SCR Bay Repair

12/10/2013 8:54 AM

I am working on a task in which we have to repair four numbers of SCR BAY , the Scr bay is fed with 600 V Ac and it gives output - 750 Volts DC .

These four Number - big Panels are resting in our workshop for years but now we have to make them like New, if not that then very close to new .

we have been dismantling the different parts from the Scr bay , cleaning it and putting it back , mainly there are three sections , upper most is a circuit breaker , followed by SCR BRIDGE section and at the bottom is the DC CONTACTORS section ,'

We are dismantling parts cleaning them, with CRC, and putting them back, after testing components.

Now my boss told me that i have to make a list of Parts which we will need in order to repair it , they are going to quote according to this list to the customer , my question is

Microswitch

1) There are certain components like Micro switch which rests on the fuse and when the fuse is blown a red clip is pushed out , which changes the orientation of NO and NC contacts fixed on it --- i have good micro switches , and some little jammed but i hope they will work fine as well , Now when deciding how many Microswitches i will need there are two options I have either I replace all of the microswitch , or I replace the faulty ones , if a replace all then it will cost more and it seems like it will be a waste of money , but if I only replace the faulty ones it will save some money , however there will be old microswitches and new one in the SCR which may look odd , My boss has no problem with both choices … I have thought about it and it seems I am a little miser so I have ordered 12 microswitches , to replace all we would have to order 24 Microswitches .

WHAT WOULD BE A GOOD DECISION IN CHOOSING THE QUANTITY OF MICRO SWITCHES ?

THYRISTOR

2) All the THYRISTOR which we took out of those bay are working good , we tested them using a kit , connecting anode , gate , cathode to the kit and then a push button is pressed , if the THYRISTOR is good A BULB FIXED in the kit glows. Otherwise NOT. Some of the THYRISTORS are having little corroded surface , not too much only little , my boss again has no problem if I use the same old ones or I change the corroded ones - the confusion what I am having in deciding the quantity of thyristor is if

I replace a few and rest are old is that a good idea or , should I replace all or none ??

- What about the corroded thyristors , can they be used ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: SCR Bay Repair

12/10/2013 9:15 AM

If you really "have to make them like New", you'd better replace the lot (all microswitches and all SCRs).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: SCR Bay Repair

12/10/2013 9:30 AM

The only advantage you get from cleaning electronics is the heat transfer is a little more predictable. (Depending on the ventilation and skills of your technicians, by cleaning and disassembling you may have lost critical evidence of this circuit and components.) Disassembling an SCR bank and not replacing all of the SCR is just making it less reliable not more reliable. Save the old SCR as spares. The micro-switches should be a trivial cost in this process, replace the whole fuse assembly with opto-coupler based fuse indication. No moving parts or long term unused contacts to oxidize.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: SCR Bay Repair

12/10/2013 10:07 AM

I would take four points into consideration for your decision:

  1. What's the cost of an unscheduled outage if a thyristor fails?
  2. What is the cost to disassemble the SCR, replace a failed part, then reassemble the SCR and return to service?
  3. What is the expected lifespan (MTBF) for the thyristors and microswitches?
  4. How much do the switches and thyristors cost?

If an unscheduled outage causes a serious financial penalty, replace all parts.

If the cost of replacing the parts is significantly more than the total cost of the additional new switches and thyristors, replace all parts. If the parts are expensive relative to the cost of installation, thoroughly test the old parts and keep the ones with pass.

If the parts have reached 90% of their expected life, replace them.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: SCR Bay Repair

12/10/2013 10:45 AM

The lifespan of SCRs that have not been abused is virtually forever.

The likelihood of SCRs that were in service not having been abused in some way at some time is virtually nil.

The gamble is in deciding the level of risk you are willing to take to save some money, and as was said, the cost in down time that this risk represents. The reward is just the little bit of money you save now by not replacing them. Prudence would dictate the lower risk of replacing them prophylactically.

By the way, on large SCRs like that, you must test them WHILE FULLY CLAMPED INTO THEIR HEATSINKS. Testing them loose on the bench is NOT a valid test, the clamping pressure is a necessary component. The typical SCR test involves checking the resistance across each SCR set while clamped, to see if the resistance is greater than 10k ohms. If it is, they should be serviceable, if not, they are bad or about to be.

By the way, if what you are saying is that some of the SCR pole faces are corroded, that implies you removed them from the heat sink assemblies. I would be VERY suspicious of any corrosion on SCR pole faces, because that implies they were assembled without "thermal grease" and implies that they were replaced in the field already by someone who did not know how to to it correctly. If what you meant was that some of the HEAT SINKS are corroded, that implies serious abuse, ie inappropriate moisture intrusion at some point. I would take that as meaning the failure risk is VERY high for the ENTIRE system.

Lastly, there will be a firing board(s) on the controller, including a circuit with a pulse transformer and pulse charging capacitors for each SCR gate circuit. If this has been sitting unpowered for more than a few years, those capacitors will have de-formed their internal oxide layers and will fail very quickly now, which results in misfires and can take out the SCRs. I would replace all capacitors on all boards. Sometimes on cheaper firing boards, the pulse transformers are cheap little cloth wound ones and the insulation will deteriorate, especially if there was any moisture present at any time. We're it me, I would see if anyone makes a new replacement firing board for that unit.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
2
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #4

Re: SCR Bay Repair

12/11/2013 7:33 AM

Very good and useful advice.

But you and all the others here apparently missed one VERY important point with regard to replacement SCRs, they MUST be rated for at least DOUBLE the supply voltage to be reasonably reliable.

(I do believe that the OP has not mentioned the type number for his SCRs, nor the body type, so I can only be of limited help.....)

An even higher rating may be needed in a location where a lot of "noise" is on the mains AC....a mains monitor may even need to be installed and used in some problem places (been there, done that and got the T-Shirt!!).

I looked on ebay and if 50 amp ones are at all helpful (for lower currents I would still stay with 50 amps or more for reliability), look here:-

http://www.ebay.de/itm/BTW691200-ST-Microelectronics-50A-1200V-TOP-3-SCR-THYRISTOR-/121103814873

I would personally replace all the older SCRs with new ones of at least 1200 Volt rating (I was not the first to say that either!).

The old ones, if at least 1200Volt, might be kept as "tested" spares only.....reliability is usually highly important....better would be new ones.

Best of luck.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: SCR Bay Repair

12/11/2013 10:52 AM

Actually, the recommended minimum PIV (Peak Inverse Voltage) rating of an SCR is 2.5 x the line RMS voltage, some say 2x the PEAK voltage, not the RMS, which works out to roughly 2.8x the RMS voltage. I would not use SCRs for a 600V RMS line supply that have a PIV rating of anything less than 1600V, then 1800V is very common on quality systems. But assuming his rectifier was properly rated before it was taken out of service, and he matches part numbers for replacements, that should not be an issue.

The good point you and SHOCKHISCAN raise however is that SCRs cannot be simply replaced with similar devices, they must be replaced with EXACT devices, or those recommended by the OEM ( if they still exist).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #7

Re: SCR Bay Repair

12/13/2013 7:22 AM

Thanks for clearing that up a bit more accurately than I did.

Installing US built computer equipment in the early 80's here in Germany made me aware of the problems (then!!), I was posting from memory, which can be a little less than accurate!!!

We at the time, replaced all the 600v SCRs with 1000v SCRs and realised a great fix, but with a massive amount of work.....

I will remember your infos for any future events, thanks.

Erring on the side of a too high PIV appears to be the "best" failure to commit.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Apr 2012
Location: Sanskrit
Posts: 57
#9
In reply to #5

Re: SCR Bay Repair

12/12/2013 10:47 AM

Hi Andy

the scr we are using is this one

http://www.ebay.co.uk/itm/Westcode-N540CH18-SCR-/181149373854

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #9

Re: SCR Bay Repair

12/13/2013 7:35 AM

WOW, that thing is HUGE!!!

Much beefier than any I have ever worked on myself, though of course the principles are the same!!!!

Never forget that on ebay they are many forged components, so although your testing will find a defective SCR, but even a forged one out of China will still pass that test......but may fail in normal usage.

Maybe you need to be thinking about a "full-blown" test(er) that explores the full allowed parameters to allow each device to be properly tested individually before installation.

Its a sad state of affairs that companies are forging almost everything nowadays.....even flight safety airplane parts.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Apr 2012
Location: Sanskrit
Posts: 57
#8
In reply to #4

Re: SCR Bay Repair

12/12/2013 10:44 AM

Thank you very much JRaef for your answer . It has been very helpful

we have tested all the SCR loose on the bench , using a kit which works on 12 volts Dc , we connect leads to anode cathode and the gate , a push button on the test kit is pressed and if the SCR is good a bulb lights up if bad the bulb wont light up .

and Yes we have got a firing transformer and capacitors .

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12
In reply to #8

Re: SCR Bay Repair

12/13/2013 11:57 AM

we have tested all the SCR loose on the bench , using a kit which works on 12 volts Dc , we connect leads to anode cathode and the gate , a push button on the test kit is pressed and if the SCR is good a bulb lights up if bad the bulb wont light up.

Never heard of a test like that, but it sounds as though you are only testing the gate itself, not the actual device capability under compression. "Good" and "bad" in SCRs are only clearly different at the extremes. That means this kind of test will only weed out the spectacularly failed SCRs, they may still not work when you put them in, clamp them, and expect them to turn off when you want them to. The anode to cathode resistance test under proper clamp pressure is the only thing I would consider valid.

Good luck!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: SCR Bay Repair

12/11/2013 9:01 AM

A word of caution in addition to all of the excellent advice already posted.

Timing signals and firing of individual SCR units is critical to controlling voltage output level, waveform shape, and in preventing "out of phase" firing that will destroy the bridge and/or components.

SCR transient "on" and "off" times as well as "forward" and "reverse" resistance are different from one application design to the next.

It is critical that you replace the components with devices that accurately mimic the design specifications and failure to do so will result in poor performance and/or failure(s).

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!