Transformer Question

03/06/2014 8:23 PM

Hello all,

I need a transformer for motor with 220kW power, full load current =349 A, starting current = 3 X full load current & power factor = 90.9% @100% load. Voltage ratio for the transformer = 3300/415 V. What the KVA rating for the transformer that suitable to run the motor??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Transformer

03/06/2014 8:49 PM
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#2

Re: Transformer

03/06/2014 10:21 PM

Contact a supplier of large transformers and ask their technical staff. They want to sell you one so they have a vested interest in getting you one of sufficient size. Remember they want to sell you one so get all the information they have and can provide. You have no obligation to buy from them. If possible contact several suppliers.

Another possibility is to contact your power supplier. Some will assist you but many will not. It is worth a phone call to ask.

Otherwise do as #1 has indicated.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Transformer

03/06/2014 10:42 PM

About 500 KVA, but you should share the motor information and starting method with the transformer mfr, and also consult with the motor mfr on acceptable voltage dip while starting. It's a two-way coordination.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Transformer

03/07/2014 7:12 AM

Following IEEE Std C57.96-1999 ch. 6. Basis for calculations of temperatures, loss of life, and loads Equivalent load of a different load and duration may be calculated using formula (3):

LEQ = [(L1^2*t1 + L2^2* t 2 + … + Ln^2* t n)/(t1+ t2 + … + tn)]^0.5

and if will be only one start per hour and no pause then the transformer has to be 253 kVA.

if will be 4 starts per hour and no pause then 300 kVA will be ok.

However, you must check the voltage drop [taking into consideration

the minimum voltage permissible at secondary terminal [usually 0.95 of rated].

The ambient temperature and the elevation have to be considered.

__________________
Julius
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#5

Re: Transformer

03/07/2014 11:05 AM

As stated in #2, but, I am sure you have a "regular" source for electrical components which you purchase, get your monies worth from them and give them your requirements and let them do the leg work for you. Why spend your time doing something you can get for no cost to you. If you want to check to see if the price you are going to pay is fair, once you have the model, etc., of what will be supplied you should be able to cross reference to other manufacturers.

__________________
Never stop learning
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Transformer

03/07/2014 11:36 AM

It would help if we knew the starting method.

With closed transition Y∆ we started 800HP blowers on 800KVA dedicated 11/.433KV transformers daily.

DOL 800HP crushers needed something a bit bigger. It was pure chance a couple of 4000KVA 11/3.3KV transformers had been decommissioned on another plant so we pinched them.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7

Re: Transformer

03/07/2014 11:51 PM

400kVA or bigger depending on what future loading you may need to account for, what is readily available and the budget of course.

400kVA for that motor is plenty.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Participant

Join Date: Mar 2014
Posts: 4
#13
In reply to #7

Re: Transformer

03/14/2014 4:04 AM

if i choose the 400kVA transformer, the secondary current will be 556 Amp. As i state before the current for starting the motor is 3 x full load current = 1047Amp. How the transformer can run the motor if i choose 400kVA transformer? any calculation to prove it?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#14
In reply to #13

Re: Transformer

03/14/2014 4:56 AM

It's not going to pull 1047A continuously.

Transformers can be overloaded for short times with no ill effect or even longer times (possibly continuously) if the resultant life shortening is acceptable. It's a time and temperature issue when it all comes down to it.

To get formulae or tables then you will have to do your own searching or contact your friendly neighbourhood transformer vendor.

If you are uber paranoid then start the motor with a VFD or soft starter. Then you can "calculate" the starting current waveform harmonic effects...

The public supply grid has many elements that are routinely overloaded to maintain continuity of service.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Transformer

03/08/2014 1:24 AM

The maximum voltage drop at start -usually for 200 kW and up-has to be equal or less than 10%-if the starting torque has to be not less than rated torque. In this case, if the transformer is dedicated for this motor supply only then 500 kVA transformer will be suitable [6% short-circuit voltage] or 300 kVA [if short-circuit voltage will be 4%].

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9

Re: Transformer

03/08/2014 9:58 AM

A very rough Rule of Thumb is 1KVA per Hp.,and is allowed for certain NEC calculations.

This will put you in the ball park, then other variables must be considered, as mentioned elsewhere, but this will give a good starting point.

As always, consult the transformer manufacturer before purchasing, and let them hold the liability ball.If you spec it, you are responsible if you get it wrong.

Good Luck

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#10

Re: Transformer

03/08/2014 11:05 AM

Is the transformer to be used only for running a motor?In my experience when ever I plan for installing /purchase of a new transformer the capacity is decided considering the anticipated additional loading expected in the near future. Ambient temperature of the area where you want to install the transformer is another factor to be considered. As per IEEE standards a 24 hour average temperature of 30 ° C is considered as base for transformer loading calculations . The 300 kVA capacity as recommended in earlier replies appears to be sufficient . I have used 250 kVA transformer for pump house motors 240 kVA motor loads. The only difference was it was a combination load of two motors 120 kVA and both runs only for peak hour requirements. So you have to decide depending on your ambient temperature and loading pattern and anticipated future requirement in the same location.

Register to Reply
Participant

Join Date: Mar 2014
Posts: 4
#12
In reply to #10

Re: Transformer

03/14/2014 3:36 AM

yup...only to run the motor...anyone can show the calculation??

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#11

Re: Transformer

03/08/2014 12:46 PM

Industry STANDARD KVA ratings 3 phase are 225,300,500---

225 also will do but why not 300?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#15

Re: Transformer Question

03/14/2014 5:51 AM

Here's the source of an excell calculator with formulae.

Download the spread sheet here.

According to this, 400kVA is ok if your locked rotor multiplier is only 3. That would be a type A motor code. What's the plate say?

Permissible/desireable voltage drop can make a difference too. Just the one motor hanging off this so a bigger dip should be fine for the short duration if it is not a code A motor.

If it is a code A motor then the voltage dip is <1%....

500kVA is better but it will cost you more (not a little) and you may not really need it.

The 400kVA transformer will not fail catastrophically if the locked rotor current is higher than you thought and you don't start and stop the motor like a kid playing with a light switch. If the transformer has time to cool it will be fine and in any event there should be thermal protection on that box of metal.

Have a play with the spreadsheet. It's explained therein. Do more reading too. Make a decision.

My invoice for finding this is in the post. You can send the spreadsheet's author a thank you note.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#16

Re: Transformer Question

03/14/2014 10:08 AM

What does this motor drive. Loading what from start? Or no load at start?

Transformer need to know!

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#17
In reply to #16

Re: Transformer Question

03/14/2014 10:42 AM

Assume locked rotor for starting.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#18
In reply to #17

Re: Transformer Question

03/14/2014 10:59 AM

Define LOCKED !

Why plan for unreal?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#19
In reply to #18

Re: Transformer Question

03/15/2014 1:28 AM

Max torque.

Nothing unreal about a motor starting from a stationary state.

Any mechanical loads coupled to the motor that also need to be accelerated will not result in a higher peak starting current (locked rotor current) it will prolong the starting current duration and that will need to be considered if the motor starts very frequently.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#20
In reply to #19

Re: Transformer Question

03/15/2014 4:11 AM

<will prolong the starting current duration and that will need to be considered if the motor starts very frequently.>

Wal you said IT ALL.

That is why OP should define - even now.

Question needs to be answered -- and settled!

Register to Reply
Participant

Join Date: Mar 2014
Posts: 4
#21
In reply to #20

Re: Transformer Question

03/16/2014 9:01 PM

locked rotor 738%

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#22
In reply to #21

Re: Transformer Question

03/16/2014 10:19 PM

And What is the Loading from Start to Full Speed?

You can describe -if not quantify.

Register to Reply
Register to Reply 22 comments

"Almost" Good Answers: