Electric Solenoid Current Draw

02/12/2014 8:16 AM

I purchased some high pressure solenoids off shore for a project 24 volt coils. The tag indicates 28 watt and in order to spec. out a power supply for the PLC I looked up the calculation for ampere draw and divided the 28 watt by 24 volt for answer of 1.17. Since I was unable to get the info I needed from buying agent I am asking the question, am I on the right track with this calculation or is there more to know. I am not involved professionally in electronics, an obvious statement. Thanks in advance for your consideration.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#1

Re: Electric Solenoid Current Draw

02/12/2014 8:56 AM

For a 24VDC solenoid coil, 1.17 Amps looks correct. When current is flowing, the rated 28W will be dissipated as heat in the coil winding. If you have several of these in a small enclosed area, the heat build up may be excessive. Think about adequate cooling when designing/implementing your project to maximize solenoid lifetime and reliability. Good luck!

Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#4
In reply to #1

Re: Electric Solenoid Current Draw

02/12/2014 9:16 AM

Thank you mjb1962853 and old salt. Very much appreciated you sharing your wisdom and experience.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#2

Re: Electric Solenoid Current Draw

02/12/2014 8:59 AM

roy hammy-

You don't state whether you are dealing with AC or DC electrical. If it is DC your calculation is correct. If you are dealing with AC the calculations are more complicated than the simplicity of Ohms Law. In AC you are dealing with several different factors but you would get an answer close to the resistance of the DC calculations. This is called "reactance". In almost all instances the calculation's for simple AC circuits can be made with Ohms law, I=E/R, to provide the data you are trying to obtain. When Inductance and Capacitance are introduced into the calculations, that's when things get much more complicated.

This may be an oversimplification to some persons but for most purposes it is near to the exact answer. Adding inductors, capacitors, phase angle, etc. would make it seem very complicated and the original question get lost in all the calculations.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#3
In reply to #2

Re: Electric Solenoid Current Draw

02/12/2014 9:07 AM

My error I am working with 24 volt DC

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #2

Re: Electric Solenoid Current Draw

02/12/2014 9:28 AM

Would there be an inrush current, even with DC? I don't know, just asking. I can't think of an obvious reason, but there might be some effect as the armature moves towards the electromagnet.

In any case I would suggest for design OP uses a safety factor at least 2 on the calculated 1.17 amp.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8
In reply to #6

Re: Electric Solenoid Current Draw

02/12/2014 9:59 AM

Yes, there would be an inrush unless there is some external circuitry to reduce or eliminate it. A safety factor would certainly be a prudent item to include within the calculations/specifications.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#15
In reply to #8

Re: Electric Solenoid Current Draw

02/13/2014 11:25 AM

Not usually on DC - the resistive component dominates. I have often seen the opposite - the build up of dc current lags due to the coil inducatnce with an R/L time constant.

With AC when the armature (or solenoid) is open the current is higher until the armature pulls in changing (shortening) the magnetic path length.

Register to Reply Score 1 for Good Answer
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#9
In reply to #6

Re: Electric Solenoid Current Draw

02/12/2014 10:06 AM

I agree with the idea of a safety factor but any inrush current will be from cable capacitance and not solenoid inductance. Depending on the circuitry that will be switching these solenoids you may need to add a fly-back (or snubber) diode in parallel to these solenoids. This diode will be reverse biased (OFF) when the solenoid is turned ON so they will not add to the current draw. The diode will be very briefly forward biased (ON) with the same magnitude of current when one turns OFF the solenoid. So the reverse breakdown voltage (Vbr) of the diode must be greater than 24V and the peak forward current must be greater than 1.17A. The 1N4001 thru 1N4007 series of diodes will do fine but you're certainly not limited to just these.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Electric Solenoid Current Draw

02/12/2014 9:24 AM

Perhaps you might want to go with a little bit of a larger unit. I would use 2 amps per coil. I have seen delivered voltage levels collapse a little bit (then recover) on cheaper DC power supplies. The collapsing voltage can cause problems in response time of some of the solenoids.

Cost difference would be minimal and being safer is better then being sorry.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#7
In reply to #5

Re: Electric Solenoid Current Draw

02/12/2014 9:30 AM

You are correct and this is the plan as we are looking for longevity even though this project is the prototype. The power supply will be of higher capacity.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Electric Solenoid Current Draw

02/12/2014 11:53 AM

You can buy a digital multimeter for a modest banknote.

Measure the resistance (ohms Ω) of the solenoid.

The current taken (cold) will be (supply voltage)/ohms. The wattage would be supply voltage x current.

The copper winding will heat-up when on continuously, and increase in resistance by up to 25%.

Sometimes one gets AC solenoids used on DC. Usually, they need an additional resistance automatically switched-in after pull-in, to give holding current without overheating the solenoid coil. A lot of DC motor contactor solenoids used to have "economy resistors" switched-in for continuous hold. Not likely in your case - the solenoid resistance would be much lower than you would expect for the wattage and supply voltage [watts/supply voltage].

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #10

Re: Electric Solenoid Current Draw

02/13/2014 8:52 AM

First even remotely helpful post when reading from the top down!!!

You beat me to it!!

That is exactly what he needs to do.

He could probably quite easily add the economy resistors (start with a value the same as the cold DC coil resistance) without much of a problem......if we knew more about the circuit!! That would reduce coil heating.....

Some coils will simply pull in with the resistor always in circuit, just a bit slower....testing needed....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#11

Re: Electric Solenoid Current Draw

02/12/2014 3:13 PM

The inrush current will depend on how much metal is inside the solenoid when power is applied. That may also be a function of how much stroke you have. If the stroke is small, you probably have a good bit of metal already in the coil. You might want to get a sample and connect it up with an Oscilloscope and some very small (shunt) resistors to observe the current.

You might consider looking for a suitable varistor since they are sometimes used as a surge protection device. It may slightly affect your timing but for a PLC application that should not be a big deal. If not already stated, you will need a good reversed bias diode to protect the PLC output since turning off the solenoid will create an inductive spike. Just like on a relay, the reverse biased diode takes care of the collapsing magnetic field when the circuit is opened.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#12

Re: Electric Solenoid Current Draw

02/13/2014 2:37 AM

1. For 28VA burden, at 24V, whether AC or DC, the current has to 1.2A.

2. You are talking of High Pressure Solenoid Valve. If the construction is that solenoid operates a pilot which in turn operates a the main valve then 28VA continuous burden calculated in correct.

3. If it is a direct operated solenoid with long travel or travel to open a valve with high pressure difference across its seat, then this may be a two coils in one solenoid. One high resistance and another low resistance coil, both in series, the low resistance provided for initial pull, the high resistance initially shorted by built in contact, which opens once the plunger in pulled in, the current reduces to value sufficient to hold the solenoid opened. In this case, you can know about such construction by connecting DC amp meter in series and noting down the steady state current. If this is the case then continuous burden on DC supply is 24 x measured current (which should be less than 28W).

4. Since you are also talking of use of PLC in the system to protect electronics as one of the contributor suggested, installed a Snubber Diode or Free Wheeling Diode to absorb surge during switching. Also select all auxiliary relays with built in free wheeling diodes.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#14

Re: Electric Solenoid Current Draw

02/13/2014 10:46 AM

The Rule of Thumb is to use 3X rated current for solenoid application. AC will sometimes actually be higher and DC usually lower but the power supply should be great enough, the wire large enough, that the solenoid does not get a voltage drop ahead of the coil. The worst thing on a solenoid is to half pull in and just set there. They will burn up. Most of the energy is expended to pull the solenoid in, and it needs very little to keep it activated. Be sure your supply, wiring, fusing, etc meets the 3X and you won't go wrong. If you need to lower that, you can, but you will need to make specific calculations.

Be sure to put in the reverse diodes across the coils as mentioned earlier or you will have failures on the energizing switches.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#17
In reply to #14

Re: Electric Solenoid Current Draw

02/13/2014 12:11 PM

True for AC - not DC coils

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#18
In reply to #17

Re: Electric Solenoid Current Draw

02/13/2014 1:34 PM

"True for AC - not DC coils"

It is always better to use the 3X rule for DC also because of voltage drop in the line. While the current is not there, DC is much more vulnerable to voltage drop on solenoids and sometimes will "hang" and not operate completely. You really need to be sure full operating voltage is at the solenoid when it is first operated. Once it operates, it is not as important. Also DC is somewhat more sensitive to line and coil inductance to be able to get the current started flowing. Impedance is important in DC circuits also and is sometimes ignored. Most of these relays I have worked with are high speed machine processes and believe me, you must not ignore impedance and use only resistance in those cases.

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#19
In reply to #18

Re: Electric Solenoid Current Draw

02/13/2014 2:35 PM

I design the electrical part of large factory machines that typically bristle with many 100's of solenoids, both hydraulic and pneumatic types.

We exclusively use 24VDC for the power to these solenoids.

For a 30W hydraulic solenoid, we design for 2A per solenoid , but we know well that this is well more than what is actually drawn, the overhead that is allowed for in this figure is always way more than is ever needed.

I don't think it necessary to go to 3x rated current, this seem a little excessive to me.

__________________
paulusgnome
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #19

Re: Electric Solenoid Current Draw

02/13/2014 2:41 PM

....and to me!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
2
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#16

Re: Electric Solenoid Current Draw

02/13/2014 11:58 AM

A picture is better than 1000 words:

At switch "on" for a step voltage the current first grows exponentially till the spring preload is reached and the armature moves, this increases the impedance and the current drops till the armature stops. Then it grows to the maximal value given by U/R. If the solenoid stays a long time under load the copper winding becomes hot and its resistance grows so that for a constant voltage the current will decrease. Which means that the COLD solenoid will drain the HIGHEST current. The dotted line is the exponential current increase if the armature does not move.

At switching off the magnetic field generates a counter voltage peak which is the reason you were recommended a high voltage and current diode to destroy this energy without increasing the switch off time. One sees the armature moving effect at the second peak.

Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#21
In reply to #16

Re: Electric Solenoid Current Draw

02/13/2014 9:03 PM

An excellent answer. GA.

A diode or similar snubber across the coil would of course kill dangerous voltage surges, but will add considerably to the drop off time due to freewheeling action of the reverse diode. If keeping this time short is important, one should use a varistor instead.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#22
In reply to #21

Re: Electric Solenoid Current Draw

02/14/2014 1:16 AM

A diode with a resistor in series approximately equal to the coil resistance will provide a faster drop out and still limit the terminal volts to 1 pn.

Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (2); 67model (1); Andy Germany (2); Codemaster (1); GW (3); kvsridhar (1); mjb1962853 (1); nick name (1); North of 60 (1); NotUrOrdinaryJoe (1); old salt (2); Paulusgnome (1); powersolutionsFBD (1); redfred (1); roy hammy (3)

Previous in Forum: Burned 25uF Cap Was Used in a 400W HPS Floodlight   Next in Forum: AC 3 Phase Induction Motor Brake

Advertisement