Power Factor of Diesel Generator

01/25/2014 11:46 AM

Hi All,

I learned that most of the Diesel Generators(DGs) are designed for PF as 0.8, what does it mean? If the capacity of the DG is 250KVA, does it mean that the load cannot be more than 200KW?

My second question is: if my plant PF is 0.5 and the DG capacity is 250KVA, the total load that can be connected then would be 125KW, But if I deploy Capacitors can I bring the PF upto 0.8 and increase the KW capacity?

Theoritically , it looks OK but practically I have not seen any body doing this. Please help me in finding out the correct solution.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Power Factor of Diesel Generator

01/25/2014 1:08 PM

Your gens capacity is 250 kva when the pf = 0.80. At this pf the max kw = 200. If the pf = 0.50 then the kw will have to be reduced. If you improve the pf using capacitors to say 0.90, then the kw allowed would be 225 kw. The KVA is fixed at 250 kva.

I would suggest that you check with the mfg.

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2
In reply to #1

Re: Power Factor of Diesel Generator

01/25/2014 2:50 PM

The max. KW may be 200, regardless of the PF. OP has not given us all the nameplate info.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Power Factor of Diesel Generator

01/25/2014 6:14 PM

Actually OP is confusing the ratings with the operating points. The Generator Capability Curve gives the locus of points that represent the boundaries of operation independent of the system to which the generator is attached:

The blue sloping lines intersect at the rated power factor point, the curved between those points represents the rated MVA, notice that the reactive capability curves (upper and lower) truncate the rated MVA curve. Operation is generally permitted anywhere inside these curves, but the system and the prime over may impose additional operating restrictions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
5
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#4

Re: Power Factor of Diesel Generator

01/26/2014 12:06 AM

Mr. Jain

250kVA 0.8PF means:

Maximum kW load the DG Set can take is 250 x 0.8 = 200kW.

Maximum Inductive kVAR DG set can take is Root (250 sq - 200 sq) = Root(450 x 50) = Root (50 x 50 x 9) = 150kVAR (hope my mental math is correct).

If your kW load exceeds 200kW, the speed of engine will start decreasing, drop in frequency. Exceeding beyond certain limit will result in lugging of engine and tripping.

If your kVAR (inductive) exceeds beyond 150kVAR, will overload the alternator and its excitation system.

If kVAR (capacitive) exceeds will result in loss of magnetic coupling, hunting of rotor and burning of field winding due to overheating in pole shoes as a result if Eddy currents induced.

Optimum is to run the DG Set at near 1PF (say between 0.95 and 1 Inductive). Advantages are:

1. Improve efficiency of DG set by 1.5 to 2% (depending upon Cu losses of alternator). SAVING IN EXPENSIVE AND RARE FUEL. AND SAVING CARBON NUMBERS.

2. Increase life of alternator as this will be running cooler.

3. Increase life of excitation system, AVR, rotating diodes etc.

4. Improve losses in cables and bus bar of Dist. Board as a result of reduction in currents.

And improving PF is a common practice, pl go ahead.

Careful of selecting power capacitors. In case PF of your load is poor due to SCR drives or rectifiers or welding machines - measure Harmonics and install tuned chokes in series as harmonics can damage capacitors due to overheating (dielectric loss). Heavy duty capacitors for this type of load are also available.

And if harmonics in load are present - you need to consult manufacturer of alternator to check is true capability for site load.

Best of luck

Register to Reply Good Answer (Score 5)
Active Contributor

Join Date: Dec 2010
Posts: 23
#5
In reply to #4

Re: Power Factor of Diesel Generator

01/26/2014 2:45 AM

Thanks PowerSolutionsFBD.

I would like to understand more about KVAr:

If your kVAR (inductive) exceeds beyond 150kVAR, will overload the alternator and its excitation system.

If kVAR (capacitive) exceeds will result in loss of magnetic coupling, hunting of rotor and burning of field winding due to overheating in pole shoes as a result if Eddy currents induced.

How can I decide what should be the maximum level of KVAr(Capacitive)? If my PF is 0.5 and I wish to make it to 1, then I need to supply Capacitive KVAr 125? will it cause any problem?

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#7
In reply to #5

Re: Power Factor of Diesel Generator

01/26/2014 8:51 AM

Manish, You did not mention value of total kVA or kW corresponding to 0.5.

Based on total kVA or kW load, Calculate kVAR and select Capacitors based on calculated kVAR and type of load.

If you are in India then I can supply suitable system.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Power Factor of Diesel Generator

01/26/2014 8:27 AM

Dear Mr.mjain.

Definitely it can develop more power and You can over load your DG set for a short duration with in 5 to 7% of the capacity. Generally the Prime Mover will have more capacity.

Your 2nd question,

The answer - Yes, You can add capacitor and improve the P.F. Less P.F. means more Line Current and the winding will get heated more, as the winding temp. is decided by the current and not the PF. At lesser PF the excitation system will be strained.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: Power Factor of Diesel Generator

01/27/2014 8:44 AM

In addition to all the excellent posts I would suggest that you determine the service (duty-cycle) factor of the DG and make sure it is used in your calculations.

A low duty-cycle machine requires even further reduction of loading in order to avoid overheating and damage to the machine.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#9

Re: Power Factor of Diesel Generator

01/28/2014 12:56 AM

usually motor is designed to handle load at 80 to 90% of its full load capacity which gives max efficiency at which pf will be around 0.85

so we have make sure that every equipment or motor which is loaded on dg should be operated at 80-90% of its full load capacity which gives 0.8 PF

adding of cap bank leads to nothing but fuel consumption

as the loading is not for along time it does not any mayor effect on eddy or hysteresis losses

:-) /////

__________________
key questions why, what & how - just think
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#10

Re: Power Factor of Diesel Generator

02/16/2014 4:57 AM

Effect of Low Power Factor on the Genset

  • The Alternator converts the Mechanical Energy, which it gets from the engine, to the Electrical Energy.
  • The Alternator is designed to deliver the output in kVA and assuming the Power Factor of the load is 0.8 lag the kW is calculated.
  • If the Power Factor of the load is lesser than the minimum required Power Factor i.e. 0.8 lag, the excitation system of the alternator gets overloaded.
  • The low Power Factor of the load produces the DEMAGNETISING effect in the magnetic field of the alternator, and to keep the terminal voltage constant more power is required by the excitation system of the alternator. Hence getting overloaded.
  • The excitation system of the alternator comprises of the Exciter Stator, Exciter Rotor, Rotating Rectifier Assembly and the Main Rotor.
  • Due to this overloading of the excitation system the failure may occur in the either of the components of the excitation system of the alternator due to overheating.

Recommendation of using the Capacitor Banks with the Genset

  • The Capacitor banks can be used for improving the Power Factor of the system powered by the Genset.
  • The care should be taken that at no time the Power Factor of the system should be more than 0.90 lag. At no time only capacitors are connected across the output terminals of the alternator. If this happens, the Power Factor goes beyond 0.90 lag and terminal voltage starts shooting up and ultimately lead to the failure of the alternator.
  • If the genset is operated beyond the 0.9 lag Power Factor, the PF may go beyond Unity i.e. on the leading side during switching 'On' & 'Off' the load.
  • If genset is operated on the Unity or Leading PF the alternator undergoes the MAGNETISING effect. Because of this effect the terminal voltage of the alternator will shoot up beyond control and this high voltage may damage the main windings and the AVR of the alternator.

· As far as Engine is concerned, normally the engines are also rated for 0.8 lag.

If the genset is operated above 0.8 lag. (By improving the Power Factor using capacitor bank), the engine gets overloaded. Thus the kW load on the engine is the limiting / deciding factor.

· Your can only improve the Power Factor to the extent, the load does not exceed the rated kW of the engine during operation.

Thanks..

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Power Factor of Diesel Generator

11/28/2023 5:57 AM

<...Capacitors...> are sometimes provided to better match the load characteristics to the <...Generator...> to reduce heat losses in the cables feeding the load. An economic case can be used to justify their addition.

Economics usually vary from place to place and as such fall outside the domain of an international engineering forum; they are commercially sensitive and have no international value.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); dhayanandhan (1); mjain (1); parvathaneni (1); powersolutionsFBD (2); PWSlack (1); RAMConsult (1); SHOCKHISCAN (1); vishram lele (1); wareagle (1)

Previous in Forum: Measuring Resistance   Next in Forum: Electrostatic Motor

Advertisement