Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/29/2014 4:11 AM

In a project on an island offshore Abu Dhabi, UAE, the system voltage available is 3phase 480V 60 Hz. Due to the time constraints the HVAC equipment supplied & installed are of 3Phase+Neutral, 400 V 50 Hz.

A solution to convert the 3PH 480V 60 Hz into 3PH+N 400V 50 Hz was made through a VFD Panel, assuming the VFDs would convert the 3PH 480V 60 Hz into 3PH+N 400V 50 Hz. It did, of course. But after some time, some of the units failed. The reason being, the Output Voltage of the VFD varied corresponding to the varying HVAC Loads. (Though the VFDs could be considered as a converter, they should have been used as a source only for Inductive motor loads which form major part of the HVAC loads and not to supply auxiliary loads)

We are required to provide stable 400V Output supply at the AC DB/Panel which would not vary based on the variations of the HVAC Loads.

The current proposal that is being carried out is to use a Static Frequency Converter, which would provide 3PH+N 400V 60 Hz stable supply from an input of 3PH 480V 60 Hz supply.

We are going to do a trial run on the equipment, next week.

We propose to feed the SFC from a generator at 480V 60 Hz supply, feed the output of the SFC to a Inductive Load bank and test it.

We are apprehensive of the testing since our earlier trial run with the VFD panel was successful but in the long run, the solution failed.
Need your expert opinions on the above.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Static Frequency Converter to provide stable power supply to inductive HVAC Load

01/29/2014 4:17 AM

There wasn't time to order the correct equipment yet there is time available to solve a problem based on the arrival of the incorrect equipment and to hang around on CR4 for proverbial straws at which to clutch. How does that work?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Participant

Join Date: Jan 2014
Posts: 3
#2
In reply to #1

Re: Static Frequency Converter to provide stable power supply to inductive HVAC Load

01/29/2014 4:34 AM

For your kind information,

The HVAC equipment is already procured and installed. Now it is too late to change the equipment to one suiting 480V 60Hz supply.The solution with the VFDs was considered to be suitable and performed successfully during a trial run before installation on site.

Considering the investment already done into the project, we DO NOT have time to change the equipment.

Gentleman,

I am seeking opinions on the solution using the Static Frequency Converter.

if you cant provide a technical opinion, why cant you consider stop being a troll? Does my hanging over here in Cr4 irritating to you in any form? if not, desist making troll comments.

I seek technical comments/opinions.

I am new here. is this the way you deal with people in here.?

If you cant contribute, then please desist.

Ciao.

Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Static Frequency Converter to provide stable power supply to inductive HVAC Load

01/29/2014 4:57 AM

OK. What has been the original equipment manufacturer's input to this problem so far?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2014
Posts: 3
#4
In reply to #3

Re: Static Frequency Converter to provide stable power supply to inductive HVAC Load

01/29/2014 5:07 AM

The original equipment manufacturer of the AC panel which has the VFDs in it is at fault that they suggested that the VFDs could provide a stable Supply. They have refused to rectify the issue and we are dealing with them separately, by litigation etc., which is taking time.

In the meanwhile, to save costs (we are running the AC Panel feeding the HVAC Loads, from generator supply), we had an engineering consultant evaluate the situation and they have come up with the Solution of using a Static frequency Converter.

I was wondering whether any of you have worked with SFCs or Marine Shore to Ship Converters or converters for Aircraft power supplies which function similarly.

this is a first for me, using a Static Frequency converter and I would appreciate all inputs.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Static Frequency Converter to provide stable power supply to inductive HVAC Load

01/29/2014 5:10 AM

It's just that VFDs are designed each to turn a single motor.

Please post the single line diagram for the equipment to be powered on this supply using the camera button.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/29/2014 9:50 AM

You're looking at the wrong piece of equipment, the problem probably lies with HVAC motors which are more than likely NOT rated for inverter/VFD/SFC duty. The converters all generate large amounts of electrical noise in the form of spikes that, if not properly filtered out, and allowed to reach ordinary motors, will cause them to have insulation failures over time. That's probably why the HVAC supplier said "not my problem":

http://motors.automationdirect.com/Information/compare.html

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/29/2014 10:03 AM

...and because of the intended litigation indicated in #4 above, any further Customer Care from that quarter is unlikely to be forthcoming, for both this and any future prospects.

One wonders if this project has become a victim of its own, over-ambitious and unrealistic Gantt Chart.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#8

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/29/2014 5:48 PM

I absolutelly agree with RamConsult, the motor should be inverter grade, otherwise the insulation will fail, but that's not all, the motor will receive electro micro-abrasion as well (unless you permanently swipe the shaft with a conductive brush connected to the shell.

Anyway, most of the 3 phase induction motors for 200 or 400 V 50Hz. can be run in 230 or 440 VAC 60Hz. with no need for extra equipment. I have done it myself; but I'm not sure that yours will withstand the full 480, specially after being ran with an inverter wich might have already derated the insulation; are you sure it is 480?.

If it is 480, you can arrange three single phase stepdown transformers (480v to 48v) as backbust, thus subtracting 48 volts from every phase, which will give you 432Vac 60Hz. perfect for your 400Vac 50Hz system.

What size the transformers ? Oh, you'll have to figure that.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9
In reply to #8

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/29/2014 11:27 PM

That could work if the load wasn't made of compressors. Using the step down transformers will work for the voltage and should be reliable but the 20% higher frequency will increase the pumping capacity of the compressors.

This will most likely produce an overload for the compressors.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#10

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/30/2014 2:25 AM

I would go for dynamic converter consisting of 600 rpm motor generator set.

Motor will be 10 poles 60Hz and Alternator coupled to it 12 pole 60HZ.

Combined Efficiency of MG set can be between 94.5 to 95%. You can not expect similar from static converter. Moreover you do not have any problem of electrical noise from MG set.

I have supplied may such units for industry, ships and air port for 50/60Hz and 50/400Hz applications in 90s and are very reliable.

Most members have suggested cause of failure of previous trials as harmonics - same will be expected from Static Frequency Converter.

Moreover it will not be easy to filter the harmonics for HVAC plant - as harmonics in supply will vary with change in load - expecting higher harmonics when SFC is lightly loaded (due to chopping of AC curve much earlier at low load).

In my opinion MG frequency converter can be better solution. To save cost instead of Synchronous motor + Synchronous Alternator combination, you can opt for Induction motor + Synchronous Alternator combination. Maximum expected slip is 3% - which is within the range of permissible frequency variation of motors.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2012
Posts: 13
#11

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/30/2014 2:26 AM

You mean to say all the equipment's are like chiller,condenser pumps ,chill water pumps and AHU's are 480 Volts or only main control panel working voltage is 480V?

Register to Reply
Participant

Join Date: Jan 2014
Posts: 2
#12

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/30/2014 8:06 AM

How about using Delta Star transformer of suitable voltage ratio! Performance of motor with 60 Hz or 50 Hz is raleted to corresponding cooling. Supplying 60 Hz to 50 Hz motor may cause marginal overheating, and corresponding derating, or additional cooling provision may resolve the issue.

KM

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#13

Re: Static Frequency Converter to Provide Stable Power Supply To Inductive HVAC Load

01/30/2014 9:13 PM

Further to my suggestion of yesterday suggesting MG set, I read your inputs again and noticed that within a week you are going for trial with Static Frequency Converter -

One important point - have you specified to Static Frequency Converter supplier that his equipment shall be suitable to cater for heavy starting current of AC motors which is inductive (Power Factor of starting current 0.2 to 0.25). If not again you may find problems.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!