Single Phase CT Metering

12/29/2013 3:49 PM

has anyone ever seen the sources power on a single phase service go thru a single ct but one phase goes thru one way and the other phase goes thru the opposite direction

Register to Reply
Pathfinder Tags: single phase ct metering
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: Single Phase CT Metering

12/29/2013 4:20 PM

Yes.

This depends on your material, like the meter unit. There are systems with 2 wire, 3 wire and also with reversed inputs. We do not know what country you refer to.

__________________
Plenty of room here
Register to Reply
Member

Join Date: Dec 2013
Posts: 7
#2
In reply to #1

Re: Single Phase CT Metering

12/29/2013 4:40 PM

Good old USA

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#8
In reply to #2

Re: Single Phase CT Metering

12/29/2013 10:06 PM

Big business for the meter reader, if one CT is used? Is the 180 degrees shift clear?

__________________
Plenty of room here
Register to Reply
Member

Join Date: Dec 2013
Posts: 7
#9
In reply to #8

Re: Single Phase CT Metering

12/29/2013 11:12 PM

Not sure what you mean by 180 degree shift clear. Our kids have bought this house and the power bill is very sporadic 700$ this month for a 2500 sq ft house. Way out of the norm for this area.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Single Phase CT Metering

12/29/2013 11:20 PM

That seems high, but do they have electric heat? Where is this, and about what price per kwh?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#58
In reply to #2

Re: Single Phase CT Metering

01/06/2014 6:42 AM

Isn't it a rather young country, though?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 6)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Single Phase CT Metering

12/29/2013 6:08 PM

Yes, if the purpose is to add the power delivered through both lines.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4

Re: Single Phase CT Metering

12/29/2013 7:40 PM

You say "single phase", then talk about "the other phase". Are you referring to phase and neutral? If so (unless there was a nasty earth fault), the CT would either "see" double the line current, or zero (depending what you mean by "the opposite direction").

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Member

Join Date: Dec 2013
Posts: 7
#6
In reply to #4

Re: Single Phase CT Metering

12/29/2013 8:52 PM

This is a 120/240 volt residential signal phase service. there is one CT donut installed by the power company. one of the power conductors goes thru from top to bottom, the other power conductor goes thru from bottom to top . I have never seen this arrangement before.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Single Phase CT Metering

12/29/2013 9:52 PM

Because of their opposite phasing, if the wires went through the same way, you would be measuring the difference in currents; i.e., earth leakage. That is also done, but for a different purpose from measuring energy consumption. See #3.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Single Phase CT Metering

12/29/2013 7:56 PM

In alternating current, any phase goes one way half the time and the other way the other half of the time.

Is this what you mean?

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#11

Re: Single Phase CT Metering

12/30/2013 12:01 AM

Do they have estimated readings every so often? If so they could be using more electricity on months that the reading is estimated. (This is sometimes called "Taking the reading from the bus") When an actual month's readings are taken adjustments are made to catch up on the actual vs. estimated. For example If they use $200/month and are only being billed an estimated of $120/month the difference accumulates and is billed along with one months actual usage on months that an actual reading is done. 5 months estimated at $120 estimated with $200 actual and the actual of $200 for the month of the reading is 5 months actual - estimated = 5*($80 shortage) = $400 difference between actual and estimated. This plus reading month of $200 = $400 & $200 = $600 for a actual month when the meter is read and billing adjusted.

This many not be the reason but it quite often is why for several months being the same billing and then either a lower or higher on the month the meter is actually read. Check the old bills or discuss this with the electric company.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#12

Re: Single Phase CT Metering

12/30/2013 12:39 AM

By ct, I assume you mean Current Transformer. Are you sure this doughnut is a Current Transformer, and not just a ferrite core to keep RF from entering/exiting the home via the power line?

I'm quite familiar with current transformers, and fairly familiar with residential kWh meters. I've never seen a residential kWh meter that had an external CT. Of course just because I've never seen one does NOT mean they don't exist...

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 2 for Off Topic
Member

Join Date: Dec 2013
Posts: 7
#14
In reply to #12

Re: Single Phase CT Metering

12/30/2013 12:50 AM

I have a picture being emailed tomorrow so will try to attach it. To the best of my knowledge and from past experience it definitely is a ct. This is baffling at best:-)

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: Single Phase CT Metering

12/30/2013 1:55 AM

It might be less baffling if you read and respond to the posts that explain it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Dec 2013
Posts: 7
#20
In reply to #15

Re: Single Phase CT Metering

12/30/2013 12:51 PM

I do appreciate all the comments but am only able to check the site periodically. I have read each comment and am grateful for all of the input.

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#43
In reply to #12

Re: Single Phase CT Metering

12/31/2013 3:53 PM

Here the "electrical inspection" made us install a 400 Amps service with CT can and 500 MCI connections. They come to the service with a 1/0 for 200 meter to the transformer. Our monthly bill is less than $100.00. It happens all the time, come and see.

Understand who can.

__________________
Plenty of room here
Register to Reply
5
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#13

Re: Single Phase CT Metering

12/30/2013 12:43 AM

In the US and Canada this is perfectly normal. Remember you have single phase system, really a 240V supply with a center tapped winding, the center tap tied to ground at the entrance to your house and renamed "neutral". So from either outside or "hot" leg to neutral you have 120V, from hot to hot you have 240v. To monitor power you need to sum the current in the hot legs and multiply by 120V, remember thought that in effect the hot legs are 180 degrees out of phase, hence passing them through the CT in opposite directions. Things like stoves and dryers go right across the hot legs, so they generate no current in the neutral,, by summing the current in the hot legs and multiplying by 120 you get power, integrate that and you get energy.

Martin

Register to Reply Good Answer (Score 5)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#16

Re: Single Phase CT Metering

12/30/2013 3:41 AM

For a residential home, a CT could be used if the meter is digital electronic type.

I the meter is a mechanical type with a rotating disc, it would be unlikely to have a CT.

In any case, the CT will have 2 wires coming out of it and connected to the meter. These are from within the CT and not the ones passing through the center of the CT.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #16

Re: Single Phase CT Metering

12/30/2013 11:16 AM

"...the meter is a mechanical type with a rotating disc, it would be unlikely to have a CT..." Digital or mechanical, a meter is a meter.

It is common practice to use CTs in rural areas where the utility company/coop only stocks one type of meter and uses CTs to adjust for the difference in loads between a farmhouse and say a milkhouse, or where there is a single drop from the line where the CT measures the current ahead of multiple overhead secondary taps distributing power to a cluster of buildings.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#17

Re: Single Phase CT Metering

12/30/2013 7:48 AM

Since your 2 phases are 180 degrees out of phase, running them through the current transformer in opposite directions gives the sum of the currents in the two phases.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#19
In reply to #17

Re: Single Phase CT Metering

12/30/2013 12:31 PM

In this case, the CT is measuring twice the current .... therefore, it could be multiplying the reading by 2. A CT is meant to have only one line through it only. Having it wired like this looks wrong but it all depends on the way the meter is built or the ratio of the CT compared with the meter expected CT ratio.

Must get the Utility company to check this setup and explain to the OP.

Register to Reply Off Topic (Score 3)
Member

Join Date: Dec 2013
Posts: 7
#21
In reply to #19

Re: Single Phase CT Metering

12/30/2013 1:05 PM

Thank you all for your input. The utility company has been notified and we are taking it from there. You have given me valuable options to present to them.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#22
In reply to #19

Re: Single Phase CT Metering

12/30/2013 3:30 PM

"...A CT is meant to have only one line through it only...", a common misconception. A CT is a vector summing device, it uses both magnitude and angle to net out what passes out through the secondary. We all have CTs in our houses, they're in our GFIs where both hot and neutral wires pass through the same CT in opposite directions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#25
In reply to #22

Re: Single Phase CT Metering

12/31/2013 3:39 AM

Maybe I did not use the full definition here: In this OP context, we are discussing a metering device and not a differential current measuring for protection, device.

In this context, a CT is used to measure the amount of current going through, in view of metering the power being consumed. therefore, You would not have 2 phases or 3 phases or a phase and neutral wires going through the same CT. This will fail the objective of this device as a current transformer only and not a protective device, measuring a current difference.

Therefore, your response to my comment is misleading and not precise. It does not explain or improve the flow of info to help the OP or any one else.

I do not know why you received any GA for your comment since it does not answer any question in this thread but just makes a useless contribution.

Thank you

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#26
In reply to #25

Re: Single Phase CT Metering

12/31/2013 3:46 AM

It is precisely the opposite directions of the conductors that makes the OP's CT additive rather than differential. I have explained this more than once already; RAM is right and you are wrong. So have another OT.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#27
In reply to #26

Re: Single Phase CT Metering

12/31/2013 3:57 AM

Sorry to disagree with you.

Ramconsult mentioned something else than the additive effect (which I did mention before as being additive and maybe required by the metering device as a multiplication factor (although this is unlikely since the meters do have settings for such...) Please re-read his comment instead of just siding as buddy-buddy...

Thank you for the OT it does not bother me. It is actually off topic since it does not fit in the answers to the op's. So should, also, be your comment! Maybe you should OT your's and I leave it to you.

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#28
In reply to #27

Re: Single Phase CT Metering

12/31/2013 4:11 AM

You're wrong again, twice. But I can give only one OT, so you get a freebie.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#33
In reply to #28

Re: Single Phase CT Metering

12/31/2013 7:11 AM

A CT on an energy meter can only have one cable(phase) through it. There is no need for any other cable to go through it and it is highly irregular. If you just stop thinking that you might be the only specialists around (like some other guy here...) maybe you will guess why.

A CT measuring a current differential will have all the cables passing through it, each once and in the same direction otherwise it fails the objective.

Your vocabulary seems limited, today, to just 'wrong' or 'right'.

Explain, since you seem to be a specialist (or Dmsc...), why a CT will be having 2 wires from different phases ( or phase and neutral), going through it in a way to add the currents, for the purpose of metering the energy being consumed?

Also, some people in this forum have to accept that it is not restricted to 'Specialists' and if so, then let every contributor submit his credentials.

Register to Reply Off Topic (Score 4)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#38
In reply to #33

Re: Single Phase CT Metering

12/31/2013 2:02 PM

Quote:>>>>>>

Explain, since you seem to be a specialist (or Dmsc...), why a CT will be having 2 wires from different phases ( or phase and neutral), going through it in a way to add the currents, for the purpose of metering the energy being consumed? <<<<<<

When I mentioned specialists, I meant other posters that studied enough and gathered experience with the US grid system. Not me. I am just checking posts and commenting to answers that are incorrect. (IMHO)

Our sponsors, who pay for this forum, deserve a no nonsense informative forum. I am happy to participate and see this as a minimum ethic, call it pride perhaps.

I have no clue where you are from and you might not be familiar with the split phase system.

In a regular single phase system as used in Europe and the UK there is no center tab in the 240 Volts (220 or 230) single phase, used as a neutral. One of the wires is connected to the neutral there. The other provides the hot line.

There I can understand, you do not put more than 1 wire through the CT because it makes no sense to put more, since the reference voltage is always the line voltage.

(say the same 220 or 230 Volts AC)

In the US, Canadian, Bahamas- system there is 120 Volts -N- 120 Volts, so that neutral is in the center of the low voltage part of the line transformer, making it possible to feed 120 volts instruments between the neutral and L1 or the neutral and L2. Suppose your girlfriend irons your cloths and uses a 120 VAC iRon between the neutral and leg 1 (the leg that goes through the CT)

The meter will register the power through the CT. (In this case 1 wire goes through the CT - the hot leg L1)

How can the same meter register the power used with my 120 Volts coffee machine that is connected between the neutral and L2?

Guess: by putting a second wire through the CT that runs the current, produced in L2 (the coffee machine)

Since in reference to the neutral the phase in L1 and L2 is reversed (180 degrees shift) the second wire has to go in reverse direction through that same CT.

Example: the iRon (the most practical tool of the "i" family) uses 750 watts and the coffee machine 1000 Watts.

With 1 wire, you use 750 Watts and the coffee machine has a free ride.

With 2 wires in the same direction, you will get 1000 - 750 = 250 registered (Look @ the minus sign, pointing to a differential as Tornado states in his posts)

With 2 wires, one in the opposite direction, you will get 1000 + 750 = 1,750 Watts. (adding up the values, what keeps the power company happy)

This being said, you could also put the neutral only through the CT, but that goes completely wrong: When the ironing is done and the coffee is ready it shows no power used. If I switch on the A/C that needs 240 VAC between L1 and L2, I go for a free ride on this one, since there is no current applied through the neutral.

As I wrote in earlier posts, the use of one CT or more CT's in residential power apps. has to do with the way the meters are able to receive info. Personally, I have seen systems with 2 wires through 1 CT as well as 2 CT's, each with one wire through it.

I get a happy feeling, to know that you will enter this new 2014 with a little more information that perhaps might find its way to enrich your knowledge. If this comes true, we both have learned something. Happy New Year. D.

__________________
Plenty of room here
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#34
In reply to #28

Re: Single Phase CT Metering

12/31/2013 7:28 AM

Once more (and I hope the last), a GFI is a Ground Fault Interrupter and it measures the currents flowing in opposite directions from the Supply to the load, thus subtracting them to check that there are no leaks to ground from the side of the load. The cables are not run in opposite directions through the CT! It is the current that flows in opposite direction (maybe RamConsult can be informed by you? He will be reading this maybe).

This is different from CT intended to be used on Energy meters. Here there is no subtractions nor additions.

Happy new year to all

Register to Reply Score 2 for Off Topic
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#29
In reply to #26

Re: Single Phase CT Metering

12/31/2013 4:21 AM

I find it a pity that no more "specialists" come up with their opinion. Just like in a few other cases where the right answer was been highlighted by only 2 individuals, answering the O.P. bluntly wrong.

I vote you a G.A. and Luke also gets another O.T. from me. I have been waiting for the evolution of this post to pick up the tread again. The function of the neutral has been misunderstood again.

__________________
Plenty of room here
Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#30
In reply to #29

Re: Single Phase CT Metering

12/31/2013 4:41 AM

If a few more specialists come forth, maybe we can have a real donnybrook.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#31
In reply to #30

Re: Single Phase CT Metering

12/31/2013 4:51 AM

I thought this was Irish?

__________________
Plenty of room here
Register to Reply Off Topic (Score 6)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#32
In reply to #31

Re: Single Phase CT Metering

12/31/2013 5:00 AM

I think so, and also supposedly have a bit of that in me.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#49
In reply to #19

Re: Single Phase CT Metering

12/31/2013 10:14 PM

You can have as many lines through as you want. The flux around the outside is proportional to the net current through the hole as per Maxwell's equations. In this case, the power consumed (assuming unity power factor) is 120 volts times the total current (rms). If you have a load phase to phase (240 volts) your current gets counted twice but your voltage is double, so the power is still figured correctly.

Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#50
In reply to #49

Re: Single Phase CT Metering

01/01/2014 6:17 AM

Please re-read your statement. Something is wrong in the conclusion.

To All: Oscarphilips gave the explanation to the topic question put by the OP. That is clear and thanks'

The Only thing that bothers me, is the final division by 2. Is this programmed in the meter software /hardware?

Register to Reply Off Topic (Score 6)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#52
In reply to #50

Re: Single Phase CT Metering

01/01/2014 8:17 AM

For a resistive load, the total power consumed is the sum of the phase currents times the phase voltage (120 volts).

Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#53
In reply to #52

Re: Single Phase CT Metering

01/01/2014 8:49 AM

Apparently, the phase voltage (L1-L2) would be 240V connected to the meter.

If 120V (L1 or L2 with Central point (Neutral) is used on the meter, then you would be right.(??)

Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#54
In reply to #53

Re: Single Phase CT Metering

01/01/2014 4:13 PM

Center tap of secondary winding of transformer at pole is neutral to the house. Other leads are 120 vac with respect to neutral (which is grounded). Voltage from one phase to the other is 240 volts. Wall outlet neutral to hot (one phase or the other) is 120 vac. Single phase load has current counted once by CT and current returns through the neutral. Phase to phase load (240 vac) has current counted twice but is consuming twice as much power because it's voltage is 240 vac. In either case, the power consumed is 120 vac times the current reading from the CT.

I hope this clarifies my earlier post.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#23
In reply to #17

Re: Single Phase CT Metering

12/30/2013 8:13 PM

There is only one phase.

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#24

Re: Single Phase CT Metering

12/30/2013 8:28 PM

In this system the reference voltage will be from L1 to Neutral for power and power factor calculations. Voltage imbalance between L1 and L2 will show power errors with a magnitude proportional to the voltage imbalance.

Register to Reply
3
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#35

Re: Single Phase CT Metering

12/31/2013 8:17 AM

Doug:

This was common practice for "farm metering" many years back, where the farm load current would exceed the ampere rating of the meter. Typical wiring would be to run L1 and L2 through the CT in opposite directions, with the neutral bypassing the CT. The voltage for the revenue meter would be from L1 and L2. In the billing calculations 1/2 of the CT turns ratio would be used.

Example: for a 200 ampere service, a 400:5 CT would be used. At full load (200 amps per leg) the meter would see 5 amps (2.5 amps due to each leg), and 240 volts ... So the billing calculation (in this case for demand {kW}not energy {kWH}) would be:

5 amps x 400/5 (CT ratio) x 240 volts / 2 (metering correction) = 48 kW

When single leg loads (120 volt) are applied, only ,the current in one leg would be impacted, and measured.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#51
In reply to #35

Re: Single Phase CT Metering

01/01/2014 6:19 AM

Thank you for the clarification details etc. GA

Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#36

Re: Single Phase CT Metering

12/31/2013 12:30 PM

Doug Trud or anyone else, especially a SPECIALIST---

The original question states: "single phase service go thru a single ct but one phase goes thru one way and the other phase".

The following dumb questions are based on being an engineer and hopefully being a reasonable person, a little more intelligent than dumb but according to some not much more---

1) Which ct are you talking about? I can think of at least 5 ct's that come to mind. Give me another 10 minutes and I probably increase that to 10. Electrical answers only please.

2) If you have a single phase service, how can you have two phases? "one phase goes thru one way and the other phase goes thru the opposite direction". If I remember correctly single phase is 1 phase, 2 phase is 2 phases, 3-phase is 3 phases, 4 phase would be 4 phases, etc. Would 10 phase be 20 phases?

3) Are the batteries in my flashlight zero phase? If it is a 3-cell flashlight is it a zero three phase or a three zero phase? Just thought I'd ask since the subject of phases came up.

Happy New Year!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Off Topic (Score 3)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#37
In reply to #36

Re: Single Phase CT Metering

12/31/2013 12:35 PM

"If you have a single phase service, how can you have two phases?" - I asked (implicitly) for clarification on this in #4. Still waiting.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#41
In reply to #37

Re: Single Phase CT Metering

12/31/2013 3:33 PM

How can a single phase system have 3 wires with different potential(s)?

The single phase theory ends at the primary (e.g. 7kV) of the line transformer. And all that comes after implementing a split secondary is tradition, deception, misunderstanding and knowledge and hot stuff to write about to kill time.

__________________
Plenty of room here
Register to Reply Score 2 for Off Topic
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#46
In reply to #37

Re: Single Phase CT Metering

12/31/2013 8:43 PM

Your question was answered in #2, #9, .

This is a single-phase, 120/240 volt, three wire residential service in the USA.

You may not be able to answer this from the UK perspective.

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#48
In reply to #37

Re: Single Phase CT Metering

12/31/2013 9:54 PM

In my early days I got fined in the US at the entrance check point of the harbor before boarding a ferry. Because my US picture I.D. (somewhat similar card to a driver license) had expired. My identity had expired and I probably ceased to be who I am. Showing other picture I.D.'s like my I.D. card from my origin (that doesn't expire), my international driver's license (for fife) my residence driver's license and the passports I showed didn't change anything. Law is law. Code is code. It is just pitiful that many times rules and common sense are so far apart. Same happens here. It does no good for the credibility of this forum.

When I O.T. someone, I explain why and repair the situation when I am proven wrong. I am the first to admit my mistakes if I make any.

__________________
Plenty of room here
Register to Reply Off Topic (Score 8)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#40
In reply to #36

Re: Single Phase CT Metering

12/31/2013 2:51 PM

Dear Old Salt,

The 2 phase or 2 leg system mystery will not be solved in our lifetime. Perhaps after we all are metric (metricians?) It is similar to french(ed) fries that are called French fries.

I don't want to spoil your festivities but they, me, you the electrical code had a dilemma to deal with: 1. The long existing 2 phase system (that does not really comply with the multi- phase theory as newer technology implemented)

2. A split system, that is nursed as single phase system, but has all the specifics of a multi- phase system.

To name a few: the phase shift between phases in a 3 phase system is 120 degrees or in general 360 degrees (a complete circle rev.) divided by the number of phases.

A 4- phase system should have 90, a 5- phase 72 degrees, a 6- phase 60 degrees and so on. Some of these angles prove not being practical for circular fields.

So analog, the split phase has a phase shift of 360/2 = 180 degrees, what makes it a perfect candidate to be named 2 phase. My penny is that first all the old 2 phase systems need to disappear before this system gets the rights it deserves. AS long as this is not official, I will use L1 and L2 instead of phase 1 and phase 2.

Who is right and who is wrong? Just don't bother is the message.

A look at the distribution panel can be enlightening.

I am not a prophet or that clairvoyant but perhaps the 2 phase guys are progressive (renovators) and the L1, L2 guys the (disappearing fossil) conservatives?

I wish you a good year ending and a prosperous new year. D

__________________
Plenty of room here
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#42
In reply to #40

Re: Single Phase CT Metering

12/31/2013 3:44 PM

Unfortunately 2 phase in the past referred to a system with a 90 degree shift between the two phases, at one time common in mines. The North American household system is as has been pointed out by myself and others, a single phase system, fed by a centre tapped transformer with the centre tap grounded and called neutral. Your previous post using your girl friends iron explained the reasons for using a single CT with the hot legs passing through the CT in opposite directions.

Martin

Power and Energy Conversion Lab Supervisor

Dept. of Comp. & Elec. Eng.

Royal Military College of Canada

(just in case you wanted some sort of credentials)

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#44
In reply to #42

Re: Single Phase CT Metering

12/31/2013 4:03 PM

Hi Martin,

You are right. Just do not see why you put your answer off topic. A lot of wanderers might miss the light.

For this year I get an iPhone from my wife and I have bought her a iRon, from the same family.

Enjoy your holidays and thanks.

D.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#45
In reply to #44

Re: Single Phase CT Metering

12/31/2013 4:30 PM

It was the 2 phase mine stuff, not really germaine to the household wiring question. I got an iPad,, thought I should see if I can find an iMop to reciprocate...

Cheers

Martin

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#47
In reply to #36

Re: Single Phase CT Metering

12/31/2013 9:04 PM

To all who have presented an answer to #36:

I too have an answer to the question which I consider worthwhile, but at 45 answers posted so far and 9 GA points and 46 OT points is it very evident that it would be possibly be suicide to add to this discussion..

For those with the legitimate phase answers, thank you for your clarifications or reinforcement to what I already knew about legitimate phasing. With the 2 phases and being 90o off of each other I even knew that. My EE father once explained to me about it and said "You will never need it". Then I had a prof who explained it in class. He also said "You will never need it and it won't be on any test". Gosh darn it, it wasn't on the test! They were then elevated to the level of intelligence hero's!

I am regretful though that no one answered my question about the flashlights! I guess I'll have to go to Menlo Park or West Orange, NJ, to find out. And here I thought you guys were the epitome of geniuses.

At 9 GA's and 46 OT's, I'll sit this hand out.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#55
In reply to #47

Re: Single Phase CT Metering

01/01/2014 7:59 PM

Hi Old Salt,

I responded earlier but I see that it is not published. The battery part I do not understand, I might be too dumb.

As far as talking phase in batteries, I see it as asking about the battery's physical condition. like empty, full, loading, discharging.

When it comes to the poles, there is a + and a - and are referred to as the polarity since they have no phase as used in A/C technology. The polarity of each battery and the way you connect them to others. will determine your resulting voltage.

If in your 3 cell flashlight, you reverse 1 battery, you will end up with 1.5 Volts for the bulb or Led.

Regards

D.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#56
In reply to #55

Re: Single Phase CT Metering

01/01/2014 9:54 PM

dvmdsc-

Thank you for putting time into the flashlight problem. I really don't have that type of phase problem because, as far as I know at least, DC has no phases or at least no more than 1/2 phase. Just watch now, someone of astute and self proclaimed superior intelligence will come down on me for being a dumb worthless creature wasting the air I breathe. NO, YOU ARE NOT TOO DUMB, at least as I see it from your answers to questions.

The mention of the batteries was said in jest and with a dose of sarcasm. It seemed to me that the original question was very short on information and that a few posters were getting quite venomous in their replies, some were very damning of others, some seemed clearly illogical and most of all forgetful of the purpose of the forum. Although I have been attacked personally a few times in the past, it has no place here and most members disapprove of it.

I am a human and make mistakes, the less the better. A few others, thankfully only a very small minority, look for an opportunity to attack, The high number of OT's and low GA's seem to show it from both sides on this OP. Some might forget that the purpose of this forum is to help others and not to attack them personally.

As with you, I am familiar with the concept of phases. Sometimes other's terminology takes a little time to adapt into my thinking but seldom stops it. My "question" about the phases greater than 3 was also intended as a ridiculous way of getting contributors back to earth and the original question. If I hurt anyone's feelings or caused them to lose precious time I am guilty and apologize profusely. EE is one of the most expansive areas of engineering and I will be the first to state that I, as hopefully others do, realize that I know only a tiny bit of all that it encompasses. First of greatest importance is the need to remember that we are humans and not perfect.

Thank you for your reply and I hope the NEW YEAR has been a good one for you so far and continues that way for another 364 days!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#39

Re: Single Phase CT Metering

12/31/2013 2:23 PM

The set up of the CT is correct. The two legs are wrapped in opposite directions so as to sum the currents in each leg, as has been pointed out in previous replies. This the same as the current coils in a direct wired single phase 3 wire meter.

The real question here is why this installation requires a current transformer in the first place? This issue was discussed in a post a few months ago regarding an unusually high electric bill.

In the US the standard meter for residential single phase service is rated for 200 amps (with 320 amp meters available for extra high loads) These meters are direct wired, and more than adequate for a single family home, even with electric heating.

Transformer rated meters requiring a current transformer are normally required only for commercial installations where 3 phase service is unavailable (such as a farm) where loads can exceed 200 amps. As was pointed out by one of our gurus in the aforementioned post, you may be being billed at a higher commercial rate rather then the lower residential rate.

__________________
The older I am, the better I used to be
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#57
In reply to #39

Re: Single Phase CT Metering

01/01/2014 11:47 PM

With regards to the real question "why this installation requires a current transformer ..." I can think of a few reasons that only the original poster can help clear up.

--Is the house the only facility being served throughout the meter?

--Were there ever additional facilities or structures served?

--What is the age of the installation?

--How big is the house?

There are (new) large homes we CT meter, and there are new large homes with three-phase service due to their size.

Yes, today you can do single-phase self-contained metering up to 380 amps, but there was a time when even 200 ampere self-contained metering was not common place, and central meter structures (aka central meter poles at a farm) were CT metered, and used a-base meters, good for 100 amps only.

Register to Reply Score 1 for Good Answer
Register to Reply 58 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

baxterm (3); dkwarner (1); Doug Trud (6); dvmdsc (11); gringogreg (1); JohnDG (2); kudukdweller9 (2); LAA_Lucke (9); lyn (1); old salt (4); OscarPhilips (3); PWSlack (1); RAMConsult (2); Rixter (4); Tornado (8)

Previous in Forum: Alternating Current   Next in Forum: Voltage Transformer Fault and Blowing Up

Advertisement