Inrush Current Limiter Circuit

10/22/2013 2:09 AM

Dear All,

Any formula for calculating inrush current for a toroidal transformer?

I have taken a formula from internet shown below,

where Vm - maximum applied voltage; L - air core
inductance of the transformer; R - total dc resistance of the
transformer; BN - normal rated flux density of the
transformer core; BR - remanent flux density of the
transformer core; BS - saturation flux density of the core material.

But i am not clear about the air core inductance of the transformer?

Using CRGO steel core and its normal operating frequency is 1.7T and saturation flux is 1.87T.

any idea pls help me.

Best regards,

M.R.T

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inrush Current Limiter Circuit

10/22/2013 7:21 AM

So, why isn't the inrush current simply the applied voltage divided by the resistance of the winding, before the magnetic field has started to build up?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #1

Re: Inrush Current Limiter Circuit

10/23/2013 10:26 AM

Because it's necessary to account for any residual (remnant) magnetism in the core and the core's characteristics. As you can see the stuff in parenthesis † can result in a significant multiplier to your approach (the stuff to the left of the parentheses).

Although we don't normally think of it as such, the core is an energy storage device, and it takes a lot of energy to instantaneously switch its state so that all the magnetic domains line up with the newly applied voltage/current. That's one of the reasons why we see statements like "...the inrush current can be 4-12 times full load current...).

Hit a transformer which was switched off with the core fully "charged" and you may get the top of the range depending upon where on the voltage waveform the switch was closed. Of course it's all statistical as to when the switch is opened then closed so we provide a range of values.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Inrush Current Limiter Circuit

10/22/2013 11:28 AM

You may find your answer in this paper:

http://pulsedmagnets.web.psi.ch/Air-core%20transformer.pdf

Plenty on the topic by Googling.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Mar 2010
Location: Salem, Tamil Nadu , India
Posts: 6
#4
In reply to #2

Re: Inrush Current Limiter Circuit

10/23/2013 4:03 AM

Thanks for your reply,

The link refers the air core inductance simply the coil alone, but not the calculation for toroidal transformer air core inductance.

In torodial transformers the winding goes from top to bottom and not in circle.

for inrush current calculation we need to account air core inductance?

Waiting for your valuable answer.

Best regards,

M.R.T

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 123
Good Answers: 7
#3

Re: Inrush Current Limiter Circuit

10/23/2013 3:10 AM

The design of the toroidal transformer results in very low air core inductance. But then inrush current can be very high. It may come up to 60x load current.

Best way to reduce the inrush is to implement a premagnetising procedure.

Register to Reply