Absorption Chiller

02/18/2014 7:33 PM

dear all,

im working with absorption chiller where we use LiBr as absorber. one of the challenge working with absorption chiller is to ensure the entire system to be in vacuum condition.

it is easy to detect leaking for pressurized system, but for vacuum system do you guys have any better idea? i went through youtube, more about using smoke.

just in case you have any, appreciate you guys can share it here.

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#1

Re: Absorption Chiller

02/18/2014 8:25 PM

When I worked for the Trane company (~1976) they manufactured these systems, they used helium. They placed a poly sheet over the unit under test, and flooded this tent area with helium. And via some sort of sensor inside the absorption pressure vessel, helium could be detected. I did not work on this product line, so it was only hear-say that I recall this leak test method. And my memory could be wrong. Helium was used as the atom is small, and could find the leak holes.

__________________
ignator -
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Absorption Chiller

02/18/2014 8:54 PM

He leak tests are common but require special equipment.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Absorption Chiller

02/18/2014 9:18 PM

You probably need to call a specialist...and then another specialist....

http://en.wikipedia.org/wiki/Helium_mass_spectrometer

http://www.lbdassociates.com/libr/index.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#4

Re: Absorption Chiller

02/19/2014 1:25 AM

Way back when ... I was working in the field, when I had an absorption (NHH20) unit with a leak, I would apply a coat of rubberized paint on everything except the generator section. Let it cure then service the system. It was quick fix and didn't require a bunch of test equipment or pulling your hair out. I had about a 98% success rate and still have a full head of hair too

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Absorption Chiller

02/19/2014 3:30 AM

Why can't the equipment manufacturer advise? Make a telephone call!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#6
In reply to #5

Re: Absorption Chiller

02/20/2014 7:30 AM

I know nothing about this type of chiller other than having looked at them in operation. Vacuum leaks are very hard to detect and I know nothing of the vacuum levels in this system. However, I did a lot of work on power transformers which on a sealed unit can run from around +7 to -5 psi in the gas space. We used an ultrasonic detector to pick up the sound made by a leak when the system was under vacuum. These also worked fine when under pressure also but then so did soap solutions, so we mainly used the ultrasonic leak detectors when we could not pressurize the units, or the customers did not want us to. They seem tricky to use at first but once you have a little practice they are great.

Do these chillers have readouts for the vacuum level? If they do wouldn't changes correlated with temperature readings give some indication of whether the unit even has a leak at all?

Register to Reply
Power-User

Join Date: Jan 2014
Posts: 206
Good Answers: 5
#7

Re: Absorption Chiller

02/20/2014 8:10 AM

Duct tape!

__________________
There are 10 kinds of people in the world.... Those who use binary code, and those who don't.
Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#8

Re: Absorption Chiller

02/20/2014 8:18 AM

UltraSound detection may work from the outside as it will pick up the noise from air rushing in the leak. If it is tiny such as much smaller than a pinhole the signature will be quite small but will show. Contact UE or SDT for more info as it is a valuable technology very useful in vacuum leaks of most varieties.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9

Re: Absorption Chiller

02/24/2014 12:34 PM

In a power plant setting we have used foamy shaving cream to test suspect areas, however, this might contaminate your LiBr system if the leak is big, and if small leak, probably not going to see it. Typically the shaving cream gets sucked in where the leak is.

If you can afford it, paint the suspected leaky joints with rubberized paint, as was suggested by another responder. That is a good idea.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 11
#10
In reply to #9

Re: Absorption Chiller

03/02/2014 3:45 AM

hi james,

thanks for comment. i personally think that ur suggestion is more practical at the moment.

Register to Reply
2
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#11
In reply to #10

Re: Absorption Chiller

03/02/2014 4:02 PM

I'm just curios about which suggestion of Jame's is more practical?

Refrigeration systems do not do well with any kind of contamination. Shaving cream might be ok with electrical transformers, but I sure wouldn't take the chance in your absorption system, at least if you expect any kind of longevity out of your system. Introducing Triethanolamine and Sodium Lauryl Sulfate, (key ingredients in shaving creams) can change the chemical make up of the LiBr. And the reason why I use rubber based paint on everything but the generator section on absorption systems.Otherwise use a ultrasonic detector, as suggested by 4wsilver.

It's your system.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #11

Re: Absorption Chiller

03/03/2014 10:04 AM

The shaving cream idea was for testing vacuum leaks on condensate pump seals where the hotwell is under approximately 23-25.5" Hg vacuum. (Based on local absolute barometric pressure of 27-27.5" Hg.) One does not allow a lot of the soapy foam to enter the system.

If it is a large enough leak to suck in a lot of soap foam, you could find the leak by listening or smoke testing. Granted, introduction of something that could lower the surface tension of the LiBr solution in the chiller might cause a foaming issue, then you would have to add some defoamer. Better to use the plastic sheet, Helium, and a helium leak detector. Or - just go around with a helium bottle and a section of tubing so you can place the helium flow in one localized area. The helium detector is pulling its sample from within the vacuum section of the chiller, and you will either see an increase or not within a few minutes of starting helium in a localized area.

I am sure there are contractors that would be more than happy to come out and help you with this for a fee. Why not contact the OEM, or the people that installed this piece of equipment?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#14
In reply to #13

Re: Absorption Chiller

03/03/2014 11:43 AM

Hi James, I meant no offence to your idea of the shaving cream trick. I like it, and could be very practical troubleshooting tool for other things besides refrigeration systems . The trouble with any absorption refrigeration system is the pH balance. What's passive on mild steel components destroys copper components and and just the opposite is true, what's passive for copper attacks the mild steel. And that's not even going into non-condensables.

Also,there's been suggestions about using duct tape, that might work temporary, but what I know from experience is, refrigeration systems are not closely watched, you don't think about them until something goes wrong. And probably the most neglected piece of equipment in use, both industrial and households.

Being the OP didn't mention what make, model or size this unit is, I totally agree with you, the OP should call a professional that deals with absorption systems. This is not something you can repair by a "U-tube" video.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Jan 2014
Posts: 206
Good Answers: 5
#12

Re: Absorption Chiller

03/03/2014 8:48 AM

Different system, but similar problem...

I used to work with high-vacuum (chemical) reactors. We routinely wrapped duct tape around each flanged connection. These were big batch reactors, and there were wide temperature-swings as each batch was heated-up, reacted, and cooled-down. After countless temperature & vacuum cycles, the inevitable expansions & contractions of the gaskets, bolts and flanges eventually resulted in small leaks. The duct tape did a good job of sealing the connection and we could see the duct tape getting sucked in as a gasket leak developed. When we needed to open a connection, duct tape was easy to remove/replace.

__________________
There are 10 kinds of people in the world.... Those who use binary code, and those who don't.
Register to Reply
Member

Join Date: Mar 2009
Posts: 5
#15

Re: Absorption Chiller

04/23/2014 2:26 PM

Just do a pressure test with nitrogen and after you have identified and repaired the leak pull the system back down with a vacuum pump. If it will hold twice design pressure it will hold vacuum.

Cheers!

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); dj95401 (3); encik.oranje (1); ignator (1); James Stewart (2); lyn (1); PWSlack (1); roy hammy (1); SolarEagle (1); solexx (1); tribefan1952 (2)

Previous in Forum: Travelaters Versus Escalators   Next in Forum: Shallow Head Design.

Advertisement