When To Use NAMUR Standard In A Switch?

03/03/2014 3:22 AM

Good day! I'm currently working on a float switch data sheet. Our project requires NAMUR output for switch but the vendor cannot provide it. But as per vendor product data sheet, their float switch have an approval for explosion protection. Is it ok if the switch does not have a NAMUR output? Thanks!

Register to Reply
Pathfinder Tags: Namur
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: When to use NAMUR standard in a switch?

03/03/2014 4:08 AM

If your project requires NAMUR output (i.e. if it's written into a contract), then NAMUR you must provide.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: When To Use NAMUR Standard In A Switch?

03/03/2014 5:30 PM

What class/type of explosion protection, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Mar 2014
Posts: 2
#3
In reply to #2

Re: When To Use NAMUR Standard In A Switch?

03/03/2014 5:47 PM

ATEX II2G (Gas Zone 1) Ex d

Register to Reply
Active Contributor

Join Date: Jan 2014
Posts: 12
#4

Re: When To Use NAMUR Standard In A Switch?

03/04/2014 1:03 PM

Normally NAMUR switches are two-wire switches which are mainly used in explosive areas. They normally produce very low current out put, that is in either <1 mA or >2.2

They are mostly preferred in places we need intrinsic safety, where in these switches/Sensors will be connected to plc/DCS via barriers.

Register to Reply
Active Contributor

Join Date: Feb 2012
Posts: 11
Good Answers: 1
#5

Re: When To Use NAMUR Standard In A Switch?

03/11/2014 12:26 PM

If you are going to use NAMUR output ensure that you have an amplifier or input that is specifically designed for low level switching current. Most of the DCS /PLC can handle NAMUR inputs , but still check with vendor if you need amplifier.

Now whether NAMUR is required or not , you need to check with your client. Is it only required for this particular switch or for all instruments that are located in hazardous area?

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abiegay (1); instruguy72 (1); JohnDG (1); PWSlack (1); SUBRAHMANIAN (1)

Previous in Forum: Supco Humidity Sensor Calibration   Next in Forum: Coal Mill Level Monitoring Sytem for a Roller Mill

Advertisement