For system users or specifiers, ordinarily this isn't calculated; one looks it up in a performance chart or table for the particular system in question.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
This would depend on the efficiency of the system....A system with 10 EER would draw 10,000 watts to produce 100k btu's...Then again this would vary according to the temperature of air or water being used to cool the condenser coil....When the unit is rated, it is usually at the design limit temperature of 95ºF outside and 75ºF inside.....So actual Wattage(hp) will vary...You can take a real time reading by checking the amp draw of all the equipment(condenser and evap) and amps*volts = Watts/745.7 = HP, which in our example of 10k watts is 13.41 hp....This will give you the HP being used, but to check the actual BTU output of the unit requires measuring the volume of air, relative humidity(dry bulb-wet bulb) and the temperature drop across the evaporator coil....
It will say on the vendor information that was supplied with it.
It will say on the label attached to it.
It will say on the technical information that was presented prior to purchase, and if all that fails,
It will say when a telephone call is made to the original equipment manufacturer with the serial number.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856