a new factory tested spring loaded safety valve behave erratically. When tested at site, it pops up at 0.5 bar less than the set pressure and sometimes 0.2 bar above the set pressure. The supplier says that it is ok. I there any standard which can be referred on this matter?
Re: Popping up of a spring loaded safety valve.
09/24/2013 10:46 AM
Yep. Go to the Engineer/Surveyor for the company supplying burst indemnity insurance cover for the facility. That individual will have access to the correct standard.
Of course the supplier says it's OK! In the facility accepting it for use, the supplier can run off to the bank rejoicing!
Re: Popping Up of a Spring Loaded Safety Valve
09/24/2013 11:15 AM
Why is this plant being operated in such a way that the pressure safety valve needs to operate in the first place?
Reply Score 1 for Off Topic
09/24/2013 11:08 PM
All pressurized boilers in the USA require safety(pop-off) valves.This is like a fuse or circuit breaker in an electrical panel..for when things go wrong.
It is a good practice to test and verify all pressure safety valves before accepting them,and is required by most insurance companies before they will issue the policy.
I remember one case where a safety pin was left in a pop-off valve,and the make up water pump failed on a coal boiler.The valve,which weighed about 600 pounds,went thru the roof of the boiler room and came back down through the same hole,and knocked out the catwalk on the top level of the boiler.Fortunately, no one was hurt.The picnic scheduled for the contractor for finishing the job early was cancelled.
09/25/2013 3:58 AM
Roger that. The question was about the operation of the plant. When a safety valve lifts, process material is being dumped. The original poster needs to explain why this is being accepted as a normal occurrence, for it indicates that the plant is being driven at the operating limit with the intention to go beyond it!
09/25/2013 7:20 AM
Ok, I interpreted the OP as testing the pop-off safety valve at a calibration test bench,not in an actual process.I also presumed a steam application,which I know is a very narrow interpretation.
Good Answers: 266
09/24/2013 12:11 PM
You can not tell us it acted erratically without more information. What is the pressure that the relief valve is rated for? What was the temperature of the valve at the time the relief valve opened? Changes in temperature effect spring tension. The relief valve set pressure should be 10% above max operating pressure. The operating pressure should not be that close to this device's set pressure. Device specs depend on what it's design to protect.
09/24/2013 2:13 PM
Apply this tool to the valve spring whenever it doesn't act to suit you.
09/24/2013 10:23 PM
What is the nominal setting of the valve? What percentage of that is the range of -0.5/+0.2 bar? Why were these essential items omitted from the OP?