Pressure Switch Calibration

02/17/2014 6:16 AM

if our high set point is 2.1psi of a pressure switch and low set point is also 2.1psi of another pressure switch then the callibration procedure is same or differ?

if same then why it is same and if callibration procedure is differ then why it is differ?

CR4Admin - removed email address

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: pressure switch callibration

02/17/2014 7:18 AM

This sounds a lot like a test question.

Calibrate the switches per the manufacturer's calibration procedure.

If you don't know what that is contact the manufacturer and ask.

This information can be found on the manufacturer's web site.

Since you provide no hint of the brand or model number, we cannot help you.

It is unwise to publish your personal e-mail address.

READ THE RULES AND FAQ's.

Finally, if both gauges are the same, why would the procedure be fundamentally different?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: pressure switch callibration

02/17/2014 8:16 AM

...and why would they be connected to the same line when a single pressure switch would do the job?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Pressure Switch Callibration

02/17/2014 1:35 PM

Hint:
Any pressure switch has a deadband. To avoid dithering or chattering when the applied pressure is right at the trip point, the mechanics of a switch are used to have a reset point which is the pressure at which a tripped switch will reset itself to the normal state.

For a trip-on-rising-pressure, the deadband point is below the setpoint. For instance, a switch that trips at 2.50 bar rising might have a deadband reset point at 2.35 bar.

For a trip-on-falling pressure, the deadband is above the setpoint. For instance, a pressure switch that trips at 2.50 bar falling might have a deadband reset point at 2.65 bar.

But, a pressure switch deadband is a pressure switch deadband; it is what it is. The pressure switch does not know whether you set it for rising pressure or falling pressure, it just trips and resets according to applied pressure.

So the question is, what besides the deadband differentiates the action of one pressure switch set to trip on falling pressure at a 2.1psi, with a 2nd pressure switch set to trip on rising pressure at 2.1 psi?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Pressure Switch Callibration

02/17/2014 1:45 PM

I think it's a trick test question.

Register to Reply
2
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#5

Re: Pressure Switch Calibration

02/18/2014 9:16 AM

Part of your grade is class participation, which, up till now, is unsatisfactory.

Hint #2:

Look carefully at the switch action as the pressure cycles up and down.



There's not one electrical switch for trip-on-rising action and another for trip-on-falling action. There's only one electrical switch. So how is trip-on-rising pressure distinguished from trip-on-falling pressure?

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Pressure Switch Calibration

02/19/2014 4:48 AM

Quite. GA

One hopes that this installation has a non-electrical way of relieving pressure to a safe place. A HazOp Study will determine the correct approach.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#7

Re: Pressure Switch Calibration

03/21/2014 9:02 AM

First, let me state your question in the way that I understood it.

You have two pressure switches. One is a high pressure alarm to be set to 2.1 psi, and the other is a low pressure alarm to be set to 2.1 psi. If this is correct, the calibration procedure is NOT the same.

High pressure alarm switches are calibrated by slowing increasing the injected pressure while the Low pressure alarm switches are calibrated by slowly decreasing the injected pressure.

regards,

Vulcan (",)

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply