Starter Type for Big LV Chiller

03/05/2014 5:54 AM

Dear all,

Can we have DOL or Star Delta Starter for a LV Chiller (comprised of two compressors, where each is 248 KW) ? or Soft Starter is mandatory?

Please support with official catalogues/references/Standards,

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Starter Type for Big LV Chiller

03/05/2014 8:27 AM

Without any other information about the system supplying the chillers or their type, the answer is "yes".

For an official answer please support with more data and a wire transfer for consulting fees.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Starter Type for Big LV Chiller

03/05/2014 8:46 AM

Motor soft starter - Wikipedia, the free encyclopedia
Centrifugal Chiller Fundamentals - Literature SearchMcQuay HVA
Low Voltage Starters

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Starter Type for Big LV Chiller

03/05/2014 8:52 AM

It depends upon the resilience of the upstream supply and cabling, no detail of which has been offered in the original post. So go with #1 above.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Starter Type for Big LV Chiller

03/05/2014 5:58 PM

Usually, the answer to this question is about regulatory compliance, not engineering. From a purely engineering standpoint, either one is an acceptable answer to "Can we..." Regulations will vary by location and are often administered by the servicing electric power utility through the permitting process.

If you are generating your own power, then it becomes an issue of the economic tradeoffs between having more generating capacity or more expensive starting methods.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5

Re: Starter Type for Big LV Chiller

03/05/2014 11:15 PM

Although DOL starting will result in higher starting current and higher voltage drop, nevertheless the starting torque developed by the motor will be higher. If the inertia of the driven equipment is high then there may be problem in starting (due to higher acceleration time or stalling) when you use a Star Delta Starter or Soft Starter because of reduced voltage at motor terminal.

Hence your decision will depend on the following:

- local regulation regarding starting of the highest rated motor

- short circuit level of the power network

- load inertia

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Starter Type for Big LV Chiller

03/06/2014 12:00 AM

Two out of three ain't bad.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#7

Re: Starter Type for Big LV Chiller

03/06/2014 2:55 AM

Soft starter is advisable. Did you check the recommendations of chiller /compressor manufacturer?

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: Starter Type for Big LV Chiller

03/06/2014 9:59 AM

Most HVAC compressor units start "unloaded".

Other than possibly limiting the higher inrush current during starting which is only present for a brief period of time, I can't see any advantage to using a soft start.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."