Stator Winding of Generator Burn Out

01/11/2014 4:28 AM

what is the possible cause to make Stator winding of generator burn out?

Generator : 250kVA , 380V , 60 Hz

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 5:40 AM

These might not apply to your case, but long-idled electrical equipment can be infested with insects, cobwebs, animals or their nests, fungi, etc. These can create conductive paths resulting in arcing, which can in turn escalate into serious damage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 8:21 AM

thats a short! any of the things Tornado mentioned or an impact to the windings, anything that gave a pathway for current to travel

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 8:47 AM

Looks, to me, like impact damage caused a short circuit.

Forensic analysis of any failure can be a tedious process. Very often initial conclusions are found to be wrong once a complete tear down and methodical analysis is performed.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 9:13 AM

Generally speaking putting outside influences aside, this is caused from degradation of the winding coating, which is caused by environmental influences and everyday wear and tear.....that is why the maintenance on these includes a megohmmeter test at regular intervals, and the occasional tear town and redip of the windings...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 10:29 AM

Based on my half vast experience with coatings and the effect of heat degradation, I agree with you.

All insulating coatings get old and brittle over time. Heat speeds the process. Excess heat speeds the process up excessively.

Insulation resistance testing - Test Equipment Depot

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 17
#9
In reply to #4

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 12:58 PM

This machine was be rewinded the stator winding one year ago.

we used VPI (vacuum pressure impregnation) for this machine.

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#10
In reply to #9

Re: what is the possible cause to make Stator winding of generator burn out?

01/11/2014 2:37 PM

Perhaps a mistake made during rewinding? Or too much load on that winding part- If phase controlled equipment is used as load, it might compromise that part. We have here a monster machine (stepping dragline) that "clips" part of the phase when overloaded. We can see that all over the grid. It is like a certain angle shortcut.

__________________
Plenty of room here
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Stator Winding of Generator Burn Out

01/11/2014 11:23 AM

If the picture is orientated correctly I would suspect a build up of debris weakening the insulation.

Is the generator used as a standby? Neglect becomes a big problem.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 17
#8
In reply to #6

Re: Stator Winding of Generator Burn Out

01/11/2014 12:54 PM

it's not used as standby.

it's used all the time.

one year after rewinding. it's burn out

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #8

Re: Stator Winding of Generator Burn Out

01/12/2014 12:32 PM

Get back to the re-winder, and get a repair done under the warranty arrangements.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 17
#7

Re: Stator Winding of Generator Burn Out

01/11/2014 12:51 PM

**below picture is rotor**

The machine is Frequency converter (50hz to 60hz) which have 2 synchronous machine coupling together (mono-shaft).

one machine is the motor

and another one is generator which burn out.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11
In reply to #7

Re: Stator Winding of Generator Burn Out

01/11/2014 5:05 PM

Perhaps it was struck by lightning....more likely an oversight during rewinding process though....What triggered the original rewinding? Perhaps there are harsh environmental forces at work here? Any corrosive use in the area? What was the thickness of the winding coating? and what type of coating was used? Is it protected from rain and wind?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Participant

Join Date: Jan 2014
Posts: 1
#25
In reply to #11

Re: Stator Winding of Generator Burn Out

01/16/2014 1:58 PM

All of the answers are valid and lightning is a potential candidate. There is a newer type starting to be recognized as "ground lightening". That type originates miles away from a conventional strike, but may travel to another point at several feet above the ground for a distance of several miles. If you decide to investigate lightening as a potential cause, check for surrounding strikes as much as a week before that could have caused damage to the controls.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#26
In reply to #25

Re: Stator Winding of Generator Burn Out

01/16/2014 4:13 PM

lightening ≠ lightning

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#27
In reply to #26

Re: Stator Winding of Generator Burn Out

01/16/2014 5:34 PM

Wow. That's heavy, man.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jan 2008
Location: East of Eden
Posts: 15
Good Answers: 1
#12
In reply to #7

Re: Stator Winding of Generator Burn Out

01/11/2014 10:57 PM

The actual cause which triggered the failure is open to conjecture as many factors could have been present.

What concerns me is now that the machine has suffered two failures some twelve months apart then I would suspect that the "iron" or laminations of the unit may also now be damaged which would cause degradation of the magnetic flux paths, which in turn will cause localised hot spots exacerbated if unit is overloaded.

Your repairer should be able to perform electro magnetic tests to confirm that the lamination stacks are OK

__________________
Everybody is a genius awaiting discovery
Register to Reply
Participant

Join Date: Dec 2009
Posts: 3
#17
In reply to #7

Re: Stator Winding of Generator Burn Out

01/12/2014 11:08 AM

The first issue I would inspect is why or where is the isolation Barrier between the windings. This is suspect to me, because it seems to have started between where the windings are closest.

Another question I need to ask; Is there a mid-ship bearing between the two sets of windings?

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 17
#24
In reply to #17

Re: Stator Winding of Generator Burn Out

01/15/2014 10:11 PM

No, it's not have.

it is single shaft.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#19
In reply to #7

Re: Stator Winding of Generator Burn Out

01/12/2014 12:13 PM

Is this not a classic case of unbalanced loading resulting in negative phase sequence currents and resultant damage to rotor and stator, I wonder.

__________________
Raghunath
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#13

Re: Stator Winding of Generator Burn Out

01/12/2014 2:05 AM

Well, to state the obvious, more current was demanded than the windings were capable of carrying without overheating. Have you checked your over current protection devices?

Martin

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#14

Re: Stator Winding of Generator Burn Out

01/12/2014 7:37 AM

If it's close to the ocean, salt in the air can accumulate on surfaces and draw moisture out of the air forming a conductive path.

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#15

Re: Stator Winding of Generator Burn Out

01/12/2014 9:14 AM

Looks like it was over loaded, which would have caused the amperage to rise. Was a heavier load installed this year? Was it made to to heavier work than usual? Please check the circuit breakers and if any, the fuse links. Often, during re-winding, they sort of forget to install fuse links.

This would be very expensive to rewind, my heart goes out to you!

__________________
If it was easy anybody could do it.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16
In reply to #15

Re: Stator Winding of Generator Burn Out

01/12/2014 10:00 AM

-----------my final comment on this thread--------------

I still think the windings took an impact, at least a good chance of it. the comments about degraded varnish/insulation are valid points for an aged motor but all that would have be disregarded when the unit was rewound. I don't think age and heat accelerated insulation this rapidly.

the quality of the rewind is certainly in question as well as the quality control of the testing procedure performed (I'm assuming it was completely tested before being returned to online service) a motor this size typically has some type of over-current protection. clearly it failed. if the overloads test as good and there is no information that supports an impact (like a dropped wrench or endbell against the windings, and after all voltage checks have been performed(imbalances, phasing etc) I would be contacting my rewinder and seeking warranty. good luck

Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18

Re: Stator Winding of Generator Burn Out

01/12/2014 11:35 AM

Blue iron is an indication of overheating caused by magnetic flux levels far in excess of the design limits. I suspect that you ran the machine with too much excitation or too little, in either case the machine consumed or produced too many VARs and that excess current caused overheating of the iron and laminations and subsequent damage from all that heat.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Participant

Join Date: Jan 2014
Posts: 3
#21

Re: Stator Winding of Generator Burn Out

01/12/2014 4:25 PM

Hello Cr4 people

Mister Soolloos

most of the replies are helpful.

I think,by installing the rewound rotor or stator, you should check the balancing of the rotor and the bolts that fastened well.

During the continuous working, vibration and heat, and the bolts might elongate.

there is a device which measure the vibration, it should be performed every period after the rewound.

__________________
Have a seat, relax, choose your words carefully, explain as detailed as possible .. I know it will take a couple minutes ... But you will get to the solution fast ..!
Register to Reply
Active Contributor

Join Date: Jan 2014
Posts: 15
#22

Re: Stator Winding of Generator Burn Out

01/12/2014 10:31 PM

It looks like the failure is at the bottom of the coil, thus suspect water flooding at the bottom. If it have been rewind before, most likely the slot was damage and the rewinder did not rectify the damage and did a quick fix to do a quick rewind. thus the slot area will get heated up and did the damage

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Apr 2009
Posts: 94
Good Answers: 3
#23

Re: Stator Winding of Generator Burn Out

01/13/2014 10:13 AM

Long ago, I was testing a generator that was coming back from a rent offshore. I hooked the unit up to the load bank and started the engine. let the engine warm up and flipped the exciter switch BOOM. The engine was brought down to its knees and the end of my finger was black from the fire that came out of the switch. After I cleaned my pants, I inspected the generator for what happened. It looked about as bad as yours. Turns out, the generator had salt in it.

Look at the rest of the stator winding and see if there is any small green areas. The copper while turn green when exposed to the air.

__________________
"Never mistake intelligence for wisdom"
Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

baxterm (1); Buoyhunter (1); Catmandu (1); Charles Tham (1); commutator (1); dvmdsc (1); Fredski (2); lguinta (1); lyn (1); PWSlack (1); raghun (1); RAMConsult (1); redfred (2); Rixter (1); SolarEagle (2); soolloos (4); Sulaiman Amr (1); TonyS (1); Tornado (2); Yusef1 (1)

Previous in Forum: Ceiling Fan Question   Next in Forum: Generator/Shore Neutral-Transfer Switch

Advertisement