Selecting Conductor/Wiring Size

08/20/2013 4:02 PM

Hi guys, was just getting rusted and duobtful.

I've got a Rotor Lock Ampere of 75A motor, what's the factors in selecting right size of conductor to use. How is the sizing done? What things to consider?

Any rule of the thumb to recommend?

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Pathfinder Tags: wire sizing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: SELECTING CONDUCTOR/WIRING SIZE

08/20/2013 4:16 PM

About the only time you would use the locked rotor amperage of the motor was if the motor was driving a fire pump.

What is normally used to size these conductors is the full load rating of the motor, which is impossible to determine from the locked rotor rating unles the design of the motor was know (the name plate should have the NEMA design code on it).

Where I am from, we would size motor conductors at a minimum of 125% of the full load rating of the motor. But, that is just where I am from.

Check the codes and standards in force where this will be installed.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #1

Re: SELECTING CONDUCTOR/WIRING SIZE

08/21/2013 1:34 PM
  • "Where I am from, we would size motor conductors at a minimum of 125% of the full load rating of the motor. But, that is just where I am from."

Technically that is incorrect (because I can see you are in the US of A). We are required to size conductors per the charts in the NEC, article 430, not the nameplate FLC on the motor. Most people do not see that clearly and ASSUME those charts are just guidelines for when you do not know the motor nameplate FLC, but in reality, those are hard and fast rules! The only time you use the FLC is when you KNOW that the FLC on the nameplate is actually HIGHER than the appropriate chart value. If it is lower, you MUST still use the chart value.

But to Noudge79, Nof60 is still very much correct in stating that how you size conductors is strictly based on local codes and regulations where the installation is happening. You do not state where you are, so we cannot help. You indicate that you have an interest in the Philippines, but for all we know you are a Philippino American in Podunk Alaska, in which case the NEC would apply to you. But if you are in fact located in the Philippines, then I don't know what your local code says, you have to look that up yourself.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #7

Re: SELECTING CONDUCTOR/WIRING SIZE

08/21/2013 3:51 PM

Hey JRaef... I am not in the US by the way, I am in Canada, where we use the nameplate values.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: SELECTING CONDUCTOR/WIRING SIZE

08/20/2013 4:18 PM

Yes,

Do a search for wire sizing on the internet, or consult NEMA or NFPA, or the local code book, or a text book

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Selecting Conductor/Wiring Size

08/20/2013 4:46 PM

Fortunately, this is the most popular topic in the Electrical Engineering section. Try "Search this Forum" on the right.

Bedtime reading of British Standard 7671 would be a good starting point, as has been pointed out here countless times before. So often, in fact, it has become tiresome.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#4

Re: Selecting Conductor/Wiring Size

08/20/2013 6:45 PM

As others say, wire rating is for continuous load. And the rule is the circuit breaker protects the wire. Motors require protection via some electrical switch that prevents the smoke from being released. How long of a run is the motor power wiring? I'm assuming this is for home owner construction. How far from the main service entrance panel is the motor connection? Is your service 100amp, 200, 400? How close are you to the low voltage transformer, that your main service connects too. Think in terms of lengths, wire sizes, during surge current type loads. Do you see incandescent light bulbs dim? This indicates IR drops in your power system.

LRA is to me typically 7-9 times run current.

So I'm guessing your running a 10amp motor. And estimating 1.5HP@120V, or 3HP at 240V. If these are out on a long extension cord, powering a motor operated machine, for example running a cement mixer, the IR drop needs to be addressed. The IR drop at connectors, duplex, with male plug can get mighty hot. Are you fighting this sort of motor problem with line loss?

__________________
ignator -
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#5

Re: Selecting Conductor/Wiring Size

08/21/2013 12:05 AM

See CR4

How to Calculate Locked Rotor Current 11/24/2009

This is covered there

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#6

Re: Selecting Conductor/Wiring Size

08/21/2013 12:51 PM

If you're just looking for a conductor that will carry / survive a 75 amp locked rotor then you are looking at 6AWG to 3AWG depending on the wire and temperature rating.

I hope you don't have to run a long way because that size wire is $$$$$$$$

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#9

Re: Selecting Conductor/Wiring Size

08/21/2013 9:51 PM

If your looking for a fast rule of thumb here it is ( not to be used by anyone to engineer a system for sure, but for trouble shooting only).

1.5 amps per HP; gives you the amp rating of motor to 10 HP. Then reduce to 1.3 amps per after. 3 Phase motors @ 480 volt. 3 conductors in a raceway or conduit.

12 Gage THHN is 20 AMPs

10 Gage THHN is 25 AMPs

#4 is good to about 85 amps.

Typical 100 amp service to homes is feed with #2 THHN copper wire. Just for reference.

Covers most motors used in smaller industries. But if you really need to figure this up and have not done voltage drops and such for a wiring run, you need to seek out expert advise and direction. That can be on site to see what your trying to do and adivse properly.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#10

Re: Selecting Conductor/Wiring Size

08/22/2013 9:10 AM

Just look at the motor name plate and see what is the FLC rated and get a conductor that can carry 1.5 time of the motor FLC or a conductor 2 x time the motor FLC rated.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

fixitorelse (1); ignator (1); JRaef (1); lyn (1); North of 60 (2); old salt (1); Original_Macgyver (1); PWSlack (1); Simon Wan (1)