HT and FO Cable Crossing

01/13/2014 12:05 AM

Can anyone help me on, how much would be the gap between HT 132kV cable directly buried cable, the FO cable crossing the HT with sleeve?

HT is direct burried and FO - buried with PVC sleeve

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#1

Re: HT AND FO CABLE CROSSING

01/13/2014 4:51 AM

FO deals with only light waves. As far my limited knowledge, EMI does not affect the signal.

It is better to provide sufficient gap between the HV cable and the sleeve for FO, as much needed for maintenance of HV Cable and its excavation. minimum of 300 mm is practical in use.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2014
Posts: 2
#2
In reply to #1

Re: HT AND FO CABLE CROSSING

01/13/2014 5:19 AM

thank you musthafa.

Register to Reply
2
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#3

Re: HT and FO Cable Crossing

01/13/2014 11:32 PM

You need to determine which codes and standards apply to your jurisdiction, then follow those rules. If the two cables are utility owned and maintained in the U.S. the clearances would be per the National Electrical Safety Code, and if not utility owned, per the National Electrical Code ... more or less.

For either code to be in effect, that code has to have been adopted by the local jurisdiction. In most states, the public utility commission, or state legislature adopts the National Electrical Safety Code, but they may lag by a few years, so the most recent many not be the applicable version. In most states, state legislature or local building departments adopt the National Electrical Code as the rule, but again they may lag by a year or two, and they may have additional rules of their own.

If you are not in the United States, I do not have a clue.

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: HT and FO Cable Crossing

01/14/2014 12:10 AM

Ramadass.ar:

Look also at what the FO cable's strength member is. It is most likely "kevlar", but if it is metal, then you have other significant issues with regard to separation.

--JMM

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: HT and FO Cable Crossing

06/16/2023 9:46 AM

The minimum gap would be zero; <...how much...> occurs in reality cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jmueller (1); Musthafa (1); OscarPhilips (1); PWSlack (1); ramadass.ar (1)

Previous in Forum: Gold Plated Aluminum Wiring   Next in Forum: 132/0.4 kV Distribution Transformer

Advertisement