NER for GTG

03/19/2014 11:57 PM

I have a GTG ( 11kv, 20.35MVA) and step up transformer 11/34.5kv, 20MVA), NER 400A to be installed at step up transformer, would it be possible to installed 10A NER at GTG?, how about earth fault discrimination between downstream fault?
Comments from experts are welcome!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: NER for GTG

03/20/2014 2:39 AM

Let me just run this through the decoder, and IGBTY....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: NER for GTG

03/20/2014 3:15 AM

Not without fewer TLAs.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: NER for GTG

03/20/2014 3:27 AM

Some ratios don't sound right.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: NER for GTG

03/20/2014 6:10 AM

If the GTG is Y then NER is OK.

I think

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Jun 2013
Posts: 39
#6
In reply to #4

Re: NER for GTG

03/20/2014 8:21 PM

My concern on NER rating of Generator

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: NER for GTG

03/20/2014 1:48 PM

If it isn't then the NER is NBG. WTF happens next is ABG.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#7
In reply to #5

Re: NER for GTG

03/20/2014 11:22 PM

IHNFCWAIS

__________________
Most people are mostly good most of the time.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: NER for GTG

03/20/2014 11:26 PM

Have you checked your local standards and GTG manual/salesperson to find out if a 10A neutral earth resistor is suitable?

These things (like acronyms) can vary from country to country.

__________________
jack of all trades
Register to Reply
Associate

Join Date: Jun 2013
Posts: 39
#9
In reply to #8

Re: NER for GTG

03/20/2014 11:43 PM

There is no standard in my country, from my previous project, we used 400A NGR at Transformer and GTG, but how to provide discrimination between GTG and Step-up Transfromer if NGR are rated same.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#10

Re: NER for GTG

03/21/2014 1:01 AM

There is something wrong in describing the system.

If I am correct it shall be Y connected GTG connected to Delta Y step up transformer.

If this is the case, then

Full load current of GTG is 1068A.

Rule of thumb is rating of NGR minimum 1/3 of full load current.

Lower than above, Will result in reduced fault current near to neutral and thus sensing of fault.

Higher earth fault will result in more damage to core on earth fault (calculate the fault energy assuming 10% at fault point and balance 90% across NGR and 400A, 80 to 100m sec fault clearing time and you can estimate the energy in fault and subsequent damage in core at location of fault).

10A earth fault is too low even at full voltage, forget fault occurring at partial winding.

Better go for 400A or at least 350A Resistance.

I will still prefer 400A as this will increase fault time withstand capability of resistance, example when comparing 400A 10Sec NGR with 350A 10Sec for the same actual fault current.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#11

Re: NER for GTG

03/21/2014 8:13 AM

Jack Daniel.

There are two systems here - generator voltage system and the 33kV distribution system.

The 400A NER is on 33kV side / star side of Delta/Star Generator transformer.

10A is in generator neutral-to-earth circuit. The 10A NER in this application is preferred considering that this eliminates possibility of any damage to the stator core laminations in the event of generator stator fault. However, if the generator is connected to the transformer through cables, the 10A NER rating may need to be increased (say 15 or 20A but still below 25A) to meet the criteria - resistive current shall be at least 150% of capacitive currents in the system at the time of earth fault.

Generator system is isolated from the 33kV system by the delta in the generator transformer and hence there is no issue of protection coordination for earth faults.

Trust the above is helpful.

__________________
Raghunath
Register to Reply
Associate

Join Date: Jun 2013
Posts: 39
#12
In reply to #11

Re: NER for GTG

03/24/2014 2:08 AM


Let say the total capcitive current is 50A, could you please advise how to size the NER?, I'm clear about rule of thumb how to estimate capacitive charging current

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#13
In reply to #12

Re: NER for GTG

03/27/2014 10:25 AM

50A Capacitive current makes the system unsuitable for high resistance earthing (earth fault current not exceeding 25A).

However, the NER shall be 1.5x50 = 75A rated as a minimum (from the point of limiting over voltages). Such a large current can mean the stator core burning risk cannot be eliminated in case of generator stator earth fault.

This is only a hypothetical case I hope.

__________________
Raghunath
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#15
In reply to #11

Re: NER for GTG

05/04/2014 7:05 AM

Could you please elaborate for further understanding

'Resistive current shall be at least 150% of capacitive currents in the system at the time of earth fault.'

__________________
When was last time you did something for first time.
Register to Reply
Associate

Join Date: Jun 2013
Posts: 39
#14

Re: NER for GTG

04/11/2014 5:41 AM

1)Do i need to terminate NER Frame earth? if yes, where is the location of termination point? is it at main substation earthing bar or grounding terminal of NER.

2) Neutral Grounding Generator cable is sizing based on full fault current rating without NER consideration or with NER consideration?

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Deefburger (1); Happy singh (1); jack of all trades (1); jackdaniel (4); powersolutionsFBD (1); PWSlack (2); raghun (2); SolarEagle (1); TonyS (1); Tornado (1)