Using Step-up Transformer with LV VFD

03/09/2014 11:36 AM

Hi,

For a water medium voltage submersible pump and motor that will operate in deep well, 500 meters pump setting, 3.3 KV at 50 Hz - 275kw motor size. Two options were proposed to operate the well pump :

1- Medium voltage VFD

2- Low voltage VFD with Step-up transformer (400V-3.3kv).

I need your help and advice for which option you recommend to use ?? what is the advantages and disadvantage of both options ???

All the Best ...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Using Step-up Transformer with LV VFD

03/09/2014 1:19 PM

I'll go for option 1, Boss.

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Using Step-up Transformer with LV VFD

03/09/2014 1:37 PM

I would consult with some VFD manufacturers who offer both voltage ranges, getting performance and price comparisons. I suspect, but don't know, that Option 1 is better. Please let us know what you discover.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#3

Re: Using Step-up Transformer with LV VFD

03/09/2014 2:38 PM

Saving cost may be a factor to consider. Also consider that MV motors have lower initial torque than LV motors, in general.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4
In reply to #3

Re: Using Step-up Transformer with LV VFD

03/09/2014 3:12 PM

That' a non-issue with a centrifugal pump as the load presents zero torque to the motor at blast-off, Boss.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Using Step-up Transformer with LV VFD

03/09/2014 3:23 PM

True, but the pump has not yet been specified as centrifugal, even if it probably is a multistage version.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6
In reply to #5

Re: Using Step-up Transformer with LV VFD

03/09/2014 3:30 PM

Probably.

__________________
Good moaning!
Register to Reply
Anonymous Poster #1
#22
In reply to #4

Re: Using Step-up Transformer with LV VFD

03/10/2014 11:59 PM

The initial operation of a centrifugal pump depends on the torque of the motor and the starting torque required by the pump. Head and gate position are two more factors when choosing the pump.

Register to Reply Score 2 for Off Topic
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#14
In reply to #3

Re: Using Step-up Transformer with LV VFD

03/10/2014 5:32 AM

The motor/pump is the same, regardless of the option he takes.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Using Step-up Transformer with LV VFD

03/09/2014 6:23 PM

There's only one real consideration. The cost.

If you have 3.3KV available use that and a VSD.
If only LV is available use a LV pump and VSD.

I can't see the sense of stepping up the O/P voltage of a VSD.

This looks to be a case of:
"We've bought this, how do we get it to work?"

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Using Step-up Transformer with LV VFD

03/09/2014 6:53 PM

500 meters of low voltage cable to a 275kW motor might swing the decision.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #8

Re: Using Step-up Transformer with LV VFD

03/09/2014 9:23 PM

Fair point but I'd still be taking a close look at the costings.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#10

Re: Using Step-up Transformer with LV VFD

03/09/2014 10:51 PM

All valid and pertinent points have been requested or discussed so far. On general principles, I support Crabtree's first idea of a medium VFD without a transformer, just on the basic principle of less parts are usually better.

I do have a few questions for the OP. What is the longitude and latitude of this motor and what color is the bearings and the motor housing?

My apologies. With so many recent postings providing nothing but useless information, I felt I could ask for some useless information.

I hope everyone is having a good weekend.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#11

Re: Using Step-up Transformer with LV VFD

03/09/2014 11:36 PM

A disadvantage of both systems is cost. A 275kw motor is a 368hp motor. There are at least 4 wires at 500 meters (546 ft) each. Take into consideration the increases in cable size that must be used to make up for the cable voltage drops. 275hp at 3.3KV for 3 phases requires 50 amps. Voltage drop for 50amps for 1,638ft is 57volts at 3% drop. Cable size required is then #6 copper. 546 ft of #6 stranded 4-conductor minimum voltage of 6,000 volt rating well wire at $40.00/ft comes to approx. $22,000. That's for the wire to the pump only.

Increase the wire size to #4 in order to reduce the cable resistance to less than 3%and the wire cost will be somewhere in the ball park of $40,000 or much more.

All calculations are conservative guess-timations or estimations.

Not only will you be sending a lot of expensive power to this motor/pump arrangement but you have to pay a lot to get it there.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#21
In reply to #11

Re: Using Step-up Transformer with LV VFD

03/10/2014 12:43 PM

Sorry-

Late night calculations weren't so good. 500m = 1,638 ft. Therefore distance is 3* stated. 1,638ft of #4 or #2 wire. Cost of wire is therefore at least $100.00, most likely more, and the total cost at least $70,000!

Good Luck, Old Salt,

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#23
In reply to #21

Re: Using Step-up Transformer with LV VFD

03/13/2014 11:44 AM

GA anyhow. OP had better verify figures, if he doesnt he's not doing his job lol.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#24
In reply to #23

Re: Using Step-up Transformer with LV VFD

03/13/2014 12:45 PM

LongintheTooth-

Yes! Just like me, he probably made a mistake on the first go around. His will be much more expensive than the cost of a line of pencil lead about a foot long.

Thanks!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#12

Re: Using Step-up Transformer with LV VFD

03/10/2014 1:13 AM

As I understood motor would be in the well, VFD and the transformer would be on the ground level. That means the cable is not a factor. The key point is the transformer and transformers do not prefer to work in a wide range of frequency or transforming extreme low frequencies needs special - expensive - transformer.

I definitely recommend the medium voltage VFD.

__________________
Aged man is not old man...
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#17
In reply to #12

Re: Using Step-up Transformer with LV VFD

03/10/2014 9:42 AM

I understand your point, but cable definitely is a very important factor, the higher the voltage, the lower the current, thus a smaller wire gauge can be used, saving a whole lot of money.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13

Re: Using Step-up Transformer with LV VFD

03/10/2014 4:28 AM

Name plate data of the motor? Volts, amps, HP

Supply voltage from the high line or generator?

Type of pump & number of stages, plus HP required per stage

Flow rate required?

Type of cable you are considering using?

Once you have given all that data then can your question be answered...

Failing that.. call a pump company who will design a completion for you

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#20
In reply to #13

Re: Using Step-up Transformer with LV VFD

03/10/2014 12:19 PM

Nice thought, how many times do we get information to give a real answer?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Feb 2012
Location: Trinidad & Tobago
Posts: 7
Good Answers: 1
#15

Re: Using Step-up Transformer with LV VFD

03/10/2014 6:22 AM

I would go with the medium VFD. The transformer may not do very well with fluctuating frequency.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#16

Re: Using Step-up Transformer with LV VFD

03/10/2014 9:35 AM

There is no benefit to installing LV equipment where MV equipment can be used.

LV applications result in a significantly larger equipment footprint, much larger power conductors/cable, and a significant amount of added weight.

All of these items add up to increased difficulty and higher cost for maintenance.

I would opt for the MV VFD.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: Aug 2013
Posts: 2
#18

Re: Using Step-up Transformer with LV VFD

03/10/2014 10:22 AM

The economics of this will in all likelyhood point you to a LV drive and step up transformer. For a 275kw motor (368HP), a MV Drive will cost you in the neighborhood of $125-$140K. Most, if not all, of the MV drive mfg.s have the 1000 HP MV drive as their smallest frame. You are pretty much paying for a 1000HP drive when you buy one for 368HP. A 400HP LV drive will run closer to $25-$30K. Add in harmonics mitigation on the input side and a long lead filter or sine wave filter on the output side and you'll be in the $50-$60K range. (Harmonics mitigation and a good output waveform are pretty standard with MV drives.) Add in the step up transformer to get this to 3300V +/- and your total will almost certainly be less than $100K. In fact, a good multi-tap step up transformer is the way to go as it allows you to adjust for depth and voltage drop based on lead length and wire size.

This is done all the time in the deep well water business in the US, and similarly in deep well oil production (see Schlumberger) all the way up to 2000HP +.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19

Re: Using Step-up Transformer with LV VFD

03/10/2014 10:36 AM

If your pump is gong to run for a significant amount of time, there are also additional losses though the output transformer that result in increased energy consumption. In addition, if you have a primary voltage of let's say 11kV, then you need a significantly larger (physically) primary transformer for supplying the 400V for the LV VFD, and the I squared R losses in that transformer will be higher as well. If it were me, I would go for the MV drive.

The only unmentioned benefit to a LV drive option would be the familiarity factor of the people who need to work on it. In some areas, special qualifications are necessary to work on any MV equipment and if your on-site people do not have that (or are afraid of MV in general), it means bringing in outside contractors whenever work needs to be done.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); brich (1); Crabtree (3); DodgySolenoid (1); JRaef (1); LongintheTooth (1); Michael Smith (1); old salt (3); Qqberci (1); redfred (1); SHOCKHISCAN (1); TonyS (3); Tornado (3); Trini (1); Yahlasit (1)

Previous in Forum: Generator Question   Next in Forum: Motor Rating

Advertisement