DP Type Level Measurement

10/03/2013 1:50 AM

Dear All, please help me to understand which is the best method for differential pressure type level measurement, directly flange mounted type or instrument tubing (not remote seal) on/from an atmospheric tank lower nozzle? Thank you all in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: DP Type Level Measurement

10/03/2013 2:11 AM
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: DP Type Level Measurement

10/03/2013 3:07 AM

Best for what purpose? Surely it depends upon application?

Otherwise, there would only be one way of doing it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: DP Type Level Measurement

10/03/2013 5:09 AM

Check the viscosity of the fluid. If low, tubing should work fine. If high, direct mounting may be necessary.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: DP Type Level Measurement

10/04/2013 6:27 AM

Why differential if the tank is open at top? Vent the low side to atmosphere.

As for mounting method,it is irrelevant,just make certain to bleed all air from tubing, if used,and that the transmitter is below the lowest level of the tank,so that tubing stays full of liquid.There will be very little flow in the tube as the pressure changes if the fluid is incompressible with no entrained air. It will simply reflect the pressure change corresponding to level.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#5
In reply to #4

Re: DP Type Level Measurement

10/04/2013 8:23 AM

Dear All

Depend on the process application, please consult your instrument design for best solution.

Regards

Register to Reply
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: DP Type Level Measurement

10/04/2013 11:45 AM

DP Level transmitter, dual head DP or flange mount? The DP transmitters are physically the same, they're mounted differently, but the differences should be taken into account:

1) Is there a flange to mount to?
For retrofits on existing tanks, the question becomes what kind of pressure tap is available? The issues involved in emptying a tank, cleaning or purging it for welding on flange, clean-up and recommissioning can be significant and costly, so most people are inclined to use what they've got. If there's a threaded connection down low, it's likely to be used because it's there and it's available.

2) Isolation valving
A DP transmitter can be readily valved off (2 way instrument valve in the tubing/piping) for removal/cleaning/whatever

A hot tap ball valve for removal of a flange mounted DP level transmitter is a much more expensive proposition.

3) Difference in component cost

A DP from one major manufacturer lists at $1,879 USD.
- Add a valve, tubing and fittings.

A flange mount DP level transmitter from the same manufacturer lists at $2,342 diaphragm flush to flange), a 4" extension is a $272 adder.

- isolation valve?

4) freeze protection

Depending on the medium, its process temperature in the tank and the climate, freeze protection might be necessary. Exposing the contents of a dead-headed impulse tube to outside-the-tank elements is far more likely to expose the contents to freezing temperatures (depending . . ), whereas a flange mounted DP level transmitter that locates its diaphragm at or near the tank wall (frequently through the lag of tank insulation) does not directly expose the medium to the outside-the-tank weather or climate temperatures.

5) zero error

A welded flange won't move up or down in elevation so the datum, the transmitter's zero reference point, will not change.However, DP level transmitters connected with tubing/piping can change, even if inadvertently.

For example, the tubing gets damaged and during the repair the transmitter get remounted at a different elevation than it was originally, shifting the zero.

Determining an exact elevation with respect to the tank is many times, guess-work. I have seen a tech get a rotating laser, set it up and get an exact point on the tank for the port elevation, but not always.

6) Temperature error

A flange mount DP level transmitter has fill fluid the diaphragm at the end of the extension tube and the sensor element. That's a closed system and is subject to temperature error. Much of that error on typical 4" extension tubes is compensated for in modern transmitters that measure body temperature if pressure body is the same as or to the fill fluid temperature.

Impulse tubing to a dual head DP should have no temperature error because the tubing is open to the tank. Any medium expansion/contraction due to temperature changes will be 'seen' as specific gravity changes, which is an inherent issue in any DP level measurement.

A diaphragm seal connected with a capillary will have a definitive temperature error. I mention this because I've seen it used numerous times.

7) Potential for damage resulting in leaks

The opinion of those I've dealt with is that flange mounted DP level transmitters are less subject to damage that could result in a leak than are tube connected DP.

Historically, tank level has been done with flanged mounted transmitters. Tube-connected DP is the exception, not the rule, in my experience.

When I had a discussion with one engineer on this topic, his view was that the $400 saved by installing a DP transmitter, rather than a flange mount, was outweighed by the increased risk of tank leakage due to damage to components outside the tank.

Register to Reply Good Answer (Score 2)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); Iris (1); lyn (1); PWSlack (1); ronron (1); Tornado (1)

Previous in Forum: Current Monitoring Diodes   Next in Forum: Instrument Drain

Advertisement