Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/14/2013 8:15 PM

Hello all,

I have simulated (both in software and experimentally) inter-turn winding short-circuit faults on a single-phase transformer working as a stand alone unit. Then I have into the harmonic content of the no-load current as a means to detect the fault. The trend I have got is as follows:

Under the fault, only the no-load current's fundamental component showed an increase while all other harmonics (3rd, 5th, 7th etc) remained almost unaltered. Thus the THD of the no-load current got improved i.e. decreased under the fault.

Why is this trend so ? It would be great to get some feedback from your end.

Regards,

Shantanav

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/15/2013 3:21 AM

Is it because the shorted turn behaves as a low-pass filter?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/15/2013 9:27 AM

The shorted turns are probably acting as a tertiary winding.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Aug 2013
Posts: 2
#3
In reply to #2

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/15/2013 2:56 PM

Thanks for the suggestion. I agree, the shorted turns definitely act as a tertiary winding whose power is being fed from the primary and the power is being dissipated in it as heat.

But how is it related to the increase of only the fundamental component of the no-load current ?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/16/2013 12:50 AM

The shorted turns will be adding load which as you say in dissipated as heat. Acting as a tertiary winding the shorted turns will reduce harmonics.

The end result will be a lower percentage of the loading will be the high order harmonics. If I'm reading your question right it is the percentage difference that is concerning you.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#5

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/16/2013 1:50 AM

Because to generate harmonics - you need a NON-LINEAR ELEMENT. Your do not have one - thus you have no added harmonics.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#7
In reply to #5

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/16/2013 8:16 AM

In my experience using high frequency testing in transformers, the sinusoidal signal waveform will be damped and its duration shortened when a winding short is present. It was also noted that even a partial winding short condition (not completely shorted winding) was detected, presented by a slightly dampen condition..

__________________
vsar
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Detection of Inter-Turn Winding Short-Circuit Fault in Single-Phase Transformers

08/16/2013 7:50 AM

May I inquire as to why you are using your time up doing this? It would appear to be something that is seldom if ever needed.

In a practical environment, if a transformer has shorted windings or a short, the effects are usually obvious and a inductance meter reading compared to an identical unit (or note the both winding inductance values before installation) will quickly show if the unit is faulty or not and could also indicate the reason - if you wish to know why.

Unless you are into making the transformers up yourself (I've done that but many years ago and its not something I feel a need to repeat personally), the information as to why it's not working is often not very useful - it's broke, replace it....

Having a temperature sensor on the Trafo might have indicated an overload condition before permanent damage was done, which may point to something taking too much current and causing overheating, which probably indicates that the "follow-on" circuit has no method of detecting such errors = bad design.

In all the years in electrics and electronics that I have had (1955 to today), I have never needed or thought to have needed such software.

A good Multimeter was enough.

Can you demonstrate here for us just what practical advantages you will be achieving with this work?

Thanks for your answer.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Andy Germany (1); olehwi (1); PWSlack (1); Shantanav (1); TonyS (2); vsar (1)

Previous in Forum: Automatic Change Over Current Limiter   Next in Forum: Why Is Delta-Wye Transformer Used In Distribution Transformer

Advertisement