High Current Passes Through Neutral

02/26/2014 2:55 PM

hello every one,

yesterday and today i faced such a big problem in power station

we just receive a generator after rewinding

when i load it on load bank generator operated normally up to 500 kw .

once we connect it to power station we notice that high current passes through neutral causing grounf fault trip to generator

you kindly should know that all neutral are connected together and earthrd directly.

i chech the internet found that the pitch factor may be the cause but i couldn't get the pitch factor for old generator from the vendor to compare it with new rewinded generator.

so

i need help to know the actual reason of the problem and how i get pitch factor and how to treat this problem.

Thanks

Adel

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: high current passes through neutral

02/26/2014 3:10 PM

Treat it as any professional would.

Call in a competent electrical engineer to trouble shoot and fix your problem.

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#8
In reply to #1

Re: high current passes through neutral

02/27/2014 12:18 PM

not you...thanks for commenting...not

__________________
common knowledge...less common than common sense
Register to Reply Off Topic (Score 7)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: high current passes through neutral

02/26/2014 3:10 PM

What were the readings from the insulation test that was carried out before its being bought into use?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: high current passes through neutral

02/26/2014 3:19 PM

is the generator wye connected? Voltage? Actual phase current readings? When you say current was high, it does not give any information. Do you have loads connected phase to neutral?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: high current passes through neutral

02/26/2014 3:20 PM

Did the rewinder make a mistake when rewinding the generator? (Perhaps).

What does the power station's Chief Engineer have to say on the matter?

__________________
jack of all trades
Register to Reply
Anonymous Poster #1
#6
In reply to #4

Re: high current passes through neutral

02/26/2014 5:48 PM

He is the station's Chief Engineer

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: high current passes through neutral

02/26/2014 3:21 PM

Some dimensioned numbers would be a good starting point.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Feb 2014
Posts: 17
#7

Re: High Current Passes Through Neutral

02/27/2014 7:06 AM

Well, Thanx all for ur concern.

firstly when we start troubleshooting this problem we do megger test to check generator, then we test it on dummy load bank (resistive load without neutral ).

when the generator tripped when put it in parallel with other generators we raise the setting of ground fault to complete testing.

we confirm that there isn't neutral current on other generators before loading the rewound generator.

neutral current before loaded generator are (19,7,25)

We confirm that no big single phase load causing neutral current.

So now we load generator found high current in generator ((180A))

and high current through other generators neutral (45,95,50)A

So please kindly advise us to know what root cause of the problem and how could it be serius problem and how we can solve it

Please also check this link

http://www.mirusinternational.com/downloads/EGSA-PL-SO11-Mirus-Article-b.pdf

Any advise will be appreciatted

Thanx

Adel

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#9
In reply to #7

Re: High Current Passes Through Neutral

02/27/2014 12:34 PM

This may be an issue with the terminations within the newly wound motor.

What values did you get when you megger'd each winding? At what point were the measurements taken, at the output terminal or at each winding termination in the case?

But...

I would compare the LCR stator winding measurements. This will give you an idea of the pitch relationship of the windings. Turn the motor over one complete revolution and measure the LCR values at equal points over the 360 degrees. Do this for each phase relationship. Plot your results through a simple Excel run chart and look for inconsistencies in the phase to phase relationships.

Research locked-rotor impedance.

__________________
common knowledge...less common than common sense
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#10
In reply to #7

Re: High Current Passes Through Neutral

02/27/2014 11:11 PM

dooola2020,

very good article, which you have linked, it also suggestes the probable cause of the problem and the solution to get rid of the Problem..

Thank you for sharing this Article..

Secondly we do not connect the neutrals of the Generators in Parallet Operation, rather we connect the Neutral of Biggest (Capacity) generator to Earth and the neutrals of all others will be kepy floating..

Regards..

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#11
In reply to #10

Re: High Current Passes Through Neutral

02/27/2014 11:40 PM

Well, that's a unique way of doing it. Kinda makes synchronization difficult, though, eh?

__________________
common knowledge...less common than common sense
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #7

Re: High Current Passes Through Neutral

02/28/2014 6:48 AM

Once more than one source is connected to the load, only one of their neutrals needs to be connected, otherwise high neutral currents will ensue.

If in doubt, consult a qualified Electrical Engineer locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856