Cable Gland

03/28/2014 5:50 AM

Dear All,

While specfying cable gland & plug used in junction box, do we require to mention Hazardous area temperature class (T5, T6)

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Cable gland

03/28/2014 6:03 AM

Rather depends where it's going to be used.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Cable Gland

03/28/2014 9:55 AM

Yes.

Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#3

Re: Cable Gland

03/29/2014 3:15 AM

For procurement of cable glands - hazardous area classification is important and equally important are providing the vendor the physical dimensions of the cable i.e overall dia, under armour dia, and armour type and sixe flat or wire etc.. as if you go through the certification of glands and conduits for explosion proof area - you will note that if the gland size and fitting are such that gaseous material can travel in / out the gland is not considereed to be explosion proof. So proper rubber washer - the sealing element has to be designed there in the gland. Thisis a small item of the system but it is extremely important in the scheme else some explosion inside the junction box may case fatality in the plant.

Moreover there is significant difference in design of gland for general purpose and flame proof cases.. in later case the threads are tapered and do not have a check nut as it is expected to tighten the gland to the extant it can so that any possibility of gas traverse is done away with.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#4

Re: Cable Gland

03/31/2014 3:44 AM

Yes of course, just like you need to specify whether is is an Ex(e) or Ex(d)/ Ex(i) gland, which will depend on the area classification in which you wish to install the JB.

Note the certification of the junction box itself, and take your lead from that.

eg If it states the temperature rating on the data plate, then match your gland to that.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Cable Gland

03/31/2014 4:31 AM

Not if the junction box is Ex e.

Not if all of the circuits passing through the junction box are Ex i.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#6
In reply to #5

Re: Cable Gland

03/31/2014 5:03 AM

True, but in the face of the OP's query, one cannot explain from first principles here.....for that there are text books and training courses available.

The OP might as well have asked the JB supplier for instant advice. Bear in mind he stated that he needed to 'specify'; that this is an engineering forum (he will probably act on advice); that the JB certification is unstated, and that no area classification was given I am uncertain that he even understands "area classification". Also, no country of origin given, so 'Jose' is the only clue (USA, S.America; Europe ? ie different codes)

Register to Reply
Commentator

Join Date: Nov 2008
Posts: 91
#7
In reply to #5

Re: Cable Gland

04/01/2014 5:27 AM

please will you explain more why not?

thanks

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#8
In reply to #7

Re: Cable Gland

04/01/2014 5:45 AM

An (IEC) Ex e junction box does not contain devices producing arcs, sparks or other sources of ignition.

An Ex i circuit is isolated such that the circuit does not carry sufficient energy to produce a source of ignition.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #7

Re: Cable Gland

04/01/2014 10:02 AM

...therefore cable glanding does not need to perform as it would were the installation Ex d - with Ex d the clearances between mating parts of the enclosure, including the gland, have to be sufficiently type-tested so as to give a high level of confidence in being able withstand an explosion inside the enclosure for real without igniting the atmosphere outside. Such a requirement simply does not exist in Ex e and Ex i; one could use bare conductors in the hazardous area under Ex ia though quite why one would want to is open to debate ad nauseam, so of what use is a hazardous area cable gland in such circumstances (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#9

Re: Cable Gland

04/01/2014 6:30 AM

In continuation, I would like to emphasis that cable glands themselves are not explosion proof or otherwise classified for hazardous areas. They become explosion proof or suitable for any other level of hazardous area, when fixed to a JB/ starter etc units. Therefore the gland needs to be considered as integral part of the system so ... requirement specific details must be provided to gland vendor.Kindly once go through the certification provided for your required classification of Hazardous for the glands to be more clear of the subject. With these information even material of the gland is decided.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

a_m_shiha (1); Hilton (2); JohnDG (2); lyn (1); M.R.Iyengar (2); PWSlack (2)

Previous in Forum: WIncc Scada Cannot Run Project   Next in Forum: Different Instruments Used at a Cement Plant

Advertisement