Capacitor Fault

11/05/2013 9:51 AM

hi everyone

i face problem that the capacitor have burn in high voltage plant in VFD motor and that is not the first time i see there will be some problem but can not find it..and before four months we have build new generation project so is there any relation between this problem with the new generation

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Capacitor Fault

11/05/2013 10:20 AM

Is there anything in the way of specific information available that might help the forum get a start on this?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: Capacitor Fault

11/05/2013 10:57 AM

I see exactly your problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Capacitor Fault

11/05/2013 11:03 AM

Indeed. That is the problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Capacitor Fault

11/05/2013 11:13 AM

Maybe I'm being a spoiler, but is the capacitor at the motor? If so, did you fail to read the instructions that came with the VFD telling you to NEVER put capacitors between the drive and the motor?

And if you had the caps on the line side, why? The VFD will correct the displacement power factor for you, there is no reason for the capacitors and they present a risk of resonance in the circuit with the VFD's DC bus capacitors.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Capacitor Fault

11/05/2013 11:28 AM

...which would explain an overvoltage at the external capacitor, and its early demise. GA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#6
In reply to #4

Re: Capacitor Fault

11/05/2013 11:54 AM

Yep, another likely ESO failure.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#11
In reply to #4

Re: Capacitor Fault

11/06/2013 8:49 AM

Good morning JRaef,

Some of our older GE & Toshiba VFD units with analog speed feedback do have capacitors on the motor side of the drive.

The newer vector drives do not.

Maybe the OP is dealing with older equipment.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #11

Re: Capacitor Fault

11/06/2013 12:18 PM

Replying to Comment by SHOCKHISCAN: "Good morning JRaef, Some of our older GE & Toshiba VFD units with analog speed feedback do have capacitors on the motor side of the drive. The newer vector drives do not. Maybe the OP is dealing with older equipment."

Maybe, although this is still suffering from a lack of attention to detail. Most likely you are seeing older Current Source Inverter drives or six step drives that used GTO Thyristors as output power devices, they often needed tuned capacitors on the load side of the drive as part of the necessary circuit design to make the GTOs turn off. That technology is now long gone. Even modern CSI drives no longer use GTO Thyristors.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Capacitor Fault

11/05/2013 11:56 AM

Or another RTFM situation...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Capacitor Fault

11/05/2013 12:35 PM

Or burned by an "energy saving" company/consultant?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Capacitor Fault

11/06/2013 3:18 AM

How about that for global warming?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Capacitor Fault

11/06/2013 4:22 AM

Dear Mr.ibrahim1988,

Your question does not indicate, like Capacity, Whether the Capacitor is before VFD or after VFD, level of Harmonics Filtering, Earting of VFD etc. Pl. give the factual ground reality. Then only CR4 MEMBERS can suggest a remedy.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#12

Re: Capacitor Fault

11/06/2013 9:04 AM

I would suggest you look carefully at the drive regeneration control circuitry.

The drive must have the means to discharge the high voltage created by the collapsing motor field regeneration when the drive supply power is removed and the motor leads are open-circuited.

If/when this voltage exceeds the insulation rating of the capacitor it will penetrate through and cause the capacitior to fail.

You should have either:

1. A dynamic grid resistor bank that is switched into the motor lead circuit automatically when the drive output contactor is opened.

or

2. The drive circuitry will have regeneration control circuitry that will use the secondary bridge components for dissipation of the voltage.

Start by reviewing the drive instruction manual to identify which type of circuitry is present.

If the drive uses internal regeneration control you must not allow any personnel to attempt repair unless they are fully trained and competent.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); JRaef (3); PWSlack (4); redfred (2); SHOCKHISCAN (2); Tornado (1)

Previous in Forum: Minimum Generator Rating to Sustain a Motor Soft Starter   Next in Forum: ZCT and Nuissance Tripping for EFR Problem

Advertisement