Cable Size Calculation Formula

12/27/2013 10:35 AM

2 X I X PF X L / 45.5 X 4 is this formula is right.and can you explain the 45.5 X 4.why we wanna divide by this value.

for example i made the calculation with 22.3amps,0.90 power factor and 164 mts length of cable. so i got answer is 36.17.so we can use 35sqmm copper cable for this apparment load. any one can explain is this right formula.......

Register to Reply
Pathfinder Tags: cable size calculation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: cable size calculation formula

12/27/2013 10:49 AM

If you don't divide by that value, you will need a really humongous cable.

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: cable size calculation formula

12/27/2013 11:40 AM

If you did not get this formula from your region's electrical code book then you probably have the wrong formula. I don't like the mixture of units nor having constant integers that are multiples of each other in the numerator and denominator of this equation. However, a formula like this might be a simplified method to generate a look-up table.

If this formula and your mathematics is correct, your conclusion is dangerously wrong. The code book and any formula inside it produces the minimum safe wiring for your application. You calculated 36.17 so 35 mm^2 is undersized wiring for this application. You should find the next larger available wire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#3

Re: cable size calculation formula

12/27/2013 12:03 PM

When evaluating any formula, one must understand all the units of measure used in the formula, and the answer must be in consistent units. In your formula the only units you give are amps and meters (PF is a unitless ratio). How do you get mm2 from these two units? The answer to this should explain where the other numbers come from, and will help you to understand the formula.

__________________
The older I am, the better I used to be
Register to Reply Score 1 for Good Answer
5
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5

Re: Cable Size Calculation Formula

12/27/2013 12:19 PM

Cable sizing must factor in at least the conductor material, cable construction, type of insulation, ambient temperature, number of conductors, length and enclosure - and mabe some other variables I've overlooked.

Which is why code books have tables of conductor sizes for various types and routing methods, and may also have derating factors which must be applied.

There is no "one size fits all" formula that can be applied.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 5)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6
In reply to #5

Re: Cable Size Calculation Formula

12/27/2013 12:46 PM

Good Answer John! It never ceases to amaze me how many people seem to think that all you need to do is to memorize a "magical" list of formulas.

These guys end up doing serious damage as managers, more often than not. They are always looking for the quick answer without having to understand where it came from.

Knowledge is handy. Understanding is better. Knowing how to apply it, is best.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#8
In reply to #5

Re: Cable Size Calculation Formula

12/27/2013 9:20 PM

Interested to know who thought it was an off-topic answer (not that I give a shit. Let the OP fry themself if that's the consensus).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Cable Size Calculation Formula

12/27/2013 9:38 PM

Maybe OP has an idea who?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#10
In reply to #9

Re: Cable Size Calculation Formula

12/27/2013 10:23 PM

Be pleasantly surprised if OP has an idea .

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Cable Size Calculation Formula

12/27/2013 10:26 PM

Touche′.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Cable Size Calculation Formula

12/27/2013 1:32 PM

This appears to be a formula for single-phase voltage drop, with some of the variables already plugged in. The 2 in the numerator would account for conductor length both ways. Wild guess, the 4 in the denominator could be the chosen allowable percentage of voltage drop.

For this length of run, the voltage drop calculation leads to a larger wire size than ampacity alone would require.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12

Re: Cable Size Calculation Formula

12/28/2013 12:37 AM

If 4 is 4 mm^2 [the conductor cross sectional area] then this formula could be the voltage drop in a case of a single phase [line and neutral] supply cable.

Voltage drop=2*I*[R*cos(fi)+X*sin(fi)]-simplified formula- and neglecting X it is Voltage drop= 2*I*R*cos(fi). R=ro*L/mm^2 ro=1/58 ohm. mm^2/m [copper 20 dgr.C] and for 90 dgr.C =1/58*(234.5+90)/(234.5+20)=0.022=1/45.5. (neglecting skin and proximity effect-for 4 mm^2 it can be neglected indeed). I is in [ A] and L in [m].

Then if I=22.3 A cosfi=0.9 L=164 m voltage drop=40.2 V

For 230 V rated voltage 40/230=17.4% [usually maximum permissible for steady state could be 5% then a 16 mm^2 will be required].

Of course, as JohnDG explained it very well, it is not the single criterion-ampacity is the first and short-circuit current withstand could be another.

__________________
Julius
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#13

Re: Cable Size Calculation Formula

12/28/2013 11:39 AM

Volts drop in a cable is I x R, and power is I2 x R. Power factor is always 1.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#14
In reply to #13

Re: Cable Size Calculation Formula

12/28/2013 2:21 PM

Sorry, Horace40, if it is a joke IMO it is not funny!

__________________
Julius
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#17
In reply to #14

Re: Cable Size Calculation Formula

12/29/2013 1:48 PM

Hello 7anoter4, for the benefit of others, perhaps you would be good enough to explain the unfunny bit.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#18
In reply to #17

Re: Cable Size Calculation Formula

12/30/2013 9:31 AM

The OP is speaking about "pf" [power factor=cosine of angle between Voltage and Current in the same circuit] .This cannot be something else but "alternative current" [a.c.] and "pf" it may be any value from 0 to 1 [lagging or leading].

A cable supplied at one end with a voltage lets through it a current as required by supplied installation at the other end and the cosine is determined by the receiver mainly.

In a.c. a cable has resistance and reactance always.

See [ for instance ]:

http://okonite.com/engineering/voltage-regulation.html

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#19
In reply to #18

Re: Cable Size Calculation Formula

12/31/2013 11:20 AM

Thanks 7anoter4 for the explanation and the link.

The current in my formula is I, resulting from the combined effect of all the resistances and reactances in the whole circuit, and the voltages and frequency causing the current to flow.

R is the resulting impedance of a copper wire where capacitance and inductance are usually marginal at mains frequency and likely to cancel out, just leaving the pure resistance component.

The instantaneous volt drop is I x R, where there is no cosΦ component.

That's my simplistic view. Simple Ohm's law is a powerful tool to have when the going gets complicated.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#15

Re: Cable Size Calculation Formula

12/28/2013 3:18 PM

You really need to get a look at the IEE regs for cable sizing. There are many things to take into account such as where the cable is running (under insulation or under the ground) is it a single cable or is it run with a group of many other possibly hot cables. Will your cable run with other cables that might only be rated to 70deg C. Spare a few thoughts on the protection available. Again this will add to the cable size. God forbid but Volt drop .....% ?? Leave Horace with his DC - he seems happy!! Over and out.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16

Re: Cable Size Calculation Formula

12/29/2013 2:03 AM

By-the-way, the NEC 310.15(B)(16)- any running system but 30 dgr.C ambient-ampacity of 6 Awg (90dgr.ins.) is 55A [6 Awg is 13.3 mm^2].IEC 60364-5-52 installation group A2" in a thermally insulated wall" for 16 mm^2 30 dgr.C ambient recommends 73 A. From BS7671 the minimum-minimorum will be 68 A permissible for 16 mm^2.

Usually in low voltage system of 400/230 V the maximum short-circuit current could be 5 kA [rms].Neither NEC nor BS7671 recommends any appreciation about conductor short-circuit withstanding.IEC 60364-5-52 I=K*mm^2/sqrt(time) K=143 -XLPE ins.Following this 16 mm^2 withstand only 4.57 kA within 0.25 sec fault clearing time.

__________________
Julius
Register to Reply
Active Contributor

Join Date: May 2009
Location: Luanda,Angola
Posts: 13
#20

Re: Cable Size Calculation Formula

01/03/2014 12:05 PM
as per drawing, i wanna run the VD40-H1VV-R5G16sqmm cable from the basement MV Panel to 16th floor apartment through electrical shaft.cable layed on cable tray, .total running meter is 251m.The apartment load is 31.7 kva.

and i get the 50sqmm cable size from the online cable size calculator.

let me know which cable size is suitable for this apartment load and how we can make calculation for suitable cable.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#21

Re: Cable Size Calculation Formula

01/03/2014 1:21 PM

This really is time to pay an engineer to do this calc. It will save you a lot of money and won't waste the fire brigades time.

You don't say what voltage you are operating at. In your last post you give us the load as 31.7kVA. At 230V its a 137A but at 110V its 288A. Who knows it might even be 400V TP&N.

Strangely it is now many metres further to your apartment. Have you stopped off at Mr Slacks for some tea. Incidentally Mr Slacks copy of the IEE regulations will show you how to make this calculation.

Regards

Silverfox

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22

Re: Cable Size Calculation Formula

01/06/2014 6:47 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (4); Anonymous Poster (1); gringogreg (1); horace40 (3); jayaprakash (1); JohnDG (3); lyn (3); NotUrOrdinaryJoe (1); PWSlack (1); redfred (1); silverfox (2); Tornado (1)