MVAR Effect

03/10/2014 1:08 PM

Dear all

What is the effect of the increase in the( MVAR ) on the transformer

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: MVAR Effect

03/10/2014 3:24 PM

An increased load on the transformer. Maybe your question refers to the power factor

or something else. Does it?

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#2
In reply to #1

Re: MVAR Effect

03/10/2014 5:16 PM

Dear sir

thank you for response

I mean if the power transformer operation with low power factor (for examlpe 0.4 PF)

are this effect on transformer

Thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: MVAR Effect

03/10/2014 6:55 PM

It may hum more.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #3

Re: MVAR Effect

03/10/2014 11:19 PM

No, they only hum when their happy. Unhappy they rattle.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: MVAR Effect

03/10/2014 10:26 PM

It's effect is simple, it is the I²R heating of the copper that rules, the transformer will overheat if it is forced to supply more than its rated MVA. Transformers are limited by the magnitude of the current they carry, and they are largely indifferent as to whether it is all reactive current in the form of MVAR, all real current in the form of MW, or any combination in between those extremes. It is always MVA = (MW² + MVAR²)½

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Dec 2013
Posts: 10
#5
In reply to #4

Re: MVAR Effect

03/10/2014 10:44 PM

MVAR - this is the rated capacity of your transformer.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #5

Re: MVAR Effect

03/10/2014 11:54 PM

No, High Voltage Power transformers are rated in MVA, kVA, apparent power; not kW, MW, kVARs, MVARs, real power, reactive power.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: MVAR Effect

03/11/2014 11:15 AM

Dear Mr.ASSER,

The Power Factor will fall.

The winding Temp. will increase. Hence Transformer oil temp. (If oil cooled Transformer)will go up and more cooling fans will get switched on.

Transformer will trip on account of High Temp.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Dec 2013
Posts: 10
#9

Re: MVAR Effect

03/12/2014 12:35 PM

transformer to be over heat.

You adjust the MVAR output of the machine by adjusting the exciter of the machine. That is to raise MVAR output you excite the machine more by increasing the current in the field (rotor). This increases the magnetic coupling of the rotor to the stator and increases the MVAR output.

Register to Reply Off Topic (Score 5)
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Apol (2); ASSER (1); dhayanandhan (1); PWSlack (1); RAMConsult (2); TonyS (1); wareagle (1)

Previous in Forum: Positive, Negative, Zero Sequence Resistance/Reactance   Next in Forum: Transformers Connected In Series

Advertisement