Low Power Factor in Arc Furnace Application

10/05/2013 12:00 PM

Our energy meter for 33 KV line was replaced last year.The new meter was running slowly and the KWH readings were low along with the low power factor of 0.70.We informed officials about low readings and requested them to check the meter.They came and confirmed that everything was OK.Since then they were billing according to the readings and we were paying.

They sent a supplementary bill this year stating that the meter readings were not corresponding to their check meter,so that we should pay the difference.We asked them to make sure that the meter readings are matching with the check meter . They have replaced the meter again.Now,the meter readings areo.k.,but still the PF is 0.65.

Now,they are saying that our capacitor bank is not correct.In fact,there is no change in our capacitor bank.It was giving us 0.96 PF before they changed the meter first time.

Our capacitor bank works on 33KV line for electrical arc furnace only.There are 4 capacitors.(416.67 each)on each phase connected parallel.The furnace transformer is 12 MVA.(33KV/450Volts).I requst you to kindly help me to solve the problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Low Power Factor in Arc furnace application.

10/05/2013 12:10 PM

How are you measuring the PF? Do you have a separate power meter, or are you using the power company's meter to judge PF.

Maybe the new meter is more accurate than the old meter, and that's why your bills have gone up.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#2

Re: Low Power Factor in Arc furnace application.

10/05/2013 1:39 PM

Are you getting separate billing for Arc Furnace usage? Or is all of the electrical usage on this one meter for all of the facility? The reason I ask is there something else that is causing the high PF readings. Do you have other large motors such as air compressors running off the utility lines. More info needed.

I might suggest asking your utility company to help you with this. Here in the states our utilities are very helpful with this issues.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: Low Power Factor in Arc furnace application.

10/05/2013 10:48 PM

I see you are relying on the Utility meters, but for the $ involved you should probably have independent measurements, and a power study done for your plant to identify what items contribute to the poor PF.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#4

Re: Low Power Factor in Arc furnace application.

10/05/2013 11:49 PM

First of all I do not have any experience on Arc Furnace and comments below are from other experiences - so all members please excuse me if my comments are not valid.

In case the Furnace Load is not steady but fluctuating - and capacitors are fixed (not switched on and off with load variation) most probably your Power Factor of 0.65 is Capacitive.

Pl check for (-) sign with Power Factor Reading on your Energy meter.

As we know discharging time of HT Capacitors (33kV or 11kV) is long (in minuets which can be seen on the name plate of capacitor), these are not suitable for variable load to effectively control the power factor.

In such case it is better to install a step down transformer and either STATCON (static inverter type capacitor/ Inductor). Or one can use switched LT Inductors and Capacitors.

LT Capacitors to improve power factor when furnace on load. Inductors to balance HT Capacitors installed as part of Harmonic Filters.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Low Power Factor in Arc furnace application.

10/06/2013 12:32 AM

Please make out sketch of SLD , showing incoming feeder,Capacitor feeder,furnace feeder.Please also show the CTs and instruments connected therein .

Now you mentioned the measured values with respect to each instrument.

In India most of the EBs charge the HT consumers based on energy consumed and maximum demand .They also charge penalty if the PF is lower than 0.9.

If you say for one year they were charging as per meter and suddenly they have demanded then for one year PF should have been normal and they have not penalysed.

Where is the PF measured?

We can study your billing, Log details, distribution arrangement, type and make of instrument and CTs and give appropriate solution provided you share all the information.

Your Capacitors are connected to system manually or through APFC relay.

Have you taken PF readings without Capacitors connected?

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Low Power Factor in Arc furnace application.

10/06/2013 5:43 AM

Dear Mr. nvrsrinivas,

The capacitor should be as close as possible to the connectedload. Pl. try this and post the information.