Delta PLC High Speed Counter

08/29/2013 4:50 AM

hi

i am using dvp24es2.

i am using C251 and C253 hi-speed counter for 2-phase 2 inputs sucessfully but when i add C233 and C234 hi speed counter for more input count, compiler gives an error.

i dont know why?

i need to write a program to read 4 high speed counters.

thank you

Register to Reply
Pathfinder Tags: PLC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Delta PLc High speed counter

08/29/2013 6:53 AM

Consider the possibility of the counter function requiring two contiguous bytes of memory. What happens when C234 is changed to C235, for example <rhetorical question - NNTR>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: Delta PLC High speed counter

08/29/2013 11:22 AM

Good eye! I saw the 251-3 skip, but the possible implication didn't register. I hope the OP does reply, so that we can know if this turns out to be the issue.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3

Re: Delta PLC High Speed Counter

08/30/2013 7:40 AM

There are 2 type of High Speed counters: Software & Hardware types.

C251 & C253 are hardware HSC, using X0,X1 & X2,X3 respectively.

C233 & C234 are software SHSC using X4,X5 & X6,X7 respectively.

You cannot use the same input for 2 different counters. This will give syntax error when executing DCNT instructions.

Check that you did not double designate in the firdt place.

You should download the Operational manual-programming for the DVP-ES2_EX2...pdf. This will show you how to check the errors as well on the limitations for using the counters etc.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2015
Posts: 2
#4

Re: Delta PLC High Speed Counter

04/30/2015 5:37 AM

Suggest an industrial automation website to us, may be can help you, there are many delta plc online sale, the most importance is customers can get a technology support 24/7, even weekend,

FastToBuy.com

Register to Reply Off Topic (Score 5)
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DavidJohnLee (1); LAA_Lucke (1); PWSlack (1); Tornado (1)

Previous in Forum: Pneumatic Control   Next in Forum: I Thought I Knew Thermocouples...But

Advertisement