Turbine Shutdown Procedure Reg

10/21/2013 8:33 AM

Dear sir

when we going to shutdown the power plant which is safety method manualy trip turbine or open the generator breaker before trip the turbine.

Thanks and regards

B.jeyachandran

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Turbine Shutdown Procedure Reg

10/21/2013 8:48 AM

I don't know but asking a bunch of strangers that don't know anything about your power plant does seem like the safest and most responsible way for you to do your job.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Turbine Shutdown Procedure Reg

10/21/2013 8:49 AM

What does the operator's manual say.

I can't read it from here.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Turbine Shutdown Procedure Reg

10/21/2013 9:11 AM

If it is anything other than emergency the safest method for you to follow is:

1. Put your hands in your pockets,

2. Walk slowly away from the controls,

3. Let someone who understands how to do this take over.

If it is an emergency hit the emergency trip button.

Either of the things you describe are steps in a safe shutdown, doing them out of sequence or with a load on a unit that has not been run through an orderly shutdown procedure, can lead to electrical/mechanical transients that threaten the equipment and/or the safe operation of the system.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Turbine Shutdown Procedure Reg

10/21/2013 9:41 AM

The best way is to follow the procedure in the User Manual supplied with it.

The next best way is to leave it to someone who has been trained to do it.

The next best way is to follow the facility's Standard Operating Procedure, which ought to be on file in the Control Room ready for use.

The worst way to do it is to ask a bunch of miscreants strangers, none of whom can see the plant, none of whom know the maker, type, rating or anything else about the equipment, and none of whom have any interest or liability in whether the thing shuts down correctly or whether it self-disintegrates catastrophically on the journey.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Turbine Shutdown Procedure Reg

10/21/2013 1:03 PM

Do you see that blue button? Press that one.

No! Not the aquamarine button, I said the blue button.

No!!!! That's the turquoise button. Never touch the turquoise button.

You're getting closer with that Cerulean button, but don't push that if you want people on the floor to live.

That's a violet button. Leave it alone. Are you color blind, too?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: Jan 2009
Posts: 29
Good Answers: 1
#6

Re: Turbine Shutdown Procedure Reg

10/21/2013 3:44 PM

I hope your plant isn't like the one I just left. I though I had gas pressure in a 16" natural gas main because the gauge said so. I had an operator explain to me that I needed to carry my own gauge because 90% of the gauges on site don't work.

Hell just start opening breakers, if something goes wrong just beg for forgiveness.

Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Turbine Shutdown Procedure Reg

10/21/2013 7:45 PM

It depends on the size and type of power plant along with documented site procedures, obviously a Hydro plant shutdown procedure is different for a gas turbine power plant. Neither of the options you have mentioned above may be correct.

Follow the site manual, which likely says something about unloading the turbine before performing a manually-controlled or automated shutdown process following a number of steps in a certain order.

Do NOT throw something in the running turbine to stop it or just hit the E-stop button, both will likely result in........unpleasantness.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Turbine Shutdown Procedure Reg

10/21/2013 8:29 PM

Actually any power plant operator that must ask a group of strangers how to shut down their turbine should first grab the spinning turbine shaft with their bare hands. Next they should verify that the generator is no longer producing electricity by sticking their tongue on every electrode.

I wonder, does Web MD get people asking how to remove a burst appendix or what is the safest way to make your own penicillin?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9

Re: Turbine Shutdown Procedure Reg

10/22/2013 1:48 AM

I do not know how big is your steam turbine or hydro turbine.

In both cases if the breaker is suddenly opened on load, in both cases there is risk of over speeding. Though over speed protection is available, but even after this functions, there is enough inertia of steam in chest of turbine and water in between shut down nozzles. and watter wheel that speed keeps on increasing beyond the trip set point.

Therefore it is always preferred to cut down the steam or water after the load has been brought to zero.

If the turbine is in parallel with Grid or other turbines, the load control is taken on "Manual" load sharing, its load is slowly cut down by changing speed set point on governor. (Also the excitation is controlled simultaneously to ensure it does not trip on load on under or over-excitation). Once the load is near Zero, the speed is further brought further down (VERY SLOWLY) to ensure the Turbine is tripped on REVERSE POWER. Two advantages:

1. Zero chance of over-speeding..

2. Also test your relay during shutdown.

Besides,

1. While cutting down load in case of Steam Turbine - we keep a watch on Differential Temperatures between rotor and casing and differential expansion of two and Eccentricity of Rotor.

2. Test back up devices for safe shut down, such as Standby Diesel Generator, Turning Motor or Barring Gear, Emergency Lube oil pump (or Jack up pump in case of Vertical Hydro-turbine).

3. Control Boiler firing and water level control in case of Steam turbine (You do not want Safety valve to lift or water level in drum going to enter water walls).

So in brief, Safer way to stop turbine is to first bring down load - next close steam/water and last to open the Generator CB.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Turbine Shutdown Procedure Reg

10/22/2013 5:00 AM

Dear Mr.B.JEYACHANDRAN,

Do not Trip Turbine on load, unless it is an EMERGENCY. Follow the INSTRUCTION MANUAL

Otherwise, Normal shut down, Alert all the staff in particular the Boiler Staff to take care of Feed Water Level in the Drum, Fuel Regulation, Stand by Power - Keep DG Set Ready in ON condition etc.

Reduce the Load Gradually. Then open the ACB, the Trip the Turbine, Ensure Barring Gear starts on at right moment. Auxiliary Oil Pump starts. Oil cooler water circulation is a must.

Then close the steam to ejector for condenser, stop cooling tower and so on. Simultaneously if single boiler - shut down will follow as per the procedure.

These are salient points, still few other points are there.

DHAYANANDHAN.S

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #10

Re: Turbine Shutdown Procedure Reg

10/22/2013 9:20 AM

Gosh, I sure hope this is not an emergency, and he is waiting for a response before he trips the unit.

Most all the above answers are suitable answers, but the only answer that works for you is the one you arrive at considering your actual plant, and the manuals. One never does trip the (steam) turbine until load is lowered to minimum, and then the generator field coils are re-opened from the grid, then you use the manual governor control (in most instances) to lower speed on turbine, then trip the stop valve.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#12

Re: Turbine Shutdown Procedure Reg

10/22/2013 11:50 AM

I really find it quite hard to believe that this is a serious inquiry and that any of us would be able to give a serious response to such a ludicrous request for advice. I really doubt that anyone who would be in a position to act upon our advice would be asking this question. At least I certain pray for the sake of anyone anywhere near that facility that he is not.

__________________
Spinco
Register to Reply Score 1 for Good Answer
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13
In reply to #12

Re: Turbine Shutdown Procedure Reg

10/22/2013 1:38 PM

A quick look at his previous posts indicates that he is indeed somewhere near this type of equipment. His questions indicate that he is a newbie observing things that no one can or will explain to him.

When I was a co-op student I spent months crawling around a fossil generating station asking some very basic questions (I was an EE in ME heaven), most of them got a chuckle out of the operators, until i found someone who would point me in the right direction. I was always told "Don't touch anything, even after we tell you how it works!!", had to read about 8 ft of manufacturers' binders to learn what others wouldn't teach me.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#15
In reply to #13

Re: Turbine Shutdown Procedure Reg

10/22/2013 2:11 PM

Went back and saw what his previous posts related to and can see your point in that he also is evidently an EE trying to swim with the big boys. Sorry, couldn't resist that little cross Majors jab. Best advice I would give in that case is always shed your load as slowly as necessary or allowable,rather than abruptly which he was referring to, to allow your system to adjust. Then throttle back your driver till you get to whatever point you want to end up with it and allow it to slow down and cool off per the manufacturer's instructions which he should be able to find by using the index in the 8 ft. binder.

__________________
Spinco
Register to Reply
Associate

Join Date: Jan 2009
Posts: 29
Good Answers: 1
#16
In reply to #13

Re: Turbine Shutdown Procedure Reg

10/22/2013 9:52 PM

I like that Ramconsult, I work on the mechanical engineering side of things. However 25 years ago I took 2 years of electrical in a vocational school. I got a lot out of it and a journeyman's licenses and really enjoyed it, and did very well in school because of that fact. sense that day's almost 25 years ago I always had a passion to work in a power plant.

Now I work as a mechanical contractor in power plants in the Denver area. Every time I have free time on the plant I'm always hanging around a few engineers and operators I know and ask questions and they are willing to take time and teach me about power production. I get a lot out of it and really enjoy learning about new technology in this field. In return I help therm out on there equipment at home. I also get a lot out of certain responses on this forum. My hat is off to the guys taking some time out to seriously help a guy learn a little bit.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14

Re: Turbine Shutdown Procedure Reg

10/22/2013 1:46 PM

The only good answer here is to first give a general idea since the details are not in question. I presume it is just an argument on which steps to follow and not an actual education on the procedures!

- generator before turbine or the opposite ? The details are not the argument here.

Therefore, Take care of the generator (Alternator) first then the turbine!

Now: the details of how to take care of these two during shut-down will depend on the urgency: Scheduled shut-down or emergency.

Then, the advice is to consult the makers on the procedures for each case, or leave it for the qualified or person in charge (Who should be competent...)

Register to Reply Score 1 for Good Answer
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: