CT's Secondary Terminal Earthing

02/05/2014 6:01 AM

CT's seconadry terminals should ground or not?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#1

Re: CT's secondary terminal earthing

02/05/2014 7:42 AM

Depends upon the application.

More information needed.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: CT's secondary terminal earthing

02/05/2014 8:30 AM

Generally, standard utility practice is to ground the CT secondary circuit at one point (and one point only!). The location varies: Some do it at the CT terminals, some at the first point the circuit enters a relay/control panel, etc. If the circuit is not grounded, there is the possibility of it having an extremely high induced voltage to ground during some operating conditions. Even with the ground, certain fault conditions could lead to overvoltages that would require additional protection (See Chapter 7 in the Art & Science of Protective Relaying free download from GE).

Note especially that a CT should NEVER be energized while the secondary is open-circuited! Any CT secondary must be shorted and grounded if unused, or else wired into a complete circuit when energized, to avoid catastrophic failure of the CT and danger to personnel and equipment.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: CT's Secondary Terminal Earthing

02/05/2014 11:42 PM

I agree with Old Salt. It depends.

For example:

CT's used in current feedback for DC drives (measuring current in AC lines)were usually always ungrounded and connected to a full bridge diode rectifier circuit.

In a simple metering circuit like a door mounted ammeter it could be grounded.

However in a sophisticated circuit like a GE MultiLin Motor Protection System you should follow the installation instructions for the instrument.

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#4

Re: CT's Secondary Terminal Earthing

02/06/2014 12:49 AM

A current transformer secondary terminal must be grounded before it is operated or put to use in an ac circuit.If it is not grounded,dangerously high voltage may build up,causing explosion in the CT.

__________________
Patrick Whowha
Register to Reply Score 2 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #4

Re: CT's Secondary Terminal Earthing

02/06/2014 1:16 PM

Your thinking about open-circuited CTs developing dangerous voltages.

__________________
jack of all trades
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: CT's Secondary Terminal Earthing

02/06/2014 1:15 PM

Yes and yes (it depends on the application).

See previous threads on CR4 as this question has been answered a few times before.

__________________
jack of all trades
Register to Reply