03/19/2014 2:37 AM

Dear Friends,


We have a UPS in our plant for 24 Emergency Exit Lights. We connected 1 X 200AH Lead Acid batteries for back up and now there is need to replace those batteries. Some of my friends advised to replace the batteries with Dry Batteries. They argument that we can use lead acid battery for only 70% but dry batteries can be used for 100% and moreover, the life of dry batteries is very long as compare with lead acid.
Please assist me what should I do.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Mar 2013
Location: Owerri, Imo State Nigeria
Posts: 1
#1

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 3:56 AM

I advice you to go for dry battries because they have great efficiency in dissipating the charges they store.

__________________
Original to the veins! I Question The Status Quo.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 4:01 AM

Friends know best.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 7:40 AM

Do the emergency exit lights stay on in an emergency long enough that everyone can vacate the building before the 70% charge is depleted? If the batteries can, the fact that the dry cell can be depleted to 100% is not valid reason. Does the cost difference warrant the change? Cost of rechargeable dry cell is appreciably higher. The dry cell will not last forever. Does the cost of replacements with lead acid exceed the cost of the dry cell over it's life.

Up to you to answer these question and do the math to find out if your friends are right or wrong. If wrong stop listening to your friends. They may get you fired.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Participant

Join Date: Mar 2014
Posts: 2
#6
In reply to #3

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 11:11 AM

well bro its not like emergency but according to current weather and our country situtation here Loadshedding Occurs, The Government Off the Electricity for 2 hours in 2-3 times per 24 hours, here 200AH Lead Acid Battery is About 285$+, and i bought two in two years. and the one i got is about dead now no enough backup, i just want to get rid of it.. if the dry battery is better. and also if you can sugges any Dry Battery Brand, will be thankful

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#8
In reply to #6

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 12:08 PM

Okay so you say that power goes down 2 to 3 times a day. Lets say it's 2. Times the days in a year is over 700 cycles. The length of time is 2 hours. If that would deplete the charge 100%. Most dry cell at 100% discharge are only good for 500 cycles. So your going to replace them in a year, pay 4 times as much maybe more and you will most likely have to get another charger to charge them.

"i just want to get rid of it.. if the dry battery is better."

If you just want to get rid of it why did you ask for advice. Sound like you have made up your mind no matter what advice anyone gives you. As far as being better depends on the application. Sounds like the lead acid battery you are using does not have the capacity to do what your doing with it. Most lead acid batteries if sized for the job will give 4 years service. It could be also that there is a problem with the charger that is causing the shorten life.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#4

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 9:03 AM

Li-ion polymer. I am a believer. Charge them up come back in 6 months and it is still charged.

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 10:48 AM

which ever type is on sale @ Walmart

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #5

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 11:16 AM

Can't beat that reasoning.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #5

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 4:54 PM

Uhhh...looking at the post about frequent power outages, it would appear as though arkthebest is not in a country where Walmart is a retailer, but rather one they buy from.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/19/2014 10:42 PM

Are you talking about this

versus this

or this

?????

None of these are dry. But if you have frequent deep discharge situations then the first and third ones will last about a year. The AGM batteries are deep discharge "tolerant" and will live longer.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#11

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 12:51 AM

Selection of dry and wet batteries are mostly for environmental cases... as wet batteries have acid fumes emanating, which may cause health concerns somnetimes. Rest wet batteries last longer and are rechrgeable and easily replaceable - lesser expenditure.. some even get them repaired. Consider economics and environment concerns and decide.

Only cost must not be a factor... it all depends on location and law of the land regarding concerns to environment. While considering options think of sealed batteries - which are wet bit emmissions are sealed... that may do good tecnoeconomiocally including environment.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Member

Join Date: Jan 2014
Location: Philippines
Posts: 9
#12

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 4:38 AM

I suggest you should use AGM battery. You should increase the battery capacity to avoid 100% discharge on every power outage.

Register to Reply
3
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 5:03 AM

I have never seen a UPS that did not overcharge (to my mind!) enough to "kill" the batteries, usually shortly after the guarantee is finished......

This "effect" comes regularly as clockwork here on CR4......

By the way, your definitions of dry and wet battery are not very accurate. You need to decide between Primary and secondary, and qualify with a proper name.......

What directly comes to mind as "dry" will not help you much!!!

I would build my own UPS, starting with a true sine wave mains converter of impeccable quality.

Followed by a lead acid battery at least twice the capacity that I would ever need.

Then an intelligent charger, that stops charging at a max of about 13.6 volts......(assuming a 12 volt nominal Lead Acid Battery!).

Let the whole system run all the time, never ever even consider one of those UPSs that try and pick up a dropping mains within "x" microseconds.....

Also, do not forget that a lead acid charger works quite differently to any other battery type.....you cannot simply swap the battery type, that might cause a fire!!!!

At BEST!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#14
In reply to #13

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 5:31 AM

What directly comes to mind as "dry" will not help you much!!!

This is what came to my mind...

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #14

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 6:00 AM

True!! My thoughts exactly!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Jan 2014
Location: Philippines
Posts: 9
#15
In reply to #13

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 5:35 AM

This sounds like overkill for a UPS used to power emergency exit lighting.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #15

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 6:01 AM

It would work beautifully for many years.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Jan 2014
Location: Philippines
Posts: 9
#18
In reply to #17

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 6:57 AM

It's overkill and would be expensive. Why would you want a pure sine wave output? The load is emergency lighting, not datacentre equipment, and is only connected when the AC power is off.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #18

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 7:01 AM

If we are talking about one or two lights, that would be true.......but if we are talking about many, it would be a cheap alternative!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#20

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 8:24 AM

I would increase AH capacity and stay with flooded cell lead acid batteries. I seem to have better luck with them for severe use when properly maintained. Also increase charger capacity to bring them to close to full charge between outages. Electric forklifts use flooded cell batteries and seem to last 5-10 years in daily use.

Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#21
In reply to #20

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 8:31 AM

Many have said to increase the battery AH for full outage period .. But that is only by experience and guess ... Faults' time can't be predicted .. outages ... yes. Hence increasing AH capacity could be helpfull but is not the final solution.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#22

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 9:41 AM

Dump the UPS and purchase tritiated water exit signs. Instant reduced energy consumption and a short ROI time.

Our facility has had the same signs since 1986 and they still work well.

__________________
common knowledge...less common than common sense
Register to Reply
Member

Join Date: Jan 2014
Location: Philippines
Posts: 9
#24
In reply to #22

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 11:29 AM

Sounds like an elegant solution, and provides a worthwhile market for decayed tritium gas recovered from nuclear torpedos.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#23

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 11:19 AM

Dear Mr.arkthebest

Dry Battery is better.

The Acid Batteries, if acid leakage occurs it will land in a serious problem and will be disastorous. Further periodical maintanance such as top up of acid level/addition of distilled water is compulsory.

Further the discharge rate is very small when compared to Dry Battery.

DHAYANANDHAN.S

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#25

Re: Lead Acid or Dry Battery, Which is Better for UPS?

03/20/2014 12:29 PM

Are the batteries charged? Lead acid does best if kept at full potential. In normal use they last 5 or more years. You did not say how much current is used. Getting a dry battery for the same AH might be difficult. You can't charge a dry battery. How long do you want it to work before replacement? If you go with dry, then alkaline is usually the most cost effective.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Register to Reply 25 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); arkthebest (1); dhayanandhan (1); Fredski (1); lrsheldon (1); lyn (1); M.R.Iyengar (2); ozzb (2); phylip (1); Phys (1); Skyking (4); StandardsGuy (1); texasron (1); The.Tinkerer (1); TonyS (1); Wal (2)

Previous in Forum: 460/3 Line Power to Multiple Frequency Speed Drives   Next in Forum: New "DMM" Test Probes - Whom To Introduce?

Advertisement