Voltage Drop Of The Motor During Normal And Starting Conditions

01/15/2014 4:49 AM

Dear All,

I am interested in:

· The formulas to calculate the voltage drop of the motors during normal and starting conditions (with code/standard references)

· Is there any requirement in IEC or any other standard/Code concerning the maximum allowable voltage dip for motors

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 4:58 AM

IIRC, NEMA (National Electrical Manufacturers' Association, U.S.A.) stipulates that motors shall be able to start successfully at 85% of nominal voltage. That number may vary with other local/regional codes.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Jan 2014
Posts: 8
#2
In reply to #1

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 5:43 AM

Please can you provide the exact reference in these codes,

Also, what about the formulas?

Thanks

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 5:48 AM

I doubt that there are any universal formulas, because it depends on too many particulars of whatever system is supplying the motor(s).

Ohm's Law applies to the conductors feeding a motor, though.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#4

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 6:31 AM

Standard practice is not to allow more than 10%.

The motor torque is directly proportional to the square of voltage; and at starting, the starting torque shall be at least 70% more than the load torque in order to ramp up the motor. If the voltage drop is allowed to drop more than 10%, the starting torque will be less than the required 1.7 times the load torque; and because of this the motor may stall during start up time.

unfortunately, I am unable to recall the formula and calculation.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 8:43 AM

I'd get copies of the references given above, go to sources such as :Engineering ToolBox and otherwise secure the knowledge you desire some place where you can cite your own references, other than saying that you got your information from an anonymous forum.

Granted there are members here who are very well informed.
Maybe start by learning How to Search the Internet - Hannon Library

Your instructor/interviewer/boss/supervisor or customer might want more proof that you are knowledgeable in the subject at hand and you should have the correct reference material at your disposal to prove your case to them.

Register to Reply
Member

Join Date: Jan 2014
Posts: 8
#6
In reply to #5

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 9:02 AM

I have already checked the internet and didnt find what i have requested in my original query, which are:

· The formulas to calculate the voltage drop of the motors during normal and starting conditions (with code/standard references)

· Is there any requirement in any standard/Code concerning the maximum allowable voltage dip for motors

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 9:09 AM

Yes. It's all in British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #6

Re: Voltage drop of the Motor during normal and starting conditions

01/15/2014 9:21 AM

"Is there any requirement in any standard/Code concerning the maximum allowable voltage dip for motors"

Yes, there is. There are numerous codes and standards. If you could search effectively, or had gotten proper education or experience you would, like many others here, know the answers to your own questions.

Do your own homework.

Register to Reply Off Topic (Score 3)
Member

Join Date: Jun 2014
Posts: 6
#14
In reply to #6

Re: Voltage drop of the Motor during normal and starting conditions

08/17/2014 2:56 AM

Please check below link for the formula

http://www.openelectrical.org/wiki/index.php?title=Cable_Sizing_Calculation

Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Voltage Drop Of The Motor During Normal And Starting Conditions

01/15/2014 9:07 AM

See: IEC 60034-12 "Starting performance of single-speed three-phase cage induction motors"

up to 1000 V rated and intended for direct-on-line or star-delta starting

The standard gives the minimum starting torque Ti for type N,NY,H,HY [for 50 Hz only type N and NY ] and since the torque is directly proportional with the square of supply voltage the minimum supply voltage has to be : Vmin=Vrated*sqrt(Ti/Tstartrated).

Let's say at rated voltage [let's take 400 V as rated] the Manufacturer "declared Tstart/Tn"=2 and minimum Ti in the Table 1 for 100 kW and 8 poles [750 rpm synch.] is 1 then

Vmin=400*sqrt(1/2)=283 V [71% approx.]

The voltage drop depends on the impedance between the supply source and the motor terminal as transformers and cables.

__________________
Julius
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Voltage Drop Of The Motor During Normal And Starting Conditions

01/15/2014 9:20 AM

For transformer voltage drop See IEC 60076-8 clause 7.4 The voltage drop equations.

For cable voltage drop see standard IEC 60364-5-52 or IEEE Standard 141 ch. VOLTAGE CONSIDERATION

__________________
Julius
Register to Reply
Member

Join Date: Jan 2014
Posts: 8
#11
In reply to #9

Re: Voltage Drop Of The Motor During Normal And Starting Conditions

01/15/2014 9:33 AM

I have seen two formulas in Nema ICS-14 (Application Guide for Electric Fire Pump Controllers) section 2.3 which are :

Percent voltage drop during motor running : (ZxMFLAx1.15xVLxSqrt(3))/(Transformer size in KVA x1000) Percent voltage drop during motor starting:(ZxMFLAx6xVLxSqrt(3))/(Transformer size in KVA x1000)

I AM NOT ABLE TO TRACK THE CODE REFERENCES OF THE ABOVE FORMULAS, AND IF THEY APPLY TO OTHER MOTORS (OTHER THAN FIRE PUMP)

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #11

Re: Voltage Drop Of The Motor During Normal And Starting Conditions

01/15/2014 4:23 PM

Fire pumps are a special situation in that they "must start" when called upon to operate; therefore, the formulas are conservative and provide a wider tolerance band for undervoltage operation.

As you have discovered, most codes simply give you the limits, they are "what to do" guidelines, the "how to do it" is left to the designers and engineers. There are plenty of handbooks out there with different formulas for different situations. As long as your calculations yield results within the standards you should be covered, but since you have your doubts you should hire a Professional Engineer to assist you and stamp your drawings thereby shifting your doubts to someone who doesn't have any.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13

Re: Voltage Drop Of The Motor During Normal And Starting Conditions

01/18/2014 9:42 AM

I do not know which country you hail from. But, here in India, the Indian Standard Specification for 3 Phase Induction Motors (IS 325) specifies that the motor shall continue to perform satisfactorily at +/- 6% of the rated voltage, which means that the permissible steady state voltage drop is 6% at the motor terminals. Another Indians Standard, the IS 12615, the Indian Standard Specification for Energy Efficient Motors, mentions this limit as +/- 10%, which means the permissible voltage drop during steady state is 10% at the motor terminals.

As regards the acceleration state voltage drop no such authentic references are available, though. The general practice is to limit the voltage drop to about 15% at the motor terminals.

And, I do not understand what do you mean by formulas for calculating the voltage drop. The Indian Standard Code of Practice for Selection, Installation & Maintenance of Cable, IS 1255, mentions the maximum permissible voltage drop in various types & sizes of cables, as V/km/A. This can be used to calculate the actual voltage drop in the cable supplying power to the motor, taking the steady state Amperes as well as Starting Amperes appropriately, to calculate the actual steady state voltage drop & the acceleration state voltage drop and comparing the same with the above mentioned limits.

This is how I had been sizing the cables all thro my career, with respect to voltage drop based sizing.

Hope this is of help to you.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (2); electricalexpert65 (1); ibrahimtohme (3); lyn (2); Musthafa (1); PWSlack (1); RAMConsult (1); satriatengger (1); Tornado (2)