Anonymous Poster #1

Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 4:49 PM

I recently noticed that while our a/c was running there was no air coming out the vents. I went outside and the fan was not turning, also saw the big line(discharge?) going from the compressor to the accumulator was icing over. A local "pro" told me to change the dual run cap and now the fan is turning but still no air. Don't know much about HVAC so any advice would be appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Why is my Janitrol unit not blowing air?

11/13/2013 5:28 PM

This is not a job for amateurs or DIY 's , call a professional....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 5:56 PM

Perhaps you could name and describe your A/C unit.

1. Is it sitting through the wall as a mono bloc?

2. Is it a split system?

3. Is it part of a central air system?

4. Is it part of a chilled system?

Some have a name, and a type.

__________________
Plenty of room here
Reply
Member

Join Date: Sep 2013
Posts: 9
#21
In reply to #2

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:24 AM

Its part of a central air system, everything is enclosed in one unit. The problem occured while the a/c was running, it seemed like very little air was coming out the vents and the air was not cold. I went outside and saw the fan had stopped turning and the big line going from the compressor to the accumulator had iced over. I turned the blower fan and it turns freely, changed the dual run cap and now the fan turns but still no air. I'm trying to do it myself because were strapped for cash right now, but if this is something a pro should fix I might have to rethink things.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 7:11 PM

Save money. Call the man.

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 7:15 PM

pay for a service call, the problem is over your head

Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#5

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 8:11 PM

AP #1

I can't see or touch your unit so I can't see what the problem is. Neither can I test it, make any adjustment, charge any gases, check the electrical of the complete unit and its components, clean it or another tasks that might be involved with trouble-shooting and adjusting/repairing you A/C unit. Therefor I am not the man to call. Call a local A/C repair/contractor for correcting the problem.

Caution- If someone claims to be able to be able to repair it without being there is a fool to say the least. Maybe also liar, con-artist, a fraud, cognitively challenged, a spy (call the NSA if this is the case), a bigamist, have an IQ of less than half the age of our president at 1600 Pennsylvania Ave., or one or more serious malady that would only make matters worse.

In Summary- get a local A/C repairman in to do the job!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 10:47 PM

You may be looking at the condenser fan rather than the evaporator fan, which is usually indoors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#7

Re: Why Is My Janitrol Unit Not Blowing Air?

11/13/2013 11:15 PM

One of the reasons for ice formation is less refrigerant. Or May be the due to dirty filters. Consult the trained service personal to resolve this issue.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:07 AM

Iced lines is a clear sign that you are low on refrigerant.

Refrigerant is not consumed it leaks out.

You need more than a quick fix. You need a refrigeration service dude to have a look and make it good.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply Score 1 for Off Topic
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#10
In reply to #8

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 5:39 AM

Goes also for previous poster:

Ice can also appear when the fan doesn't work. The coil cannot rid the cold to the environment. Since OP 's claims show this, the fan might be just the problem. A good analyst reads and listens to what the OP comes up with.

We do not even know what machine het has, unless Janitrol says it all?

The A/C man might clean the exchangers too and test the system pressures.

Here in the land of the blind, the A/C man charges $70.00 to fill up a car A/C. That is $5.00 worth on refrigerant and $65.00 for 10 minutes of the time of ""THE MAN"" behind the meters.

__________________
Plenty of room here
Reply
Associate

Join Date: Oct 2013
Posts: 29
#9

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:21 AM

Heave it outside it is cheaper to get a new one instead of trying to get it repaired.

Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#13
In reply to #9

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 7:21 AM

really now???

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#11

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 5:45 AM

__________________
Plenty of room here
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#18
In reply to #11

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 9:27 AM

nice sticker but that's a nat gas furnace!

Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 268
#12

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 6:28 AM

Because it Sucks. hahahahahahahahaha

__________________
guds777
Reply Score 2 for Off Topic
Member

Join Date: Sep 2013
Posts: 9
#31
In reply to #12

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 4:47 PM

Wow.. I bet it took you a long time to come up with that one.. very impressive.

Reply Score 1 for Off Topic
Power-User

Join Date: Feb 2010
Posts: 268
#34
In reply to #31

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 7:37 PM

no very quickly.

__________________
guds777
Reply Score 1 for Off Topic
Power-User
Fans of Old Computers - PDP 11 - New Member

Join Date: Mar 2007
Location: In a mushroom field somewhere in Canada. Kept in the dark and fed sh--, well you know.
Posts: 312
#14

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 8:00 AM

Maybe you need to buy her dinner and flowers first. LOL

UFG.

__________________
Dirt is for vegetables. Pavement is for racing.
Reply Score 1 for Off Topic
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#15

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 8:52 AM

I the process of replacing the cap did you shut it down long. With the lack of air movement though the evaporator it may have ice up also. To point it has restricted the flow.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#17
In reply to #15

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 9:04 AM

In that case shut it down for a LONG time and let it all melt out. Then you can evaluate the system in a non- congested state.

GET PROFESSIONAL HELP ( for the AC that is )

__________________
Smart as a post and twice as fast.
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#16

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 8:56 AM

In addition to the outdoor fan (condensor fan) there is an indoor fan (evaporator fan). This is inside the unit. Might be a broken belt, bad motor, or bad wire. I can't tell from here.

If you don't know how to find the evaporator fan or check the above items you might want to talk in person to someone that does. The internet is not the best way to troubleshoot equipment. Need to be able to verify what you read.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#19

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 9:46 AM

First note that the "big line" from the accumulator to the compressor is the suction line. I say accumulator to compressor because this is the direction in which the refrigerant flows. The accumulator is to prevent liquid refrigerant from entering the compressor. (Thus "accumulating" it.) NOT to be confused with the receiver tank.

That is, if your system has both these.

I am speaking from the standpoint of general HVAC, and I know nothing specific about your unit.

Having said that;

There are more conditions than low refrigerant that can cause iced lines.

Low suction pressure can cause iced lines. What can cause low suction pressure?

Glad you asked!
Low suction pressure could be caused by:

Restricted evaporator air flow - fan not running (as OP said it's not!) debris in the coil, a damper stuck, return air blocked.

Restricted expansion valve

Restricted suction line or modulation

Yes, also a leak or low refrigerant charge.

I advise finding the evaporator fan. It's the one in your house that you would notice is not blowing. It blows the hot and cold around your house.

The fan outside is the condenser fan. It expels the heat or cold from your house.

Once you find the evap fan, confirm it is not running. Check your primary air ducts and see if anything is blocking them. Check to make sure your filter is not clogged, plugged, totally filthy. Maybe replace it anyway - it's good to change frequently.

After you do all this, you're about at the limit of what an average person can do. If the evap fan is indeed not running, it could be a range of problems.

Most HVAC units have a control circuit board. This board could have gone bad, lost a connection, have a plug that loose, or etc. A technician can and will check it rapidly and affordably.

Do not attempt to mess with refrigerant or refrigerant lines, unless you are EPA certified or whatever your local country (I didn't check your location) requires for certification. You do NOT want to vent refrigerant under any circumstances. It is bad for the environment, and it can kill you by suffocation - a most unpleasant occurance.

Feel free to ask more if you find something and you're curious.

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#20
In reply to #19

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:11 AM

"expels cold".........interesting concept

Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#22
In reply to #20

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:24 AM

Scientifically innacurate. I was in a hurry when I typed it.

I know in residential HVAC you typically just burn a fire and blow the heat around.
In transport HVAC, we reverse cycle and other methods to REINTRODUCE heat.

Better?

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#24
In reply to #22

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:31 AM

its all good any refrigeration system (including AC) is a machine that moves heat. you can't create cold!

Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#25
In reply to #24

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:34 AM

I know... you shamed me... it sucks!

That'll learn me! Here I thought I was going to be all cool and provide a good answer... and one slip of a word, and it's all crap!

I'm kidding of course. Just so everyone who reads knows. I find it amusing that I made such a stupid comment and got called on it. Amusing in that 'my pants fell off in public' sort of way.

Reply Off Topic (Score 5)
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#23
In reply to #19

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 10:26 AM

The fan outside is the condenser fan. It expels the heat or cold from your house.

I made an oopsie.

Note that of everything I said, this is all that is noticed.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#26
In reply to #23

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 1:19 PM

No not all...your stated possibilities of icing, are woefully inadequate....any encouragement for the OP to attempt to troubleshoot a complicated system like this, is a disservice to them, that could end up costing much more in the end....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#27
In reply to #26

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:00 PM

Hi Solar:

So the OP shouldn't check air flow on a system OP has already worked on. You have more reasons why the suction line could be icing, but don't want to share them, and our standard answer on CR4 is "Go call a professional" ?

I know this discussion has been held a million times. On the forum, any question is most likely to be met with ridicule, and maybe some helpful statements.
I didn't say ALL of the causes of icing on the suction line were listed. Just some of them. I said to check airflow and not mess with the actual refrigeration.

You were the first to respond: " This is not a job for amateurs or DIY 's , call a professional...."

I've seen lots of your posts, and am aware that you are knowledgeable in a lot of areas. So when in your career or experiences did "call a professional" help you to gain knowledge or understanding?

I'm all for fun, humor, and maybe even some ridicule from time to time. Most of the time, I am reading for search of interesting topics and to learn new ideas.

Since we're throwing out "woefully inadequate" I would challenge that your own posts are woefully inadequate and lack any educational insight into why it is even necessary to "call a professional".

Yes, we can't see the unit, we can't test the unit, and we can't a great number of things. Isn't that assumed when we are on the internet?

In general when I see questions too vague, too poorly phrased, or that I don't know, I don't post anything. I'm been on here for years, and have less than 200 posts at the current time. (Shows in my profile).

Further, saying that checking the airflow on a residential air conditioner is a disservice and could end up costing them more is akin to saying that telling someone to check the oil on their car is a disservice that will end up costing them much more.

As engineers, we certainly wouldn't want OP checking their filter to make sure that a cat didn't fall asleep in there, would we!?!

I'll grant, my perception is my own. Perhaps I am completely off in thinking that the open exchange of information and ideas is a good thing.

Perhaps I should make more of an effort to watch for new posts and tell people to go call a professional?

Anything less might be woefully inadequate.

That's all I got for now. Please commence any mocking and ridiculing you find entertaining.

Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#28
In reply to #27

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:11 PM

first off, anon posters get zero respect. the op probably doesn't have refrigeration gauges or the EPA cert to play with refrigerant..... the part about a dual cap is extremely unlikely to be a part of his problem. he might have just run the unit in low ambient conditions., maybe the blower quit, maybe the filter is plugged, maybe he closed off too many vents in too many rooms. you need to lighten up. no one here gets paid for their time or knowledge. so sure there can be lots of smart ass replies and jokes.........its the internet, what do you expect for free?

Reply Off Topic (Score 5)
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#29
In reply to #28

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:19 PM

Fair enough. Not trying to be inflamatory... I'm just sayin' ...

But I would rather be called a stupid @r$ehole than my mostly good information, aside from the mistake you already pointed out be called woefully inadequate. From my perspecitve it wasn't too bad.

Foolishly, I didn't notice the OP was anon either.

So I guess I'm saying - If I'm a moron say so, or if my information is wrong, tell me why.

So, I'll shut up and go back in my corner.
Sorry, no offense was intended.

Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#32
In reply to #27

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 4:57 PM

After many years of selling and servicing these systems I can tell from what the OP said that the OP is not qualified to repair the system ...Any attempt at trying to repair the system may damage it further, or injure the OP or somebody else...maybe even the guy that has to come after the OP has given up........There are a lot of things that lend themselves to DIY in the home, with guidance....and you can even learn things like electrical, plumbing and A/C, but under the close and personal supervision of an expert....not an on-line format...I have seen a homeowner run a simple repair into the thousands by operating on blind ignorance....Now if the OP wants to attempt it, then they probably will...I can only offer some advice...call a professional

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#30

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 2:20 PM

If the compressor Low side is icing up the most likely cause is the unit is trying to reach a temperature that is not attainable because the system cooling capacity is undersized, the evaporator is restricted, the duct work is too small or rstricted, or there are duct leaks adding to much heat load to/on the evaporator/refrigerant or the thermostat is set too low or is faulty.

The lack of air flow is usually either due to ice buildup on the evaporator or there is a restriction such as a collapse, restricted, ruptured duct, and/or insulation trapped against the evaportator coils.

The second most likely cause would be that the refrigerant charge is too low causing the evaporator to ice up and restrict air flow.

If the unit is properly sized and the icing is not being caused by a low refrigerant charge the next likely cause would be a faulty TXV (Thermal Expansion Valve).

If none of this makes sense to you, I would hire a competent refrigeration repair service to troubleshoot the system.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#33

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 5:02 PM

One more small item that can be a very large one that will cause icing of the low side.

There is a flow orifice that must be installed inside the high side refrigerant connection at the evaporator inlet.

This orifice must be correctly sized for your application based on application cooling/heating BTU/tonnage requirements.

In todays high focus on cost savings marketing most HVAC manufacturers use the same size compressor in different cooling capacity rated units.

For instance: You may have a 4 or 5 ton compressor installed in a 3 - 3-1/2 ton unit which will require the proper sized orifice for whatever cooling rating is required for your application.

You need to know exactly what size your application requires and this can only be answered by a trained, competent HVAC engineer/technician.

Once you determine the application size then a call to Goodman Technical Service Support will yield the proper size orifice required however you must have a certified, licensed HVAC technicain perform the needed replacement.

Good luck.

Hope this helps.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Commentator

Join Date: Mar 2006
Location: Central Canada
Posts: 84
Good Answers: 2
#35

Re: Why Is My Janitrol Unit Not Blowing Air?

11/14/2013 9:11 PM

The unit outside has nothing to do with the air-flow through-out your house, the air flow to the vents comes from the main unit that is seen in post # 11. It will be a squirrel cage fan, run direct from the motor or is may be belt driven. Belt may be broken or loose, fan is siezed or motor problems. Make sure you disconnect the power to both units before putting your hands in there. Good luck...Rescue

Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#36

Re: Why Is My Janitrol Unit Not Blowing Air?

11/15/2013 11:48 AM

If the fan is truly running but no air is circulating you have air blockage somewhere in the duct sytem or the unit. I suggest you hire a genuine pro to investigate.

Good luck.

Lou Bindner

Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#37

Re: Why Is My Janitrol Unit Not Blowing Air?

11/15/2013 1:59 PM

The problem is that it is a Janitrol system. absolute junk builder's grade (and then only barely) crap.

call the guy and get a quote to scrap that POS and replace it with a real HVAC system.

__________________
Who is John Galt?
Reply Score 1 for Good Answer
Commentator
United States - US - Statue of Liberty - How's it going?

Join Date: Oct 2012
Location: USA
Posts: 95
Good Answers: 4
#38
In reply to #37

Re: Why Is My Janitrol Unit Not Blowing Air?

11/16/2013 7:00 PM

If the fan is truly running the condenser may be frozen up. Turn the AC Off and the Fan ON and let the ice melt. You should start to feel the air at the registers in an hour or so. Let it run for a bit longer to make sure all the ice is gone. If the problem was caused by a bad capacitor it should be fine. It might be time to replace the blower fan motor. Usually under $100.00 if the cap goes out again.

I have done this several times and each time it lasted a year or two.

If the system is older than 15 years. Save some money and get a new system. The new ones are much more efficient and will save you money on your cooling bill.

__________________
If you can't explain it simply, you don't understand it well enough. AE
Reply
Commentator

Join Date: Nov 2012
Location: Central New York
Posts: 84
Good Answers: 4
#39
In reply to #38

Re: Why Is My Janitrol Unit Not Blowing Air?

11/18/2013 9:31 PM

There may even be a rebate or energy credit towards a new unit. Even if you figure out what the problem is, you don't have the tools to fix it. If you had the tools, you would know what is wrong.

Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#40
In reply to #39

Re: Why Is My Janitrol Unit Not Blowing Air?

11/18/2013 10:15 PM

If you had the tools, you would know what is wrong.

Amen!

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Reply to Forum Thread 40 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

babasiga (1); dvmdsc (3); Fredski (6); guds777 (2); JCase (6); LongintheTooth (1); Lou Bindner (1); lyn (1); mcap (2); mrswamy (1); nvirciglio (1); old salt (1); ozzb (1); Rescue (1); Ried (1); Rorschach (1); SHOCKHISCAN (2); SolarEagle (3); Tornado (1); unclefastguy (1); Wal (2); walt (1)

Previous in Forum: Recovering Rechargeable NiCad Batteries   Next in Forum: What is the Best Way to Pay for Things When Traveling Overseas?

Advertisement