9 comments
Rating: Comments: Nested
Anonymous Poster #1

kVA Rating Question

11/02/2013 8:10 AM

help me out !

a phase ,50 hz ,6600v ,alternator is rated at 6600kw..

what is kva rating ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: kva

11/02/2013 10:33 AM

Reply
Anonymous Poster #2
#2

Re: kVA Rating Question

11/02/2013 1:00 PM

Please punctuate correctly.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #2

Re: kVA Rating Question

11/03/2013 9:45 AM

Whoever marked this comment as "off topic", cannot understand the finer points of punctuation....The statement is correct and on topic!

That being said, ones command and comprehension of said language, does ultimately depend on how and when the correct comma, period, and exclamation marks are placed.

Mastery of that skill, while not easy, can be mastered by reading any English book, and I will hazard a guess that the OP copied from a text book, STILL manged to get it wrong!

What is the world coming to?

__________________
The square root of nothing is what you make it!
Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: kVA Rating Question

11/02/2013 1:03 PM

It depends on what power factor has been allowed for in its design. If 0.80, 6600/0.80 = 8250.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Participant

Join Date: Nov 2013
Posts: 3
#5
In reply to #3

Re: kVA Rating Question

11/03/2013 6:06 AM

thanks ..

and how can i find current rating ?

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #5

Re: kVA Rating Question

11/03/2013 6:20 AM

here.. and I want FULL credits for me doing your homework

LINK 1

if that don't do it for you try this this one

LINK 2

or

LINK 3

next time do your own googling...

__________________
The square root of nothing is what you make it!
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: kVA Rating Question

11/03/2013 3:58 AM

Dear Friend,

The Alternator Manufacturer could have given the POWER FACTOR in the name plate. Devide KW (In your case it is 6600 KW) by the Power Factor. That will give you KVA. Generally P.F will be 0.8, hence your Alternator KVA is 6600/0.8 = 8250.

DHAYANANDHAN.S

Reply Score 1 for Off Topic
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#8

Re: kVA Rating Question

11/18/2013 4:22 AM

"help me out !

a phase ,50 hz ,6600v ,alternator is rated at 6600kw..

what is kva rating ?"

likely 3 phase if real, if homework, well.....

__________________
BSEE but always learning
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9
In reply to #8

Re: kVA Rating Question

11/18/2013 10:26 AM

I guess from your last post you did not check out the links I placed in my reply. go to my first reply and click on the first LINK....

__________________
The square root of nothing is what you make it!
Reply