Motor Overloads

03/04/2014 3:23 PM

If a motor thermal overload is installed in a cooler environment compared to the motor, Will that cause the overload to trip earlier, If the question I asked is true, how do I go about compensating for that error.

The above motor is a 3 phase induction motor with no internal thermistor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: motor overloads

03/04/2014 3:29 PM

No.

Register to Reply
Anonymous Poster #1
#2

Re: motor overloads

03/04/2014 3:33 PM

A Thermal which is not installed in or near the device it is supposed to protect WILL NOT protect that device correctly.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Motor Overloads

03/04/2014 4:37 PM

It will tend to trip later, rather than earlier. Depending on the specific overload relay design, you may able to compensate by using the next lower heater size, or setting the adjustment slightly lower.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
7
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Motor Overloads

03/04/2014 6:42 PM

There is no valid universal answer, it varies by each individual OL relay manufacturer, even by product within the same mfr's portfolio.

There are what are called "Ambient Compensated" overload relays in which case you need do nothing at all because they have a separate internal thermal sensor that adjusts the trip curve pick-up point in accordance with the relay ambient so that the trip curve is automatically biased to protect the motor.

Solid State overload relays are NOT based upon temperature at all, they SIMULATE the effects of temperature on the motor, but do so based SOLELY on the current flow through the sensor.

Then there are bi-metal "Ambient Insensitive" overload relays in which you need do nothing within a certain range, because the bi-metal element is designed to deform at a much higher temperature than others, so the effects of ambient are less important, but if your ambient falls outside of that range, typically -20 to 60 degrees C, you must take action (most IEC bi-metal overload relays fall into this category).

Then there are those that have no compensation, such as NEMA style bi-metal and eutectic melting alloy overload relays, so you need to very specifically do manual compensation, which itself varies by selecting different values of replaceable heater elements (if it has that kind), changing the dial setting, or adjusting a compensation setscrew.

RTFM.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 7)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Motor Overloads

03/04/2014 7:12 PM

We seem to have more management material.

Good answer, none the less.

Register to Reply
Associate

Join Date: Oct 2011
Posts: 34
#6

Re: Motor Overloads

03/05/2014 3:49 AM

If in case ,a bimetallic relay is placed in cooler environment compared to the motor - it is intended to give delayed trip . this bimetallic relay operates on physical expansion property of two metals , hence elogation of metal will be delayed in cooler circumtences.

Register to Reply
Active Contributor

Join Date: Dec 2013
Posts: 10
#7

Re: Motor Overloads

03/29/2014 11:21 PM

that's right!!!

Register to Reply Off Topic (Score 5)
Associate

Join Date: Apr 2014
Posts: 51
#8

Re: Motor Overloads

04/08/2014 7:10 AM

No it doesn't happen that way, current drawn will cause tripping of motor not the temp. so think technically not like environmental officer

Register to Reply Score 1 for Off Topic
Register to Reply 8 comments