I am trying to relate the earthing system practiced in India to BS or NFPA requirements, however I am finding few things confusing.
I know there is separate Neutral and Earth conductors on the distrubution side and it is TN-S as per BS 7651 , however the whole confusion( to me, alteast!) is regardng the source Transformer side. I think the practice is to provide 2 separate earth for body and Neutral of the transformer. Noone ever dares to interconnect the body and Neutral earthing.( you mention that, the contractor's Foreman becomes wild! ..Ultimately what he says is the rule. ). Earthed Neutral is brought to the Main Switchboard neutral bus and is further distributed to the distribution panels. Main switchboard will have its own earthing bar which is independately earthed . I do not see anywhere the Neutral is connected to the earth. Then how do the earth fault currents return to the sourse Nueutral?.
I have seen the practice in Middle eastern countries is to provide an Earth-Neutral link in the Main switch baord which will link the Transformer earthed neutral to Main earth bar of the Main Switchboard . Even the US practice seems to be same with a Neutral-Ground link at the intake service cabinet and an Equipment Grounding bar connected to N-G link.
My question is whether the Indian practice is right? Forum expert's views on this is requested.
Best Regards,