400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/06/2013 12:56 AM

Dear sir,

I am looking at my client's power distribution system and this system consists of a 22kV which is stepped down to 6.6kV and then further step down to 400V.

Our client is required us to trip the 6.6KV switchgear panel whenever there is a fault at the 400V switchgear panel.

Isit a norm to trip from downstream to upstream?


Isit possible to trip from upstream to downstream ( i.e trip from 6.6kV panels to 400V panels)?

Kindly advise.

Thanks

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 400 V Switchgear Panel Trip all the way up to 6.6kV Switchgear panel

11/06/2013 3:16 AM

If the 6.6kV panel trips then it is very difficult to see why a trip at the 400V panel could occur, as there would be no power on it as a result of the 6.6kV trip.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 400 V Switchgear Panel Trip all the way up to 6.6kV Switchgear panel

11/06/2013 5:01 AM

On the other hand, working back upward, loss of 400V power could be used via a shunt-trip breaker to then interrupt the 6.6kV power.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/06/2013 8:58 AM

Not possible to trip but to interlock the switch gear.

I would though look at all the systems the 6.6kv switch gear powers. That you may not be creating a hazard for personnel if it shut down.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Member
India - Member - Electrical Engineering Fields - Power Engineering - Electrical Engineering Fields - Electrical Engineering - Electrical Engineering Fields - Electromechanical Engineering - Electrical Engineering Fields - Energy Engineering - Electrical

Join Date: Sep 2008
Posts: 6
#4
In reply to #3

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/06/2013 1:36 PM

Yes, you can trip the 6.6kV Panel if there is any fault in the 400V Distribution network through Relay Co-ordination.

But still, it is hard to understand that why you want to trip 6.6kV Network ,instead of 400V Distribution Circuit.

You can have much precise and selective trippings in 400V Network and will be easy to troubleshoot also.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/06/2013 9:49 PM

I recently altered the tripping on an 11/.66KV system. The fault currents on the LV side were so large that I got the MV side to clear the fault first.

I inherited this system, it was terrible. The LV ACB was loaded to the max at 4000A, I didn't want that tripping under fault. So a bit of jiggery pokery on the MV side got that to clear the fault first.

I was stood next to an ACB when it opened under fault, I had to go and change my underwear!

The entire room lit up.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7
In reply to #5

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/07/2013 10:12 AM

This is scary.

The upstream protectioin should be designed to protect the power conductors between the MV and LV switchgear.

The LV switchgear should be adequately sized and have the necessary protection circuitry equipment to safely interrupt any/all "bolted fault" conditions on the load side.

If the LV equipment cannot do so safely, it is either undersized or faulty and either way should be repaired, tested, and/or replaced as soon as possible.

The upstream MV/HV protection in any electrical circuit should never trip unless the LV protection fails to clear a fault within the acceptable circuit protection time limit.

Allowing the upstream protection to clear a fault will cause great difficulty in determining the location of the fault and will create very unsafe operating conditions not only for the equipment but also for anyone in the immediate vicinity.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Member
India - Member - Electrical Engineering Fields - Power Engineering - Electrical Engineering Fields - Electrical Engineering - Electrical Engineering Fields - Electromechanical Engineering - Electrical Engineering Fields - Energy Engineering - Electrical

Join Date: Sep 2008
Posts: 6
#8
In reply to #7

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/07/2013 3:06 PM

Yes, i am fully agree with SHOCKHISCAN:

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#6

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/06/2013 11:18 PM

In case of earth fault in the secondary winding of a the 6.6 kV/ 400V transformer it is better to trip the 400 V ACB first through stand by earth fault protection sensing earth fault current from the CT in the transformer neutral circuit. The 6.6 kV circuit breaker should then be tripped after a time delay.

However for overcurrent or earth fault on 400V side ( incoming bus and outgoing feeders) it may not be necessary to trip the high voltage circuit breaker as the fault will be cleared by the incoming or outgoing 400V ACB.

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#9

Re: 400 V Switchgear Panel Trip All the Way Up to 6.6kV Switchgear Panel

11/09/2013 12:33 AM

As per the fundamentals of protection system, faulty feeder should be isolated first to ensure uninterrupted power supply to the remaining consumers fed from the healthy feeders.

In case, the faulty 400 V feeder fails to trip due to any reason, then the respective incoming feeder should trip. If this also fails to trip, then the upstream 6.6 kV feeder should trip. This is achieved through proper protection coordination.

However, automatic tripping of the upstream feeder from downstream feeder and vice versa is possible through shunt trip and suitable interlocking scheme, if required.

__________________
Learning is a never-ending process.
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); ozzb (1); PWSlack (1); sandeepelect (2); SHOCKHISCAN (1); spradhan (1); TonyS (1); Tornado (1)

Previous in Forum: What is Power System Stability Study?   Next in Forum: Power Rating Calculation

Advertisement