Anonymous Poster #1

Restricted Earth Fault Relay

09/04/2013 1:27 AM

Hi All,

While trying to understand more about REF protection for transformer I came across this statement.

"As the winding fault position moves towards the neutral, the magnitude of the current seen on the primary rapidly decreases and could potentially not be detected (limiting the amount of winding which can be protected)".

I didn't understand how.? Can any one help me in understanding..?

I have a few doubts also (it may sound stupid).


1. I am from India in our area we use separate CTs for REF and Stand by earth fault(SBEF) + OC protection. i.e in 5CT method 5 nos PS class CTs (3 in Phases 2 in Neutral) along with 4 no 5P10 class CT ( 3 in Phases 1 in Neutral for SEF+ OC. We use separate relays for REF, SEF, & OC For SBEF we use CDG relay. My query is that is it possible to use only one type of (PS Class) CT for all the protections..? Is it possible to use a single relay(if the relay is capable of) to incorporate all the protections.?

2.Can I use Class PS CT for OC or SBEF protection or for metering purpose.?

3 When a fault occurs between one phase and the ground will the fault current travel back from the ground through the neutral to the fault point..? (using the concept that current flows only in a closed circuit)
For faults outside the Zone SBEF will operate, REF will not operate.
For Faults inside the Zone the REF will operate the When an earth fault happens inside the zone will the CT provided for SBEF sense the fault current. (i mean when a current flows in the primary (neutral) a proportional current in the secondary)?

Please clarify my doubts.It may sound silly or stupid but I would like to know why and how.

Thanks in advance

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Restricted Earth fault relay

09/04/2013 3:19 AM

<...As the winding fault position moves towards the neutral, the magnitude of the current seen on the primary rapidly decreases and could potentially not be detected (limiting the amount of winding which can be protected)....>

In the limit of this movement, the neutral is connected to earth as a fault. At this point, no change in the primary current might be detected. As the earth fault moves from neutral towards the phase, the fault current increases and becomes more detectable.

<...When a fault occurs between one phase and the ground will the fault current travel back from the ground through the neutral to the fault point..?...>

No. It flows from the fault point through ground back to the star point of the secondary of the last transformer upstream until such time as (a) circuit protective device(s) operates to disconnect the supply from the fault.

<...For Faults inside the Zone the REF will operate the When an earth fault happens inside the zone will the CT provided for SBEF sense the fault current....?...>

That is correct, however it is a prerequisite that all CTs and protection circuits are connected and working correctly for that to happen, such proviso being inherent in the correctness of the postulate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
5
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Restricted Earth Fault Relay

09/04/2013 9:27 AM

I will try to answer your queries one by one!

First, you do understand that current is voltage / impedance. Do you?

In a transformer winding, voltage or EMF is proportional to the number of turns in the winding (Recall: EMF = 4.44 (phi) (f) (N) volts). And, near the neutral end of the winding the voltage is zero and at the terminal, the voltage is 100%. In between, the voltage is in proportion to the number of turns involved. So, as the fault is nearer to the neutral end of the winding, you have less number of turns and thus less voltage or EMF to drive the current. Thus, when an earth fault happens close to the neutral terminal in a winding, the fault current magnitude will be lesser. Particularly, in impedance earthed systems, the fault current for a fault in the winding, close to the neutral, is so low that it can go undetected by any conventional earth fault relay.

But, the above is true only in star connected windings. In delta connected windings, it will be minimum in the mid-point of the delta, maximum at both the extreme ends and proportional in between.

1. I am also from India. There are two methods of REF connection. A 4 CT REF Connection & a 5 CT REF connection. If the neutral is distributed & you anticipate a phase unbalance, then in a 4 CT REF Scheme, if the unbalance current is more than the relay setting, the REF Relay might trip spuriously, causing panic. In a 5 CT REF Scheme, the 5th CT is the distributed neutral, takes care of this unbalance and thus the REF Relay setting can be made more sensitive. If your neutral is not distributed, you may go with a 4 CT REF only, as there would not be any unbalance current from the load side.

And, to the second part of your query, please note that Class PS CTs are bulky and costly, due to higher knee point voltage requirements & lesser magnetisation current requirements. Now, if you connect all the protective relays to the Class PS CT only, it would further increase the burden of the CT and would make it further bulkier & costlier. So, to economise, you opt for Class PS CTs, only where it is mandatorily required, such as in differential & in REF Schemes and choose a relatively cheaper & smaller Class 5P10 CTs for all back-up protection requirements like O/C, E/F, S/B E/F, etc.

Today, you can very well get a comprehensive numerical feeder protection relay, incorporating all the above functions and much more. Please search the net for further information on this.

2. Refer (1) above. You may very well use Class PS CT for OC, EF Protections & metering, but that would be unjustifiably costly. Also, the relays & meters have to be designed for a higher short time withstand current rating.

3. I strongly suggest you to kindly brush up your fundamentals, such as Kirchoff's Laws. Yes, when a phase-to-ground fault occurs, the fault current does travel from the SOURCE - to - the faulted point -and back to the source, through either the natural ground or the grounding conductor (depending upon the network type, either TT or TN).

Yes! For earth faults outside the zone, SBEF will operate, but after a time delay, base on your current settings, your time settings, the magnitude of the fault current as well as the above settings in the main EF Protection relay and on the proper co-odination between the two. For these external faults, REF will not and SHOULD NOT operate.

For earth faults inside the zone, only REF should operate.

For faults within the zone, REF will definitely operate, if the connections & settings are alright.

When an earth fault happens inside the zone, the CT provided for SBEF will definitely sense the fault current, if this CT is located in the fault current path. But, the SBEF will not operate for this fault, as this is time-delayed. As REF is instantaneous, it will clear the internal fault, immediately.

Just in case, the REF fails to clear this internal earth fault, the SBEF will definitely clear, albeit with a time delay. (i.e.) the SBEF will act as a back-up for the REF and that's how it got its nomenclature too "STAND BY EARTH FAULT" Relay.

Hope it is clear now.

And, don't worry that your questions are silly. They are not. Even, if they are don't bother. We all too learnt by asking such silly questions only.

Reply Good Answer (Score 5)
Anonymous Poster #1
#3
In reply to #2

Re: Restricted Earth Fault Relay

09/04/2013 3:12 PM

Thanks you for giving such a good reply and for sharing your valuable knowledge in this subject.

While searching in google for the answer for my doubt no 2, I got this

"If you use a PS class CT for metering, the metering will not be accurate and at time of a heavy fault, the meter will burn out.

A metering CT must be accurate between zero load and full load and must saturate above full load. Protection class CT must not saturate until the specified level."

The link is <http://in.answers.yahoo.com/question/index?qid=20081006072730AAQq6Zh>

Can it be true.?

One more thing

Should the CT secondary used for REF protection must be of 1 A even in the case of indoor substations. I have seen few drawings in which secondary rated ampere for the CT's used for REF is mentioned as 1 A. Is it wrong to use a 5A rated secondary. (usually all the CT secondary used in outdoor substation is of 1 A rating in which lengthy cabling is required, but for most of the CT's located inside the panel the secondary is rated as 5A). Is there any particular reason or any rule for that..?

Once again thank you electricalexpert65 and PWSlack for your reply.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Restricted Earth Fault Relay

09/04/2013 8:49 PM

i) Yes! If either a protection class CT like 5P10 or Class PS is used for metering, the meters must have a short time rating pertaining to the Accuracy Limiting Current else they would burn out. This is what I have mentioned in my answer too.

Yes, a metering CT must maintain its accuracy between 100% to 120% of rated primary current (and, NOT from zero load to full load, as mentioned by you. Even at 20% rated current, the ratio error of a metering CT would double and at 5% rated current, it would quadraple). Also, a metering CT need not saturate just above its rated primary current. The saturation level of a metering CT is denoted by a parameter called ISf (Instrument Security Factor) of FS (Factor of Safety), which is 2 or 5 or 10, but generally it is 2.

Also, it is agreed that a protection class CT like 5P10 must not saturate until the specified level. The specified level is more technically known as the ALF (Accuracy Limiting Factor). And, it must be remembered that the ALF does not specify that the CT would exactly saturate at the ALF current level; no, it is not! ALF just implies that the given protection class CT would maintain its limits of composite error at least upto the ALF current. It may saturate anywhere AFTER the ALF current.

And, for Class PS CTs, this ALF is more precisely calculated as the Knee Point Voltage, duly taking into consideration, the fault current magnitude (as reflected at the secondary terminals of the CT), the CT secondary winding resistance, the connected burdens (load burden plus the lead burden) and a safety or cushioning factor.

It is not necessary to go for a 1A Class PS CT for indoor mounted CT & REF too. The CT & Relay can be 5A. There is no hard & fast rule on that.

Reply Score 1 for Good Answer
Anonymous Poster #1
#5
In reply to #4

Re: Restricted Earth Fault Relay

09/05/2013 5:47 AM

Thank you once again...

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6
In reply to #2

Re: Restricted Earth Fault Relay

09/05/2013 7:18 AM

Sir, Very good answer. You have explained very clearly. Regards.

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#7

Re: Restricted Earth Fault Relay

09/05/2013 7:55 AM

EE65 has explained clearly and there is not much to add. However I thought I will try to make the answer more complete.

Is it possible to use a single relay(if the relay is capable of) to incorporate all the protections.?

Yes, It is possible with current generation numerical relays to programme all protections in one relay. However protection philosophy mandates that all eggs should not be placed in one basket and hence redundancy / back up protection is always included. This backup protection (if sound engineering practises are followed) will have complete redundancy like separate CT's, Control schemes etc so that no single element failure ( CT, PT auxiliary supply etc) will lead to non clearance of the fault. In fact even with the latest generation relays provided as the first line of protection, the humble electro mechanical relay like CDG will be preferred as the backup redundancy protection.

For Faults inside the Zone the REF will operate the When an earth fault happens inside the zone will the CT provided for SBEF sense the fault current. (i mean when a current flows in the primary (neutral) a proportional current in the secondary)?

REF is zone (unit) protection and standby earth fault is non directional unbound protection. By protection philosophy, unit protections are tuned for sensitivity and instant operation for fast clearance of internal faults. However for backup protection scheme, time and current grading is followed to allow for clearance of fault by the upstream breaker closest to the fault. Therefore even if the standby protection is primed for operation for any faults downstream (including within the zone protection of REF), sufficient discrimination is provided in the settings so that the principal protection relay clears the fault.

Reply Score 1 for Good Answer
Anonymous Poster #1
#8
In reply to #7

Re: Restricted Earth Fault Relay

09/06/2013 2:35 PM

Thank you for replying..

Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#9

Re: Restricted Earth Fault Relay

09/07/2013 2:00 AM

Anonymous your question was not at all silly but I would like to ask experts here a silly question.

If a fault happen outside the REF zone then still the fault current will travel from the transformer neutral, then how REF will not sense that current?

I have seen people don't do any co-ordination for a REF (as its instantaneous). For a scheme with bus section, if a REF operates that will not activate the lock out relay and allows the auto change over to take place. But if a SBEF will operate then 86 will operate and hold the auto change over. So it is very important for REF should not operate for a fault outside the zone.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#10

Re: Restricted Earth Fault Relay

02/08/2014 10:58 PM

On this subject I would like to add one point. For transformer REF relay , the relay is provided in the LT side Panel and the relay is made to trip the LT side breaker. But not the HT side breaker. Actually it should isolate the source of supply to the transformer ( HT side).But I notice even the leading Switch board manufacturers provide the tripping only LT Breakers. It should be corrected.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #10

Re: Restricted Earth Fault Relay

02/09/2014 2:05 AM

There is an economical reason in locating the REF Relay in the LT Panel. Because, in distribution transformers, the LV winding is generally star connected and as such you need three phase CTs & one neutral CT for REF protection of the LV winding. If you place the REF relay in the HV Breaker, then the LV CT leads have to be taken to the HV Breaker Board thereby increasing the lead burden and thus the rated burden of the LV CTs. This would make the LV CTs bulkier & costlier. If the REF Relay is located in the LV Switchboard, this can be economised. Yes, it is agreed that for REF protection, the HV Breaker must be made to trip.The LV Breaker may trip on under voltage (caused by the the HV Trip) or inter-trip signal from the HV Breaker or directly from the REF Relay. Alternately, the REF may trip the LV Breaker and the HV Breaker may be made to trip on an inter-trip arrangement, wherein for any fault trip of the LV Breaker, the associated HV Breaker would trip.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#12

Re: Restricted Earth Fault Relay

02/11/2014 10:29 PM

I come across peculiar scenario on this matter.

In many projects the LT Panel supplied by one source with 3 CTS provided on the phase side of the incoming supply say with CT of ratio 3000/1.Non numeric REF relay of 1 Amp incorporated in the LT Panel.

The Transformer is supplied by another source with neutral CT incorporated in the LV box. say with CT ratio 3200/5.

The anomalies are noticed during the commissioning. But the concerned people talk about remedial action for few days but do not take any action. Ultimately in many projects I have observed the REF relay is out of picture without any protection for the transformer.

Best solution would be change the NCT at the transformer from 3200/5 to 3000/1.

But it is not done due to some reason or other.

Under such circumstances can we use suitable interposing CT to match the phase CT secondary. The interposing CT can be located in the LT Panel.

What are the implications ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); electricalexpert65 (3); Pattabhiraman (2); PWSlack (1); ramvinod (2); shock007 (1)