Previous in Forum: Tie Rod Torque Question (Hydraulic Cylinder)   Next in Forum: Atmospheric Tank
Vacuum Breaker for an Open Tank Loop
02/19/2014 2:02 PM
I would like to know if there is a critical or set distance for an inverted trap as it relates to the height for the trap and the horizontal distance? This is for a large cooling loop that returns to an open tank. Our objective is to keep from dumping the whole loop into the hot well cold well tank in the event we lose power to the pumps.We are figuring on building the inverted trap at the pipe drops with a vacuum breaker at the top of the inverted trap. This would drain only the pipe drops if the pumps fail.
Any advice would be appreciated.
Thnx
P I
Re: Vacuum Breaker for an Open Tank Loop
02/19/2014 2:49 PM
Well, yes. It depends upon the density, viscosity, temperature, flowrate and its pressure drop as it passes along the down leg of the loop into the tank, which is a function of pipe size and length. As none of these things can be seen from here, consult a qualified Process Engineer locally.
02/20/2014 5:54 AM
If the power to the pumps is lost, then the ability to cool will be much reduced as well.
Rather than solve the problem from a perhaps-blinkered Mechanical Engineering perspective, subjecting the whole design to the rigorous analysis of a HazOp Study (see the article in Wikipedia as introductory reading) comes highly recommended.
Also, apply the principle of Inherent Safety - can the facility be redesigned such that the cooling doesn't require the pumps to be present? Etc., etc.
02/20/2014 7:50 AM
Another way of doing it would be to turn it into an overflow weir, perhaps?