Anonymous Poster #1

Neutral Conductor

10/21/2013 11:04 PM

AS/NZS 3000/2007

rule# 3.5.2 (b) Exception (2) "Multiphase circuits. "The neutral conductor of a multi-phase circuits may have a current-carrying capacity lower than that determined by this clause, provided that a detection device is fitted and arranged so that the current cannot exceed the current carrying capacity of the neutral conductor"

My understanding here is simply a detection device rated to that of the neutral conductor and is connected to the neutral conductor which will protect the cable from heating up/melting. While the active conductors remain the same with its circuit breaker protection rated to the active conductor current carrying capacity.

Open for discussion.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#1

Re: Neutral Conductor

10/22/2013 1:19 AM

Not a good idea, What will happen if only you neutral breaker trips?

My understanding is that you only need to be protecting the active conductors.Your neutral conductor is always going to be less amps in a multiphase circuit, zero if balanced perfectly.Even though you did not size your breaker to your neutral cable, it is still protected by the breaker that is protecting tha active cables.

Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#2

Re: Neutral Conductor

10/22/2013 9:00 AM

if you want to protect the neutral by a breaker, it should be a 4 pole breaker, 3 hots and a neutral, factory built common trip, not field installed handle tie.

__________________
BSEE but always learning
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Neutral Conductor

10/22/2013 2:33 PM

My understanding here is simply a detection device rated to that of the neutral conductor and is connected to the neutral conductor which will protect the cable from heating up/melting.

Correct. In practice you need a current monitoring relay or similar (not a multi-pole or separate circuit breaker for the neutral obviously) to ensure the reduced neutral current level is not exceeded.

Depending on the length and cost of cable run weighed against the cost and complexity of the additional monitoring circuitry and whatever associated control gear is needed to drop out the associated phase circuits, reducing the neutral size may be a viable cost saving option. High current long copper cable runs are a good example.

The previous standard AS/NZS 3000:2000 only allowed the neutral to drop to between 1/2 to the full size of the largest phase conductor depending on the phase conductor current.

__________________
jack of all trades
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Neutral Conductor

10/22/2013 10:46 PM

This is actually a quite simple circuit, but that doesn't mean it's cheap. A current sensing relay on the neutral can be set to trip a MCB feeding the line conductors via a shunt trip.

It begs the question, why would you need such protection? The only reason I can think of is high harmonics. With normal 3Ph+N distribution the neutral current should never get near the line current.

Can you give more details?

Is this a homework question?

__________________
The reports of my death are greatly exaggerated.
Reply
Member

Join Date: Mar 2011
Posts: 6
#5
In reply to #4

Re: Neutral Conductor

10/22/2013 11:18 PM

Thanks for the input. Its not a homework its a real situation whereby parallel 185mm²Cu conductor is used for active 3 phases and single 185mm²Cu for neutral. Fiji follows the Australian electrical wiring rule. as/nzs 3000/2007. For clarification matter if we use 1 x 185mm²Cu as mentioned in my first submission rule 3.5.2 also allow for single conductor provided current monitoring device is fitted. My understanding at first hand is incorrect as there should be a complete isolation if the neutral current exceed the capacity of the neutral cable.

Thanks

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #5

Re: Neutral Conductor

10/23/2013 7:59 AM

If you need to break the neutral then the MCCB must be 3Ph+N, where the neutral is early make - late break.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Neutral Conductor

10/23/2013 6:41 AM

Actually, the sentence does not say quite what you have assumed. Just breaking the neutral could actually kill someone for example.......not in a correctly installed system though, though breaking the neutral alone is to my mind "is not a correctly installed system".

But, if say the trip was a four way trip, removing all three phases at the same time as the neutral, if ANY one of them was in an over current situation, surely that would be OK?

As in most countries the neutral is earth bonded at some point, there is actually no need to open the neutral as long as the 3 phases are opened.

A seriously unbalanced loading could cause a higher than normal current in the neutral, which can easily be spotted when measuring a high voltage between the neutral and ground. I don't remember what the legal limits are, sadly.....someone else here will know.

Which is why I run separate neutrals to each single phase leg, not a single 5 wire cable ( 3 phases plus neutral and ground), but 3 x 3 way (1 phase, 1 neutral and 1 ground). Not that I need to do it often.....not for years....
5 wire cables are a mixed blessing, but loads should be carefully distributed and no leg should use the max power when the other legs are not being used....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8

Re: Neutral Conductor

10/23/2013 1:46 PM

I think you may find that this device is a earth leakage unit (EL Unit or RCD), where by any current higher than 30ma (long ago upgraded to 60ma in some countries), becomes unbalanced against the phases will cause a trip and three phases and neutral will be disconnected, (tripped) on the EL Unit. The phases still go through a CB after the EL unit, so short circuit protection is available as well as the unbalance from the phases opposed to neutral.

Google Circuit Breaker Industries or try Group Schneider for an EL Unit. I have not checked the AS/NZ standard.

http://www.cbi-electric.co.za/products_all_circuitbreakers.php

EARTH LEAKAGE PROTECTION

Advanced electronic Residual Current Devices (RCDs) for use in residential and industrial applications. These include RCD modules, which can be attached to Moulded Case Circuit Breakers.

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); Andy Germany (1); eltech (1); IQ (1); jack of all trades (1); scandrews (1); TonyS (2)

Previous in Forum: Turbine Shutdown Procedure Reg   Next in Forum: Inrush Current Limiter Circuit

Advertisement