phase to neutral voltage but not in the
phase to phase voltage (which is probably the case that your Professors
taught you). If there is a delta tertiary then the third harmonics will
be suppressed regardless of either wye windings' grounding.
In general from ibid "..The paths permitting the flow of third
harmonic currents are determined by the system and transformer
zero-sequence circuits..." (which are even more arcane (mysterious,
secretive) than the above discussion!)
__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/19/2013 12:28 PM
Dear Mr. RAMConsult,
Thank you very much for your reply. Indeed a good amount of explanation given by you, which will help to up-date the knowledge. What we studied in the college and what we see in the Industry varies some times.
You have mentioned "...........making a total of sixteen different
scenarios (which I will not bore you with, for more info see the
Westinghouse T&D Handbook)."
I never feel bored, and I want to know more about the 6 different Scenario. I also request you to give me the web-link where I can down-load the Westinghouse T&D Hand Book or you can send to my cr4 personal messaging system.
Thanks,
DHAYANANDHAN.S
Note: Sorry for delay in acknowledging your reply.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/15/2013 8:36 PM
The various types of transformers are used for many different reasons. Some economic, some may be phase sequencing, along with the many other requirements a transformer is used for.
Unfortunately for you, you have to research why they are used in each circumstance.
Tell me why you think Yy is used on MV instrumentation or why ∆Yn is used for MV/LV distribution? I'll help if you help yourself.
__________________
The reports of my death are greatly exaggerated.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/15/2013 10:44 PM
Wye xformers are used in 4wire systems for increased current capacities as their leg to leg potential value is derated by 1.713. As the neutral is center tapped the unbalanced loads are a non issue. Delta xformers are better for transmission as their leg to leg potentials are higher to compensate for I2R losses. Ie 120/208 in commercial and 120/240 in residential.
__________________
Don't believe everything you read on the internet just because it's qouted by a famous person. Benjamin Franklin
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/16/2013 4:50 AM
3-wire delta is cheaper than 4-wire wye, not just for cable costs, but narrow trenching if its underground, so you would only use 4-wire if you have a currently carrying neutral.
Re: Why Is Delta-Wye Transformer Used In Distribution Transformer
08/16/2013 8:37 AM
The type of transformer connections (wye or delta) has each own individual and unique characteristics.. They are connected / terminated depending on the needs or as governed by its intended application. Intended application therefore will determine how, to take advantage of this inherent and fundamental connection characteristics..
You need to study to better understand the basic theories relating to transformers.
Good Answers: